I was surprised to find that bridging neutral and ground in a socket at home tripped the RCD. Measuring with a multimeter, there is indeed 0.1 V between them. If the RCD trips at 30mA that would mean that the wiring in the house must have resistance lower than 3 ohms. (Sounds likely if household wiring is around 0.01 ohm/meter.) So the questions are:

1) why is there a p.d. at all?

2) isn't it a problem for doing electrical work, since switching off the circuit breaker for the ring only disconnects the live wire, meaning the RCD can still trip the whole house if the neutral and ground wires touch?

EDIT: since there are different earthing standard apparently, this question relates to the UK and to a normal urban setup (2-wire 1-phase mains). Also, the live wire is disconnected on the ring. I think the RCD trips because the (small) potential difference between the neutral and earth creates a small but big enough current through the neutral wire, which is not balanced by current in the live wire.

share|improve this question
    
What do you mean by "RCD"? Is that the same as what we call GFCI in the US? –  The Photon Aug 30 at 18:26
    
sorry, RCD = residual current device –  snoopy Aug 30 at 18:27
    
@ThePhoton AFAIUI RCD is the UK/European term for what we call a GFI/GFCI in North America. –  Spehro Pefhany Aug 30 at 19:09

3 Answers 3

up vote 5 down vote accepted

1) Why would you expect a potential difference not to appear? N and earth are tied together only in distribution/transformer boxes, that's a long way till your house, the N wire is usually carrying some current so its potential might slightly differ from ground.

2) If you call tripping the whole house an issue, well that's an issue then. I'd say that safety is not compromised at all, it is instead enforced by this behaviour. Disconnecting also the N through the circuit breaker would work.

share|improve this answer
1  
Hadn't heard the term "transformer cabin" before. I think we'd just call it a box or a vault if it was underground. Googling it led here: goo.gl/iiBf3j –  Spehro Pefhany Aug 30 at 23:30
    
Thanks for the insight, corrected. –  Vladimir Cravero Aug 31 at 6:39
    
Where I live, neutral and earth are also tied together at the distribution panel in every house. I guess this answer is applicable to the UK electric system? –  ntoskrnl Aug 31 at 9:40
    
@ntoskrnl I'm not sure, in Italy this is not true... –  Vladimir Cravero Aug 31 at 10:07

With earth and neutral being tied at a distribution panel but the neutral being used to close the power circuit with live, there will be a potential difference but that will not be why the RCD tripped.

An RCD checks for a balanced current in the live and neutral. If you have paralleled live and earth there will be an imbalance in the current and thus the RCD trips.

share|improve this answer

1) Because the currents in the neutral and ground are different.

2) Switching off the live wire means that there will be no current in the neutrals served by that breaker, effectively floating them, so - other than a momentary spike caused by charge accumulated on the neutrals - touching them to ground shouldn't affect the RCD's balance.

share|improve this answer
    
I agree with you but I think that the breaker only disconnects the live wire, thus current can flow from N to ground, that current coming from another leg of the circuit (possibly another house). –  Vladimir Cravero Aug 30 at 18:44