I've noticed my experiments in the lab with RS-485 work fine with fairly short cables, but termination resistors are needed for true installations. Is their presence or absence a function of the cable length, or other factors?
|
All RS-485 cables require termination. Some may just happen to work without them, but all should have them. |
|||
|
|
Since terminating resistors load down the network, they should not be used unless they are required. Since reflected waves will dampen in 3-4 cycles, if the time for this to occur is less than one data bit width (or one half the bit width if sampling in the middle), the reflected waves will not interfere and terminating resistors are not required. It is a simple enough calculation, figuring on the propagation velocity averaging around 65% of the speed of light: For a 9600 bps communication rate, on a 1000 foot cable, you have a round trip time of 3 usec, a dampening time between 9-12 usec, and a bit width of 10 msec. Therefore, each reflected wave will dampen out prior to you sampling each bit, so termination resistors are not required. |
|||
|