0
\$\begingroup\$

I am wondering, if I reduce the voltage going through a specific sized wire, can I therefore increase the current? I am creating a series-parallel battery bank and it will output 7.4 volts at 75 amp however all cable rated for 75+ amp is far too thick for the product. 10awg is the biggest I can really go. Someone please give me your knowledge!

\$\endgroup\$

1 Answer 1

3
\$\begingroup\$

I think you've confused several concepts here, but the short answer to the question I think you're asking is no, you can't increase the allowable current in a wire by reducing voltage.

The allowable current for a given size wire is determined by the how much temperature rise is acceptable in the wire and by how much voltage drop is acceptable between one end of the wire and the other. The heating limit of the wire sets the allowable power loss per unit length. Since wires have resistance, the power loss in the wire is equal to the current squared times the wire's resistance. Heating limits are usually determined by applicable standards, for which various tables are generally available.

The maximum allowable voltage drop depends on the application; you would have to know the characteristics of your load to be able to determine how much voltage drop is acceptable. Because the resistance of a wire is a function of it's cross section and its length, shorter wires of a given gauge will have less resistance (and thus less voltage drop) than longer wires, so the length is a factor as well.

Where I think you may be getting confused is that if power is held constant, reducing the voltage requires increasing the current. So for a constant power load like a switching converter, reducing the voltage will mean that the converter has to draw more current from the supply to maintain its output power. In contrast, a resistive load like an incandescent light bulb will draw less current from a lower voltage supply.

To get more power through a given size wire, you generally need to increase the voltage. This is why mains power distribution systems generally use very high voltages (hundreds of thousands of volts) for high power/long distance distribution links. The voltage is stepped up for transmission, then stepped back down again close to the point of use. As similar strategy can be done in a battery power distribution scheme as well, but the cost versus benefit for a small system may not make sense.

\$\endgroup\$
4
  • \$\begingroup\$ So in your obviously professional opinion, what gauge wire do you suggest using for a 7.4v 75amp circuit? (Don't mean to convey that as sarcastic) \$\endgroup\$
    – N Martin
    Nov 4, 2018 at 23:25
  • \$\begingroup\$ Without knowing more about your application, probably somewhere between 8AWG and 2AWG. It really depends on the details, of which you haven't provided nearly enough. \$\endgroup\$
    – ajb
    Nov 5, 2018 at 0:29
  • \$\begingroup\$ It's essentially a vape box mod, 3 18650 25amp batteries per bank in series, and the two banks in parallel, which, if I have calculated correctly each battery being 3.7 volts and max discharge of 25 amp should output 7.4 volts at 75 amps \$\endgroup\$
    – N Martin
    Nov 5, 2018 at 0:32
  • \$\begingroup\$ You would need to look at the characteristics of your load and determine what level of power loss is acceptable in the wiring and how much voltage drop your load can tolerate without adverse effects. \$\endgroup\$
    – ajb
    Nov 5, 2018 at 3:59

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.