I am working on an LED panel video wall project made up of 3x8 squares of 128x128 pixel panels. Each panel has a worst case power draw of 65 W (typical: 35 W). I can get the panels as either 24 V or 48 V supply voltage (an embedded DC to DC switcher will make 5 V for the LEDs).
I plan to put the 24 V or 48 V power supplies in a NEMA box at floor level and run power cables 10 ft up the wall (either inside the wall or in a raceway enclosure). Space constraints won't allow me to put the power supplies in or near the video wall.
I am leaning toward choosing the 48 V supply to reduce the current through the power cables, but I am confused by the NEC specifications for low-voltage systems in this case. Some sections refer to less than 50 V, Article 411 Low-voltage lighting uses less than 30 V, Table 11 says Class 2 power supplies between 20 and 60 V. Does the low-voltage lighting section apply to this case? Would the 24 V panels be a safer route to meet NEC requirements? Am I missing an obvious section in the NEC specifications that would apply to powering a video wall with 24 VDC or 48 VDC?
Also, in Table 11a on Class 2 power supplies, they set the maximum VA to 100 for 20-60 V supplies. Does that mean that I need to use 16 100 W power supplies? But then to have less than 100 W per power cable, I would need to run 24 separate cables to each panel since 2 panels combined could add up to over 100 W. Then I would need 24 100 W power supplies. This seems absurd to me, I must be misunderstanding the NEC spec.
I would prefer to use 6 300 W or 4 500 W supplies, then run 6 or 4 separate power cables up to the video wall and distribute the power to each panel. Is there something in the NEC spec that would allow this?
Since your application demands up to 2kVA LVDC this NEC class 2 of product is not desirable. You want a LED driver that is UL60950-1 compliant and 48V is a wise choice since 50A cables are rather heavy gauge. Look harder for an opportunity to locate it close to the load.
Without more details I might suggest 48V LED strings with http://www.meanwell.com/productPdf.aspx?i=366 Does this work for you?? Have a hot spare for reliability or current sharing.