There is several documents say that for three-phase instrument transformers (CT,PT), there should be only one grounding point. With this argument, can I short the the secondary sides of current transformer and voltage transformer together on a bus-bar and then ground this bus-bar to create a single grounding point?
In fact, these CT and PT have already been installed at the substation and they are grounded, just not at the same point. My company will install a meter that uses their outputs. This meter have its CT and PT neutral wires connected on the circuit board and as mentioned, these neutral wires are grounded at their own points. So technically, the grounds of the said CT & PT are connected together. I'm asking if there is any potential danger to this.
Note that these CT and PT are used in measurement of High Voltage substation (110 kV).
Circuit to illustrate the idea: enter image description here
  • \$\begingroup\$ What do the data sheets for the CT and PT recommend? \$\endgroup\$
    Commented Aug 2, 2018 at 10:01
  • \$\begingroup\$ The datasheet for CT state that there should be only one single grounding point (for CT) and the same goes for the PT datasheet. I just wonder if these two grounding points could be connected together. \$\endgroup\$
    – HacLe
    Commented Aug 2, 2018 at 10:09
  • \$\begingroup\$ Electrically that makes sense, I don't know if there are any regulations governing that. \$\endgroup\$ Commented Aug 2, 2018 at 10:11
  • \$\begingroup\$ Do the data sheets explicitly say that the outputs MUST be grounded? \$\endgroup\$
    Commented Aug 2, 2018 at 10:14
  • \$\begingroup\$ I forgot to mention that these are 3-phase transformers. In fact, these CT and PT have already been installed at the substation and they are grounded, just not at the same point. My company will install a meter that uses their outputs. This meter have its CT and PT neutral wires connected on the circuit board and as mentioned, these neutral wires are grounded at their own points. So technically, the grounds of the said CT & PT are connected together. I'm asking if there is any potential danger to this. \$\endgroup\$
    – HacLe
    Commented Aug 2, 2018 at 10:20
The CT and PT secondary are grounded following the high voltage standards on the high voltage side of the installation. This area inaccessible by uncertified personnel, this grounding may not be removed.
You cannot, since you would make a ground loop.
If your meter requires this, you must add additional isolation transformers.
so far as I can see.
The grounding of those windings must be at their neutrals else connecting the meter could cause a short-circuit
The two separate ground points must be bonded together else external fault currents could flow through the meter