I've got a request to fix a snafu made by engineering when they designed this layout. The end-user wants 3 lights that monitor the voltage status on each of their phases to ground (neutral is bonded to ground in the panel).
Since the incoming utility is 208/120Y, they just connected a 120VAC light from each phase to ground and called it a day.
However, we include transformers (labeled XRFMR) for control power in our cabinets for (somewhat) isolated control power. Most of you will see the issue right away here... Whenever they lose A or B phase, the voltage will backfeed through the primary of the transformer and keep the phase light illuminated.
I've been wracking my brain here on simple solutions, but I can't come up with anything that gives us individual lights for each phase. There are numerous phase-loss relays out there that monitor all 3 phases and give you a single NO/NC contact, but nothing with a contact per each phase.
Any ideas?
Example Circuit
    \$\begingroup\$ Can't you connect the lights from phase X to neutral, where X is the phase to be monitored? \$\endgroup\$ Commented Dec 17, 2015 at 22:18
    \$\begingroup\$ What's a CPT? Remember you have an international audience. \$\endgroup\$
    – Transistor
    Commented Dec 17, 2015 at 22:58
    \$\begingroup\$ changed CPT to control power transformer \$\endgroup\$
    – Darksabre
    Commented Dec 18, 2015 at 4:40
    \$\begingroup\$ @user94774: Yes, that would work normally, except we have a transformer with primary taps on the A and B phase. Since a transformer is basically a long run of wire coiled around a metal, you can still get conductivity (backfeeding) from A to B (or B to A) if the other phase drops out. This would keep the light illuminated, even though the phase is really dead. \$\endgroup\$
    – Darksabre
    Commented Dec 18, 2015 at 4:44
    \$\begingroup\$ Connecting the lights to equipment safety ground is not good. For what you're trying to do there, connect them phase to neutral. Never attach to equipment safety ground unless you are installing a main service panel, the one place you bond to ground. This is totally separate from any advice to connect them phase to phase. \$\endgroup\$ Commented Jan 28, 2018 at 4:53
8 Answers 8
Connect three lamps across the phases, rather than to ground.
One lamp between phase 1 and 2, the second between 2 and 3, and the third between 3 and 1.
If a phase loses power, one of the other two phases may backfeed on it, but since it will mostly be in phase then the lamp will go out between the phase that's lost power and the phase that's backfeeding it.
    \$\begingroup\$ Yeah, I thought of that as well, but if you lose one phase, you lose both lights that share that phase, correct? \$\endgroup\$
    – Darksabre
    Commented Apr 18, 2014 at 15:46
    \$\begingroup\$ No, you lose one light. It doesn't tell you which phase failed, but narrows it down to two possible phases. At that point you'll have to do additional testing, but at least it does tell you there's a failure. \$\endgroup\$
    – Adam Davis
    Commented Apr 18, 2014 at 18:59
  • \$\begingroup\$ Hmm, I could see how that would work for Phases 1 and 2 since they're coupled through the transformer primary. But what if I lost Phase 3? I imagine I'd lose the second and third lights in that case. \$\endgroup\$
    – Darksabre
    Commented Apr 21, 2014 at 13:16
  • \$\begingroup\$ @Darksabre Yes, in your case that is what will happen. If phase 1 or 2 goes out, you will lose the one light between the two phases. If phase 3 goes out, you'll lose both lights connected to that phase. So you'll have a little more information than otherwise. Having thought about it more, I don't see a nice off-the-shelf solution for you, though. Were it me, I'd wire a 3 phase plug in the location where you need the indicator, then use a power analyzer along with the lights. When any light goes out, have them look at the power analyzer to figure out the exact issue. \$\endgroup\$
    – Adam Davis
    Commented Apr 21, 2014 at 16:29
  • \$\begingroup\$ ...and arrange the three lights in a triangle representing the wye, with a little wye graphic between them so it's visually clear what's happened... \$\endgroup\$ Commented Aug 24, 2014 at 20:35
this is a very good question and also a very good puzzle! I think that the lights will still work somewhat as desired even though its wired with a transformer. The reason why is because the transformer coil is like a piece of wire if DC is applied but like a resistor when AC is applied. It adds impedance. In this case the transformer coil will act like an inductor and impede the flow of current and cause the Phase Indicator Lamp to dim. So while the lamp doesn’t fully extinguish when a phase fails, it will dim indicating a fault. I would test this out to see how it works. Also, the lamps should not be grounded but connected to Neutral if available. If not (Delta wiring), connect the lamps in a Delta configuration. If one phase fails, two lamps should dim. The lamps should then be labeled Ph1-2, Ph2-3, Ph3-1. If lamps Ph2-3 and Ph3-1 dim, you will know that Phase 3 is out.
  • \$\begingroup\$ I have removed some material from your post. The rules of this site do not allow unrelated / non technical material to be included in posts. A link / reference to this material on your profile page would be acceptable. See comment on this edit for a slightly longer comment. \$\endgroup\$
    – Russell McMahon
    Commented Dec 12, 2020 at 10:26
I'm not sure if you want to do this sort of hack in an industrial setting, but you can produce individual phase indicators fairly simply. Get a commercially available monitor which has indicator LEDs for the 3 phases. Open it up, remove the LEDs, and wire their leads to 3 optocouplers (you might need to replace the LED limiting resistors as well). Then use the optocouplers to drive relays. It's not pretty, and it's a kluge, but if you're careful with workmanship it ought to be fairly reliable.
  • \$\begingroup\$ Heh yep - while it sounds like fun, I don't think UL would approve of that type of setup :( \$\endgroup\$
    – Darksabre
    Commented Apr 18, 2014 at 15:47
If you don't care about sequence test, you could detect any fault imbalance with 3 equal R's , one to each phase and the common Y junction to a light of low current (back-back LEDs or photocoupler switch)
You can also use two lamps and a cap of equal impedance in a Y connection. The two lamps will be chosen to be half power when balanced. (Dim) the cap gives phase shift such that any imbalance causes one light to be brighter than the other.
My initial thought was that a diode (actually three) wired in series would solve your problem -- a diode being a one-way valve that only lets electricity go one way -- it's how a car alternator can generate 3 phase AC and then (with 6 diodes) produce DC. But a diode would only get one side of the sine wave -- and would let the other one through, which got me to thinking:
The question I have is why is that light backfeeding? If you loose the phase, if the wire is cut/disconnected, the wire still isn't grounded, and even if it was, there shouldn't be a voltage between it and ground, so assuming your ground is sufficient (is it?) how could the current backfeed from the ground connection? Now what if something upstream was connecting two of the phases together -- e.g. A is both disconnected from A and connected to B.
In that situation, the light wouldn't be backfeedng -- it'd be running off B, just like B is. Could a defective 3 phase motor do this -- I don't know.
I know it's a bit old question, but I've run into a similar situation. Maybe you could add a phase detector between A & B. In case of failure, the phase detector will lit.
Edit: This can be combined with the solution proposed by @Adam Davis in order to obtain the exact faulty phase.
I suggest the easiest answer is to use neon bulbs with correct (100-200K ish) resistor very small but high-over-rated voltage incandescent indicator bulbs with resistors. they will light when phase is active. Feed back will be so minimal that it is nearly non existent. Not real complicated so you can see it will work and last. Don't trust diode array setups or LEDs as they are not electrically durable over the long hall and are killed by spikes.
The 3 lights need to be connected prior to the transformer
  • \$\begingroup\$ siralexe - Welcome :-) Thanks for trying to help. However your current answer is rather short and not as detailed as we usually expect here. Can you explain more about your suggestion, add a diagram showing where you suggest the lights should be, and add detail about what why connecting the lights "before the transformer" would prevent the problem explained in the question? There is currently no supporting evidence in your answer, to explain how it answers the question, and solves the "backfeed" problem. Click Edit to improve your answer. Thanks! \$\endgroup\$
    – SamGibson
    Commented Mar 21, 2021 at 22:01