I have 7 contactors that need to be controlled remotely (a permanent installation). These are controlled with 240V AC and, according to specs, uses 9.2 VA of power when turning on and 2.7 VA of power when actuated, which in my understanding translates to 40/12 mA.
For this I am designing a PCB with ATmega as a brain, but I am not sure of what is the best way to actually drive those contactors. My back-up plan is that ATmega will drive small relays via transistors, and those relays will switch 240V AC that will actuate the contactors. However, I prefer to do it without intermediate relays. Initially I thought I'd find a TRIAC based circuit and use it as an example to make my board. While browsing the web I found an interesting SSR from SHARP: PR39MF21NSZF. As I understand, I could control it directly from ATmega's 5V pin via a 220 omhs resistor, and connect it's output in series with a contactor and 240V AC. However, the spec says, that:
- this SSR might not be suitable for certain kinds of loads (due to zero-crossing feature).
- it might need snubber circuit to protect output for certain kinds of loads.
Here's an excerpt that says it:
Particular attention needs to be paid when utilizing SSRs that incorporate zero crossing circuitry. If the phase difference between the voltage and the current at the output pins is large enough, zero crossing type SSRs cannot be used. The result, if zero crossing SSRs are used under this condition, is that the SSR may not turn on and off irregardless of the input current. In this case, only a non zero cross type SSR should be used in combination with the above mentioned snubber circuit selection process.
When the input current is below 0.1mA, the output Triac will be in the open circuit mode. However, if the voltage across the Triac increases faster than rated dV/dt, the Triac may turn on. To avoid this situation, please incorporate a snubber circuit. Due to the many different types of load that can be driven, we can merely recommend some circuit values to start with: Cs=0.022μF and Rs=47Ω. The operation of the SSR and snubber circuit should be tested and if unintentional switching occurs, please adjust the snubber circuit component values accordingly.
When making the transition from On to Off state, a snubber circuit should be used ensure that sudden drops in current are not accompanied by large instantaneous changes in voltage across the Triac. This fast change in voltage is brought about by the phase difference between current and voltage. Primarily, this is experienced in driving loads which are inductive such as motors and solenods. Following the procedure outlined above should provide sufficient results.
For over voltage protection, a Varistor may be used.
Any snubber or Varistor used for the above mentioned scenarios should be located as close to the main output triac as possible.
My problem is that I don't understand what kind of load a contactor is (e.g. how much it is inductive, does it give current surges, or kickbacks as a DC relay, etc.) Given the fact that the load will only be those contactors, can they be driven with such SSR? Do I actually need a snubber circuit? I've read that snubbers have leakage current, and that does not make me happy. Maybe it's worth mentioning, that I will only be using 1-2% of it's current handling capacity. The contactors will be in closed state (ON) for long periods (and in total longer than in open state).
I am aware that a diode is required when driving DC relays to handle kickback current, but when it comes to AC, I'm stuck. I wasn't able to find any valuable info on the web about controlling AC-driven contactors.
So, to summarize, my questions are:
- What is the optimal way to drive a contactor from TTL, given that priorities are simplicity (component count), low cost and (preferably) solid-state solution?
- If given SSR is a good option (and should drive the contactor), do I need a snubber to protect it's output it this concrete scenario?
NOTICE - my knowledge in electronics is very basic, I have almost no experience in designing circuits (I have made a bunch of them from examples though) but I have experience working with mains power and do realize all the associated risks and take all the necessary precautions.
UPDATE:
After some helpful hints and comments here's my decision. I chose to use PR36MF51NSZF SSR's to control my contactors and put a [100nF/600V + 4.7k/3W] snubbers across the load. I've received all the components, hooked them up on a breadboard and left there toggling the contactor at 3Hz for several minutes. Everything OK. Then I left it constantly on for ~10 minutes. Temperature of SSR was stable @26 degrees C. So I suppose it's safe to put everything in a permanent installation. I've designed this PCB, and will order to make it next week: