8
I need to model a 80MVA transformer 132/33kV built in 1973. There is very little information on this transformer but I need to populate certain values in the model.
Where can I find typical zero sequence impedance values for this type of transformer?
The positive sequence impedances are as follows:
  • HV – MV = 15%
  • HV – LV = 22.9%
  • MV – LV = 4.9%
Here is the information given:
Specs
And the fields which need to be populated:
Values
  • \$\begingroup\$ A reasonable assumption is that Z0 is about 85% of Z1. \$\endgroup\$ Aug 7, 2014 at 13:05
  • \$\begingroup\$ On further inspection, this appears to be a wye-wye transformer with buried delta tertiary. The above comment I made a year ago isn't really accurate for this case. Try reading some of the references I have cited in electronics.stackexchange.com/questions/195239/… . \$\endgroup\$ Oct 14, 2015 at 15:40
usually the 132/33kv transformers have a Y / D connection and th LV side is resistance grounded through zig-zag transformer and so they have a moderate zero sequense impedance. but some tests show that,
The zero-sequence impedance is usually given as a percentage of the rated phase impedance.
When the transformer has a three-limb core and no delta-connecter windings, the zero-sequence impedance is about 30...60 %. When the transformer has a delta-connected winding, the zero-sequence impedance is 0.8...1.0 times the corresponding short-circuit impedance (uk%).
(from Testing of Power Transformer – Measurement of Zero-Sequence Impedance)