Most generally I'm looking to design a UPS for a low power DC device given higher voltage AC current, with storage handled by a supercapacitor, or a bank wired in parallel.
For my specific case I'm looking to power a RasPi driven from 24VAC 3 Amp HVAC transformer with backup from supercaps in the 2.5V - 3V range.
Some similar commercial products exist, the closest being Juice4Halt, and several LiPo (UPiS) products exist, and more general battery driven options have been questions on this site before. I'm only aware of one project using supercaps, but they're wired in series and between need for capacitor balancing and not using a boost converter the usable time on backup power is more limited than possible and inefficiencies can be reduced. I'm wondering what the most efficient topology for this system would be.
Currently the two methods I can think of each have relative values and I don't have the experience to pick the best, or to know if I'm not thinking of a better idea.
The first is the simple method seems to be (24VAC->Rect->2.4VDC->5VDC->Load):
A more complex version would be buck to 5V then a bidirectional Boost/Buck to the caps (24VAC->Rect->5VDC(<->2.5V)->Load):
My expectation is that the second version would be more energy efficient assuming the power source was generally available, but that the first design would work better given a blackout or brownout situation.
Which one would be the most efficient considering both energy usage and power factor? Would either one be more likely to work as expected in most situations? Would either design cause power issues for the load device (RasPi) while the caps are initially charging? Anything else to watch out for/gotchas to know about?
Your first schematic is pretty straightforward to make, and will most probably work fine. The decrease in efficiency is not that important when you're running on mains power. The second one will be trickier to implement.
For either design, you won't be able to use the cheapest boost converters available, because the most widespread are made for the Li-Ion voltage ranges (i.e. they boost 3..5V to 5V).
Also keep in mind that capacity does not measure the amount of energy stored, that would be C*V2, so a 10F capacitor rated at 2.5 volts stores the same amount of energy as 2.5F capacitor rated at 5V or 0,1F capacitor rated at 25V. This fact also explains why low-voltage caps are cheaper and smaller.
Yet another issue with supercaps is that they often are just gloryfied RTC backup batteries with recommended discarge currents of order of 1-10 mA and internal resistance of 1-10 Ohm. Pulling 0.5 A from such caps will result in permanent damage. Carefully read the whole spec before buying, don't just check capacity and voltage and assume everything else will be fine.
I still suggest you consider a Li-ion battery as the cheapest and most effective solution. That's what I use in my Banana Pi, which exposes Li-Ion battery pads on the board and requires no extra parts (besides the battery itself) to have back-up power.
  • \$\begingroup\$ I'm less concerned with the efficiency while the mains is supplying power (other than not wasting everything), and going off the assumption that the connection to the mains will be intermittent (the use case is a thermostat). So I want to be able to cycle the charge source from any point in the charge cycle. While Li-ion or Li-poly batteries are a lot better than Ni batteries for issues like low cycle lifespan and charge memory, capacitors are still much better for this sort of purpose over the span of several years from what I can tell. \$\endgroup\$ – btharper Jun 21 '15 at 4:48
http://hackaday.com/2014/10/04/supercapacitors-for-the-raspberry-pi/
Here is a complete description of a design that includes handling brown-out and shut-down. (And why are you not checking Hackaday morning and night out of habit?)
  • \$\begingroup\$ That's actually the Juice4Halt device I mentioned in the question. Additionally the capacitors are wired in series instead of parallel as I'm looking to do. I'm also trying to do away with the need for the microprocessor (Altmega328P in the drawings). \$\endgroup\$ – btharper Nov 4 '14 at 18:33
  • \$\begingroup\$ @btharper I missed that. I recently bought 10 5.5V 1F Tokin supercaps to use for the same thing. Cheap out of China and each about the size of a stack of 5 U.S. nickels. I like your second design but need to experiment. \$\endgroup\$ – C. Towne Springer Nov 5 '14 at 22:16
  • \$\begingroup\$ Yea, a 5.5V would be simpler (just inline), but 2.5/2.7V capacitors are cheaper and come in much higher capacities. Looking at it some more I can't figure any reason two conversions would be better, although tweaking is definitely still needed. \$\endgroup\$ – btharper Nov 7 '14 at 5:27