I wanted to know the difference between the induced-EMF and current, in a series circuit layout, vs a parallel circuit layout.

In a series the current would stay the same,however, the induced-EMF would increase? While as a parallel circuit is opposite to that? Same voltage while the current increases?

\$\endgroup\$
2
  • 1
    \$\begingroup\$ If the circuits are identical, then yes - in parallel the voltage output will be the same and the current doubled, and in series, the voltage output will be doubled and the current will be the same. \$\endgroup\$
    – Jodes
    Apr 13, 2015 at 12:50
  • \$\begingroup\$ what do you mean by identical? \$\endgroup\$
    – Pupil
    Apr 13, 2015 at 14:37

1 Answer 1

1
\$\begingroup\$

Start with DC batteries. Easier to understand. We'll turn them into vectors based on polarities which will help when we go to AC.

Series: \$E_T\ = E_1∡0°\ +\ E_2∡0°\$. If the batteries are identical. \$E_T\ = 2\ E_1∡0°\$. Current will be Ohm's Law, \$I\ =\ E_T\ /\ R\$. Twice the single battery current if R is constant.

Series: \$E_T\ = E_1∡0°\ +\ E_2∡180°\ =\ 0\$. Opposite polarities means no voltage or current.

Parallel: \$E_T\ = E_1∡0°\ =\ E_2∡0°\$. If the batteries are identical (same voltage, capacity, etc.) then \$I\ =\ E_T\ /\ R\$ and each battery will supply half the current to load. If the batteries are not identical in every way, current will flow from higher to lower and quickly discharge (in secondary cells).

Parallel: \$E_T\ = E_1∡0°\ =\ E_2∡180°\$. Both batteries act as loads and will quickly discharge and possibly explode or cause a fire. (Hence a lack of response to your question).

So single-phase AC.

Series: Each AC source has a magnitude and an phase angle \$V_1∡0°\$ and \$V_2∡θ\$. Now you must do vector addition on the two voltage sources to find the resultant. \$Vector\ V_R\ =\ Vector\ V_1\ +\ Vector\ V_2\$. Again Ohm's Law gives us current \$I\ =\ V_R\ /\ Z\ =\ V_R\ /\ R\$ - Assuming a resistive load. Current is also a vector. As phase angle between sources varies between 0° and 180°, current will vary from twice to 0.

Parallel: Now, assuming they are identical (same voltage, frequency, phase angle, etc.), current will flow from each source to load with each source providing half of the total.

If they are not identical, large currents will flow in the windings of the generator coils, hopefully activating protection or burning out generators.

In principle, if the main characteristics of devices are identical, you can generally parallel many electrical devices (drivers, regulators, transformers, generators, batteries) to get the same voltage and supply a proportional amount of current.

Three-phase generators can be paralleled if phase sequence, voltage levels and frequencies are the same. Generators can have different kW or kVA ratings with each supplying the same proportion of the load. 200kVA and 100kVA generators operating in parallel at 60%, would supply 120kVA and 60kVA.

A three-phase generators can be connected in wye or delta. When connecting a new generator in delta, odds are that the manufacturers instructions will state connect phase 1 to phase 2, phase 2 to phase 3. Then apply a voltmeter to unconnected terminals of 1 and 3 and measure the voltage when the generator is powered up. If 0V, phase 3 can be connected to phase 1. If one of the phases is backwards, \$2\ ×\ V_{PHASE}\$ would be applied to small impedance of series connected generators, creating large currents and quickly burning out coils.

\$\endgroup\$