Earthing is meant to provide reliable contact of an electric appliance to earth so that if there's an insulation fault current goes into earth instead of through a person's body. This requires earthing to be made of thick conductors driven deep into earth.

Here's how good earthing was described in one domestic pump manual (I'm pretty sure that it correlates well with local building codes): three steel pipes each at least one inch in diameter and twenty feet (six meters) length must be driven into earth vertically in a triangle pattern with at least two feet distance between each two pipes. The top of each pipe must be at least two feet below the ground surface. A common steel rod must be welded to all three and the equipment being earthed must be connected to that rod. Welding spots must be painted to protect them from corrosion.

Now that's plenty of metal and looks impressive. But how does it guarantee a low resistance path for insulation fault currents? What happens if earth is dry and not conductive enough?

\$\endgroup\$
0

6 Answers 6

19
\$\begingroup\$

When the earth is dry. sometimes, earthing works badly.

A pathological case for earthing is things on top of mountains.

The mountaintops tend to be pretty dry. People like installing observatories atop mountains. In a past life I worked with observatories.

The earthing rods are laid out in a ring around the observatory with a buried cable linking them. The rods have tops high in the air; point is to get some lightning protection, and an earth that works at all. (Lightning likes high, metallic things like observatories.)

The air is very dry on top of mountains. ESD is normally prevented by earthing.

Standard protocol was for staff to urinate on the earth spikes instead of using the porta-potty (whenever possible without upsetting tourists).

To make it harder, many sites share the mountaintop with radio transmitters. All that radiated RF is hard to screen when there is no functional earth to connect to. (Radio guys, you have the same problems but you caused mine dammit!)

A co-worker had similar problems earthing in a past life with sand dunes and earthing. Getting the septic tanks to drain on to the dunes can help.

\$\endgroup\$
9
  • 1
    \$\begingroup\$ Do NOT urinate on earth rod during a power fault or if there is any significant earth leakage. Rate of earth electrode corrosion will be much accelerated :-). AFAIR sacks of dolomite dug into hole dug around where ropd would go were NZPO cure for bad earth. (Never urinate on electric fences, even if you are SURE that they are off.) Long (long long ...) radials of wire in a fan may be used for radio station grounding. \$\endgroup\$
    – Russell McMahon
    Jul 27, 2011 at 7:12
  • 3
    \$\begingroup\$ Peeing on a lightning conductor - what could possibly go wrong?! \$\endgroup\$
    – Al Bennett
    Jul 28, 2011 at 11:12
  • 2
    \$\begingroup\$ @RussellMcMahon - I think you mean bentonite (as recommended by Ergon Energy), not dolomite. There's also "carbon cement" which is something like conductive graphite mixed up with concrete - the manufacturer claims that this doesn't shrink when it dries out, so it provides a more consistent earth. \$\endgroup\$ Sep 28, 2013 at 12:42
  • 1
    \$\begingroup\$ @Li-aungYip - Well spotted! Yes, Bentonite was what I intended. Brain served up wrong word :-). Bentonite is a complex Aluminum-Silicate clay that has good water retention qualities and which swells in size when wet. - which as you note may be a less than desirable property. Carbon loaded concrete like an excellent idea as long as the conductivity is high enough to achieve a suitably low ground resistance. Fault current handling would need to be acceptable - eg does not go high-R under high current etc. \$\endgroup\$
    – Russell McMahon
    Sep 28, 2013 at 23:25
  • 1
    \$\begingroup\$ @RussellMcMahon -- concrete works well even without any extra additives, it has sufficient ionic content to be acceptably conductive \$\endgroup\$ Feb 4, 2015 at 13:28
21
\$\begingroup\$

There are no guarantees. Earthing systems will be worked out on the basis both of theory and of empirical results gained from long experience. The earth that you describe is extremely impressive, and far superior to what I have seen in some other standards.

Grounding does NOT ensure personal safety

Note that while personal safety is invovled in grounding considerations, the effectiveness of an earth is not liable to play a major part in improving many shock related outcomes and may make many of them worse rather than better.

The ability to handle fault currents without causing local ground potential rise and to thus trip power interruption equipment (fuses or breakers) is the major consideration. Within premises the path to earth for a person who contacts a live conductor will either be to a grounded metal object (kettle or toaster body etc, or via distributed local ground to earth - wet floor or apparently ungrounded semi conductive surface. In the case of a grounded appliance body, the grounding is intended to offer a short circuit to any fault current from within the appliance and will function without reference to the building ground, provided the return conductor is at ground resistance, or meant to be. eg in NZ (my country) we operate a MEN or "Multiple Earth Neutral" system where ground and neutral are connected at each switch board. Some systems may only connect neutral and ground at the building distribution box and in some systems there is NO neutral to ground connection - eg at least some shipboard systems float the whole system wrt local (seawater and hull) ground. In a ground connected system the local grounded appliance bodies will INCREASE the chance of electric shock for a person touching a live wire from another source than the appliance concerned as they offer a hard ground path, regardless of building ground efficacy.

In the case of distributed ground inside a premises, a situation similar to the above arises with current from an exposed conductor to ground being via the informal local ground and then to earth. Good building grounding may make the shock worse.

ie Building grounding will have little direct effect in protecting occupiers from shock. Where it does have effect is in ensuring that protective equipment operates.

ELCBs - lifesavers Where it DOES work is if ELCBs (Earth leak circuit breakers) are equipped. An ELCB detects the imbalance in current between phase and neutral (go and return) that occurs when a person diverts part of the current from the live circuit to ground. ELCBs are designed to trip at currents below that liable to be drawn by a person contacting mains. They are designed to trip in less than the time taken for one "heartbeat", thereby removing (theoretically) the ability to cause cardiac fibrillation. You can still feel the kick ! - ask me how I know :-). [[Back of clenched fist testing probably allows you to check this. YMMV. Don't try this at home. Ouch!]]

enter image description here

The above diagram is from "Electric Shock Protection"


ELCB, GFCI, GFI, ...

As Connor Wolf notes, in the US, and in various other countries, ELCBs are almost universally called GFCIs (Ground Fault Circuit Interrupter).


Going to ground

Earth resistance is based on providing a means of accessing an effectively zero resistance earth that is "out there". "Out there" is accessed by providing a large enough connection to the zero ground that the resistance of the medium (soil) does not add too much to the resistance achieved. Often an "X" ohm ground is aimed at where "X" is set by experience as being adequate for the protection required. The described method of achieving "X" (here 3 x 20 foot rods etc) is based on acceptable worst case conditions (or should be).

A linear group of conductors spaced "not too far and not too close" relative to each other, form an effective cylinder of about the diameter of the bundle - with too far and too near being based on both theory and practice. This cylinder can be conceived to connect by "curvilinear squares" of the surrounding medium to a larger cylinder of surrounding medium which grows into an effective half sphere as you get further away. The resistance of each "square" is equal (when properly constructed) as a square which is N units wide will also be N units deep.

The transition from effectively a cylinder of conductor to a half sphere occurs over a few radii of the original conductor bundle. It's up to the specifying authorities to ensure that the typical water tables, soil types, conductor type, specified conductor arrangements and phases of the Moon are such that the arrangement will meet the need often enough to be safe enough for the applications considered. ie under very dry conditions with some soil types under some fault conditions results may not be good enough on some occasions. Cost and practicality play a part in determining how often "on some occasions" may be. As failure may lead to death or fires, earthing systems' requirements tend to err on the generous side of sensible.

\$\endgroup\$
3
  • 1
    \$\begingroup\$ Wow. I wish I could upvote this twice. \$\endgroup\$ Jul 27, 2011 at 4:21
  • 8
    \$\begingroup\$ It's worth noting that where I live (USA, West coast) ELCBs are almost universally called GFCIs (Ground Fault Circuit Interrupter), to the point where if you went to any local hardware store, no one would have any idea what an ELCB is at all. \$\endgroup\$ Jul 27, 2011 at 7:42
  • \$\begingroup\$ @ConnorWolf Added a clarifiction to the text based on your 2011 comment :-). \$\endgroup\$
    – Russell McMahon
    Jun 29 at 2:34
3
\$\begingroup\$

tl:dr; Since the "earth" is a common factor to both you and the conductor, it's a non-issue.

It's not that the "earth" is dry and not very conductive at that point of contact, because if that were the case, why would my body be a better conductor, seeing that it's standing on some substrate directly above the "earth" that the copper/steel/etc is driven into. The main thing here that we're looking at is how much more 3 giant pieces of conductive metal want to take that current than your poor little body, and here, they want to a hell of a lot more.

\$\endgroup\$
6
  • 1
    \$\begingroup\$ May I craft some extreme counter-example? Like I'm standing in a pool located over a huge mass of wet earth and those earthing rods are driven one hundred feet away into dry earth. And I'm playing with a mains-connected electric motor that is earthed using those far away rods. Will I still be protected? \$\endgroup\$
    – sharptooth
    Jul 25, 2011 at 13:52
  • \$\begingroup\$ The ground connection normally carries no current, the other two wires ( single phase ) do. It should be limited to fault currents. \$\endgroup\$ Jul 25, 2011 at 14:02
  • \$\begingroup\$ @sharptooth At that point you're needing to calculate the resistivity of the water and the ground, whichever is lower should be the path that the current takes, since the aim of the rods is to create a relitive 0 resistance it can be assumed that any minute difference that the soil creates won't be enough to make that resistance larger than one that you can create around yourself (even if submersed). \$\endgroup\$ Jul 25, 2011 at 14:23
  • \$\begingroup\$ That's what bother me in this scenario. I'm in a pool with a possibly faulty motor and those rods are connected to rather dry earth. Why are they "relative zero" resistance? \$\endgroup\$
    – sharptooth
    Jul 25, 2011 at 14:27
  • 1
    \$\begingroup\$ Re pool query - see my reply. Building ground will not protect you no matter how good or poor it is - that's not its job. \$\endgroup\$
    – Russell McMahon
    Jul 25, 2011 at 14:41
3
\$\begingroup\$

"Dry earth" is a relative term. What appears to be dry may still conduct to a certain level. Real dry earth pulverizes and leaves just sandy grains. And dry soil doesn't go deep. In Belgium the earthing norm (document in Dutch) is a 1.5m rod vertically buried 60cm deep, or a 2.1m rod reaching the surface (so both go to 2.1m deep). In most cases that's enough to reach moist soil. An accepted alternative is a loop buried at least 60cm deep, so that's even less. It's worth noting, though, that Belgium has a moderate climate and nowhere has extremely dry soil, not even in the sandy soil of the Kempen.
A pipe 6m long(!) will give you extra safety. (I'm just thinking how you will drive this into rocky soil..)

\$\endgroup\$
3
\$\begingroup\$

Russell is the closest to correct here: it's not grounding that saves you from shock. Instead, it is the bonding of the equipment grounding conductors to the mains neutral at the service entrance (and only at the service entrance!) that provides the return path for current to flow from a "grounded" chassis back to the source (service entrance neutral) via the EGC and thus trip a breaker or blow a fuse upon a live-to-chassis short -- this works even if the system is floating (i.e. ungrounded), such as on the secondary side of an isolation transformer (a "separately derived system" in NEC verbiage).

As was already stated, personnel protection differential trip devices (ELCBs, RCDs, and GFCIs that conform with UL943 Class A or equivalent trip curves) are vastly superior to grounding and bonding alone in protecting against shock; in fact, NEC 2014 406.4(D)(2)(b) and (c) authorize GFCI protection as a substitute for the presence of an equipment grounding conductor when it is impractical or undesirable to replace existing ungrounded wiring.

Furthermore, when it comes to connecting a building's mains network to earth -- this is needed to protect against certain surge and lightning related effects, even though the EGC bonding will work quite nicely without a grounding electrode connected to the service entrance ground as portable generators used "off the grid" are wired this way as per OSHA/... specs -- ground rods are not the most effective means for accomplishing this task. Instead, what is known as an Ufer ground or more generically as a "concrete-encased ground electrode" is used. In this arrangement, the reinforcing matrix of a large reinforced concrete object in soil contact, such as a building foundation, is bonded to in lieu of driving a ground rod and bonding to that. This is allowed for all construction in the US per NEC 250.52(A)(3), and is even required in new construction in some local building codes.

\$\endgroup\$
1
\$\begingroup\$

"Earthing is meant to provide reliable contact of an electric appliance to earth so that if there's an insulation fault current goes into earth instead of through a person's body. This requires earthing to be made of thick conductors driven deep into earth."

This is wrong. The actual connection to the physical ground is a rod whose purpose is to protect a building from lightning strikes. It has absolutely nothing to do with insulation fault protection.

Also, in a fault condition, the current is passing through to the safety ground conductor, so the conductivity of the actual soil doesn't enter into it.

\$\endgroup\$