I have a question that seems to baffle electricians that I've spoken to. I'm running a 115V Fan off a TRIAC controller that utilizes a 0-10VDC control signal. When I power the DC control signal down, the fan stops running as expected. However, when I take voltage readings at the fan terminal box I get 120V readings from Line/Ground and 120V from Neutral/Ground but zero volts from Line/Neutral. Can somebody explain this to me?
2 Answers
Assuming there is a neutral to ground connection somewhere between your supply transformer and your building ...
simulate this circuit – Schematic created using CircuitLab
Figure 1. Switched neutral.
It sounds as though the triac controller is in the neutral line.
when I take voltage readings at the fan terminal box I get 120V readings from Line/Ground
That's the VM1 reading.
and 120V from Neutral/Ground
That's VM3. The live feed is coming through the lamp filament.
but zero volts from Line/Neutral.
That's VM2. The lamp is off and there is no voltage drop across it.
- pl. check the earthing (ground)..perhaps it is floating
- Instead of checking voltage by voltmeter, pl. check the voltage by 240 V filament bulb..vtingole