I have a question that seems to baffle electricians that I've spoken to. I'm running a 115V Fan off a TRIAC controller that utilizes a 0-10VDC control signal. When I power the DC control signal down, the fan stops running as expected. However, when I take voltage readings at the fan terminal box I get 120V readings from Line/Ground and 120V from Neutral/Ground but zero volts from Line/Neutral. Can somebody explain this to me?

\$\endgroup\$
1
  • 4
    \$\begingroup\$ I'd guess that your controller is switching the Neutral line and therefore Live is always connected. Whether or not this is a good idea is a different question ... \$\endgroup\$
    – brhans
    Commented Jun 9, 2015 at 17:21

2 Answers 2

2
\$\begingroup\$

Assuming there is a neutral to ground connection somewhere between your supply transformer and your building ...

schematic

simulate this circuit – Schematic created using CircuitLab

Figure 1. Switched neutral.

It sounds as though the triac controller is in the neutral line.

when I take voltage readings at the fan terminal box I get 120V readings from Line/Ground

That's the VM1 reading.

and 120V from Neutral/Ground

That's VM3. The live feed is coming through the lamp filament.

but zero volts from Line/Neutral.

That's VM2. The lamp is off and there is no voltage drop across it.

\$\endgroup\$
0
\$\begingroup\$
  1. pl. check the earthing (ground)..perhaps it is floating
  2. Instead of checking voltage by voltmeter, pl. check the voltage by 240 V filament bulb..vtingole
\$\endgroup\$