There is no way to calculate the Starting Current or Locked Rotor Current (LRA) without more information!
Single-phase or three-phase? NEMA Motor Design B, C or D?
What does academic education's sake mean? A voltage of 15V with a power of 132kW is meaningless for an induction motor. You just can't make up numbers. You are also using \$P = V\ I\$, which is DC power.
You'd be better off looking up a motor nameplate and going from there.
Take a 150hp, 1789rpm, 460V, Design B, Code G, 3-phase induction motor. So rated current is 163A, with a power factor of 0.897 lagging and an efficiency of 96.2%.
Code G gives you locked rotor kVA on a per hp basis. Locked rotor kVA will allow you to calculate LRA. Code G = 5.6 up to but not including 6.3. Worst case = 6.3.
$$150hp \times 6.3 = 945 kVA$$
$$ S = \sqrt {3}\ V_{Line}\ I_{Line} $$
$$ I_{Line} = \frac {S} {\sqrt {3}\ V_{Line}} = \frac {945 kVA} {\sqrt {3} \times 460V} = 1,186A $$
LRA will be between 1,102A and < 1,186A vs 163A or 676% to 728% of full-load current.