I have some existing Romex 12/2 installed on my machine. If I doubled the conductors used for each of the two line wires needed, would that adequately carry 30amps at 240 volts? This will be in open air at room temperatures.

\$\endgroup\$
  • \$\begingroup\$ Good luck getting it past an inspector. The fact that it's on a machine and not in a wall might help with that, simply by an argument of jurisdiction. \$\endgroup\$ – AaronD Oct 27 '15 at 15:53
  • \$\begingroup\$ Consider what happens if one wire comes off for whatever reason (cut, corroded, etc.) and the other stays there. \$\endgroup\$ – AaronD Oct 27 '15 at 15:53
  • \$\begingroup\$ Information readily available via Google. Question should be closed. \$\endgroup\$ – Leon Heller Oct 27 '15 at 15:54
  • \$\begingroup\$ It isn't in a household and won't be subject to inspection. I am wondering if it can handle it without overheating or not. As for Google - I am not sure what to sure for that is why I have asked for clarification here. \$\endgroup\$ – Jeshua Lacock Oct 27 '15 at 15:55
  • \$\begingroup\$ If the wire gets cut I have bigger issues - worth consideration though, thank you. \$\endgroup\$ – Jeshua Lacock Oct 27 '15 at 15:56
2
\$\begingroup\$

Short answer: Yes, doubled-up 12 AWG conductors will safely carry 30 Amps.

You need to adequately identify and document what is going on so that someone else down the road who works on your machine why you did what you did.

| improve this answer | |
\$\endgroup\$
  • \$\begingroup\$ This would not be the worst code violation in history and doubling up is safer than not while you are in charge of the facility. When you leave rip it out. Tape or sleeve the conductor pairs together at the ends so it is obvious they are to be together (100mm or so) and most people will figure out what you did, getting it passed is likely to work in very rare locations though it was allowed in some cases in South Africa though not sure if any longer as they have approached the BS/ISO wiring code more closely. \$\endgroup\$ – KalleMP Oct 27 '15 at 18:40
  • \$\begingroup\$ I will use doubled 12 AWG conductors for testing and replace with 10 AWG before finishing the project. \$\endgroup\$ – Jeshua Lacock Oct 27 '15 at 20:21
  • 1
    \$\begingroup\$ Using multiple conductors as primary power feed conductors is common practice in larger electrical installations. The main reason for doing so is that multiple smaller conductors are MUCH easier to pull through conduit than large conductors. \$\endgroup\$ – Dwayne Reid Oct 28 '15 at 5:08