I use an analog input (AI) reading board with 12 bit resolution and read range +-10V. The board AI reading error is given as +-5mV.
I need select a pressure sensor, one of them gives 0-5V output, the other gives 0-10V, so which is ideal for my board.
Thanks.
What you should do is choose the sensor which has the widest output swing which doesn't go beyind the input range of your analog input.
The 0-10v sensor has double the range of the 0-5v sensor, and doesn't go beyond the input range of ±10v. Therefore you should choose the 0-10v sensor.
Since that sensor covers half of the analog input range, you will use 11 of the 12 bits of resolution.
  • \$\begingroup\$ Note that you could use an op-amp, powered from +/-15v, to scale the sensor output to the +/-10v range, giving you most of that bit back. It will introduce a little bit of error and noise, but should give you at least half of that bit resolution. \$\endgroup\$ – rdtsc Oct 28 '15 at 21:32
  • \$\begingroup\$ Mr rocketmagnet thanks for response. What if ai board voltage range can be tunable, can be set 0-5 v or 0-10. Still 0-10v output sensor good for me? \$\endgroup\$ – Soso5 Oct 29 '15 at 6:10
  • \$\begingroup\$ If you can set the input voltage range to 0-10v, then definitely do that, and use the 0-10v sensor. \$\endgroup\$ – Rocketmagnet Oct 29 '15 at 15:57