\$\begingroup\$

I almost had a serious electrical accident last week when I was trying to use an oscilloscope to test out a circuit a student had built.

I had the scope plugged into a floor outlet, and the circuit board powered through a USB cable plugged into a PC in the lab. I was having trouble getting the scope to display a signal with just the probe tip exploring points on the circuit board, so I tried connecting the probe ground alligator clip to the circuit board ground (even though I thought that should be unnecessary), and got a large arc and melted wire and charred parts of the circuit board and some sensors.

After some head scratching and a few more sparks I finally verified with a voltmeter that the metal shield of the USB port on the PC was connected to 120VAC relative to the third prong on the outlet that I had the scope plugged into.

So I am convinced that an electrician made some sort of wiring error when connecting the power to the table in the lab. Instead of being plugged into a wall outlet, the power to the lab table comes from a conduit that goes into the wall opening that serves two lab tables' power needs. A sticker on the conduit shows a wiring diagram indicating that the two connections are supposed to share the neutral wire, but one is connected to "hot1" - a red wire, and the other to "hot2" - a black wire. It also shows a green shared ground wire.

I apologize for the long setup to my actual question, but I am trying to understand what the wiring error could be to cause this situation. I am certain that the USB shield was at 120V relative to ground. Shouldn't the shield be connected to the computer case and therefore be grounded? How could it be at 120V potential then? If the electrician accidentally reversed hot and neutral, shouldn't plugging in the computer have blown a circuit breaker instead of making the shield be at 120V?

I am glad I did not get electrocuted. Now that the scare has worn off, my curiosity about what actual wiring mistake was made is rising. I hope my explanation is clear enough for someone to identify what is wrong. (By the way, I reported all of this to many people at school and an electrician will be brought in to correct things right away.)

Added: I hope I made it clear that I did indeed refer the actual work of correcting this hazard to an electrician the school will bring in. But I am very interested in understanding the error as well, so that I may simply increase my knowledge. I hope someone out there can help with that.

EDIT: WRONG--SEE BELOW "Today I got to school after the electrician had already corrected whatever the error was." I wish I had had the chance to ask what was the matter. I hope I can get more info from the people at school in the next few days or so.

I did use an ohmmeter to convince myself that the USB shield of the computer is indeed tied to the third prong of its power plug, so I am convinced that the entire metal chassis of the computer was hot last week.

I heard second hand that our maintenance people had used some sort of outlet tester on the circuit in the past and that it actually passed the test(!) How is that possible with such a serious fault as the ground being missing and what should have been grounded connected instead to 120VAC? Is there some sort of strange faulty connection scheme that a simple outlet tester would miss?

Since it seems that the job of rewiring the circuit didn't take very long (I got to school at 11 am and everything was fixed) I assume it wasn't something that took a lot of hunting to find. But I am still mystified. I'll add any additional info as I learn more...

IMPORTANT UPDATE: Yesterday I proved myself to be an idiot. What I thought indicated repair work was just evidence of our head maintenance man doing some more checking and turning the power off. I was simply measuring no more 120V on the computer case because the power was turned off. Bonehead.

Today the electrician is upstairs working the problem and finding some very strange stuff. Right now it's looking like the computers are correctly wired to the power, but the floor outlet has some issues between ground and neutral. He showed me how he gets a nice clean tone from his tester across ground and neutral on the computer supplies, but a sort of warbly tone between ground and neutral on the floor and wall outlets.

Also, our maintenance man was finding weird voltages like 36V and 23V on some of the computer power outlets during his experimentation yesterday. Thus the electrician visit today. All simple theories for this seem to be out the window. So it is getting more interesting by the minute ...

THE LATEST -- The instructor in the closest office told me that the guys were cheering success late this afternoon, but I wasn't there to get the answer. Dang. Maybe tomorrow. Whatever the issue was it had the electrician making phone calls for help and our school personnel doing a lot of head scratching all day.

MORE: Today I hear that they tracked down the culprit as the "modular whip in the furniture." Our head maintenance man says (and I saw) that the outlets to the PCs are held in trays in the lab tables, and each strip is sort of daisy chained together. I gather somewhere in the chain there were both open ground and open neutrals. He says he has lost all confidence in the power connection materials that came in the lab furniture.

I still don't understand how an outlet tester would not have detected these faults. Maybe it was just that the tester was only used originally when the strips were indeed healthy and then the fault occurred some time later. Any ideas on what would lead to these sorts of faults developing?

I found something here that fits a lot of the symptoms we discovered. He calls it "reverse polarity bootleg ground." Do you think this could be it? But how could this be a failure in an outlet strip? Wouldn't it still have to be in the building wiring?

http://ecmweb.com/contractor/failures-outlet-testing-exposed

ADDED: I just had a very nice phone conversation with Mike Sokol, the author of the above article. He says my accident sounds exactly like his RPBG scenario, and he also made me understand that the "warble" from the electrician's tone continuity tester is likely evidence of a good ground and neutral connection, while the "clean" tone is probably a sign that the ground and neutral lines are bootstrapped straight to each other, a code violation. I think the "warbly" sound is showing there is a voltage drop between ground and neutral, as there ought to be with a load connected. The electrician thought the exact opposite. Hmmm...

MORE RECENTLY: The people at school seem satisfied that the problem has been corrected. However, I'm told that the fix was simply that they unplugged something and plugged it back in(!). I checked things with a non-contact voltage tester and the computer case is now grounded. But I don't understand how simply reconnecting something could fix that. Maybe I did not understand the complete story, but I am still nervous that this situation could reoccur. I'm not satisfied quite yet ...

\$\endgroup\$
12
  • \$\begingroup\$ Did you check if the usb shield and pc case are at the same voltage? Is the pc case grounded or to what voltage from ground? \$\endgroup\$
    – berto
    Mar 14, 2016 at 4:16
  • 3
    \$\begingroup\$ Do you live in a country with 120 V or 230 V mains? In the latter case what you measured is a symptom of no protective earth on a product with a grounded chassis. The power supply has filter capacitors from the live and neutral to the ground for reducing electromagnetic interference. Without a proper ground, the filter caps act as a voltage divider, causing the entire PC to float at half of mains voltage. The low reactance of the caps at mains frequency does not allow significant current to flow. If you live in a 120 V country, the cause is different and the situation is dangerous. \$\endgroup\$
    – jms
    Mar 14, 2016 at 4:22
  • 3
    \$\begingroup\$ Of course a huge arc would disprove the capacitive divider hypothesis altogether. \$\endgroup\$
    – jms
    Mar 14, 2016 at 4:27
  • \$\begingroup\$ Is there an 'extra' GFCI anywhere in this wiring system? \$\endgroup\$
    – brhans
    Mar 14, 2016 at 12:35
  • 1
    \$\begingroup\$ Looks like you've got the answer. I think you out post that as an answer. Spehro had the right idea (ground hot) but not the cause. \$\endgroup\$
    – JRE
    Mar 17, 2016 at 13:01

4 Answers 4

11
\$\begingroup\$

Assuming the North American electrical system, the only error that the electrician could make that would cause that symptom would be to swap the GND and HOT wires. Swapping hot and neutral would not do it.

That's a very serious error- and quite negligent in not checking for it, if that indeed is the problem. It could easily cause someone to perish.

If it is the problem you will be able to measure 120V between what you call the third pin on the two outlets.

It's also possible, but unlikely, that a problem with the PC could cause this symptom.

Edit: as others have pointed out, the PC functions so it can't be a simple swap, in fact no single error can cause these described symptoms.

If the hot is connected to both gnd and where it should go.. For example if the hot shorted to the conduit and the conduit gnd was broken.

Looking forward to a follow up on what this was...

\$\endgroup\$
4
  • 1
    \$\begingroup\$ Would swapping Hot and Gnd allow the PC to function? \$\endgroup\$
    – Passerby
    Mar 14, 2016 at 4:31
  • 1
    \$\begingroup\$ Since the PC turned on, the line voltage would have to be connected to two of the three terminals of the outlet, and not just the ground. So, it could not be a simple swap. It's also possible (though unlikely) that the power cord was miswired. I would expect the PC to function (until connected with a cable to a properly grounded device). \$\endgroup\$
    – Pigrew
    Mar 14, 2016 at 7:26
  • \$\begingroup\$ Thank you for your insights. I am in Minnesota so this is a 120V system, but the wall "outlet" (not a standard outlet but two conduits coming out of an outlet-sized box) is using two "hot" wires, one for each. I think that means they are opposite phases. If I understood what I read just yesterday that allows the shared neutral to carry lower current when there are loads on both lines. Have I got this right? \$\endgroup\$
    – user55515
    Mar 14, 2016 at 11:58
  • 1
    \$\begingroup\$ The North American system can have two or three hot wires that are 240 (2 for residential) or 208VAC (3 for commercial) relative to each other. So if you measure between two hot wires on different circuits you could see 0 or 208 or 240 if residential, but I'm not seeing any way that could have an effect on the safety ground \$\endgroup\$ Mar 14, 2016 at 12:04
6
\$\begingroup\$

I can think of one possibility, but it's pretty scary.

If your conduits are indeed providing two separate hots, your PC is getting 240 volts AC. This is not, by itself an issue: lots of PC power supplies will handle 120/240 automatically. However (and this is where it gets scary) these supplies assume a hot/neutral input, with the neutral nominally at the same voltage as the ground. If I'm right, your entire PC electronics circuitry is sitting at 120 VAC, just waiting to bite somebody.

I recommend calling your electrician immediately, and if you don't get immediate response, go to your local hardware store on your lunch break and buy a 3-LED power tester for 10 bucks or whatever they go for.

There are two puzzling aspects of this: 1) why your display (assuming you have a detached monitor) has not smoked. Printers are often double-insulated, so they can float, but monitors are always (as far as I know) grounded. 2) Why hasn't the ground lead of your PC kicked up a fuss? Is it possible that the electrician never connected ground to the socket?

Basically, it seems likely that what has saved you is the fact that a modern PC does not require that you touch anything conductive.

I'm with Spehro: I can't wait to hear what really happened.

EDIT - The reason I find this pretty scary involves a personal experience you may find entertaining.

I was involved with a missile launch out of Wallops Island, and our payload included a bunch of low-sensitivity optical sensors. We tested these by shining a bright light on each sensor in turn. Just before launch, we mated the payload to the solid-fuel booster, and then ran a final test. Note that, while the booster did not have its ignition core installed, it was a perfectly functional skyrocket. We were using a standard work lamp to provide high-brightness light, and were partway through the test when the guy with the light let the guard framework touch the skin. He drew an arc. It was one of those Come-To-Jesus moments as, for an extraordinarily long instant, everybody waited to see if the booster would ignite. It didn't. To our credit, the guy with the light didn't drop it, and nobody actually soiled himself.

A post-mortem determined that the socket we'd plugged into had swapped neutral and ground, and the load in the building was unbalanced, so neutral had floated significantly from ground. As a safety precaution, of course, the bird was grounded, and so made a good return bath when connected to the nominally grounded (but actually connected to neutral) wire cage on the lamp.

So don't mess around with this.

\$\endgroup\$
6
  • 9
    \$\begingroup\$ Many 80+ rated PC power supplies have active PFC, and can handle universal AC input (85-264VAC, 47-63 Hz). I think you cannot achieve 80+ Gold or Platinum without active PFC. \$\endgroup\$ Mar 14, 2016 at 16:09
  • 2
    \$\begingroup\$ @passerby: i have just thrown away a few in January \$\endgroup\$
    – PlasmaHH
    Mar 14, 2016 at 18:03
  • 3
    \$\begingroup\$ +1 for handling a load that packs a wallop on Wallops Island, and the poor fellow who got walloped doing it. \$\endgroup\$
    – user39962
    Mar 15, 2016 at 1:42
  • 3
    \$\begingroup\$ Also, many monitors nowadays have a universal SMPS as well. \$\endgroup\$ Mar 16, 2016 at 1:15
  • 1
    \$\begingroup\$ "these supplies assume a hot/neutral input, with the neutral nominally at the same voltage as the ground." umm no. When designing a portable appliance one has to assume that the "neutral" input connection may in fact be live, otherwise you would have a big problem when someone tries to use your appliance in Germany. \$\endgroup\$ Sep 27, 2019 at 16:17
2
\$\begingroup\$

I heard second hand that our maintenance people had used some sort of outlet tester on the circuit in the past and that it actually passed the test(!) How is that possible with such a serious fault as the ground being missing and what should have been grounded connected instead to 120VAC? Is there some sort of strange faulty connection scheme that a simple outlet tester would miss?

Yes, the cheapest plug-in mains testers only test a very few of the simplest permutations of possible miswiring.

Here's a chart from a maker of such devices, note that there are many more permutations of fault conditions than there are permutations of three LED indicators.

enter image description here

Note 1 - EN reversal not detectable.
Note 2 - Investigation required by qualified electrician.
Note 3 - Caution! Investigate with care. Socket wire(s) may be live, but LED’s will not light. Investigation required by qualified electrician

You can buy Advanced and Professional versions of these socket testers which do distinguish between a greater variety of faults, but none of them can correctly distinguish between all possible miswiring errors.

The more advanced plug-in socket testers typically cost ten times the price of the cheapest ones. The more comprehensive ones measure earth loop impedance and can test RCDs/GFCIs.

enter image description here enter image description here


References

\$\endgroup\$
0
\$\begingroup\$

A low voltage (legal term for <1000 VAC) such as mains voltage in EU or US won't cause an especially long arc in comparison to the quite robust energy supply at 12 VDC of the PC power supply. In either case you would have had to start the arc by at least almost making a contact >1 mm distance and then extending the arc by pulling the probe away.

Many modern devices are designed to operate in the EU and US 110/230 VAC systems, so they might react differently in the case of mains - mains fault in a socket. That would explain why some devices continue to operate, while some fail.

Some lab tables have their own RCD and have therefore their ground "prong" connected to the zero-lead. I'm sure that wouldn't be legal anymore, but they were designed to be operated with an isolated source, as many electronics labs still do have. They are just as safe as long as they have their internal RCD operational and don't have a plug that might be connected the wrong way around into a non-isolated source.

As a conclusion I do believe your measurements were correct, but what would have happened with any load. Might have just been a disconnected ground, with the voltage showing through a power supply filter arrangement and nothing to do with the arcing or burned components.

\$\endgroup\$
1
  • \$\begingroup\$ I do realize this is an old topic, but was tempted to answer anyway \$\endgroup\$
    – Ralph
    Feb 25, 2022 at 21:46