Here is the link to the emergency stop switch - http://www.ebay.com/itm/NC-N-C-Emergency-Stop-Switch-Push-Button-Mushroom-Push-Button-4Screw-Terminal-K2-/272048010923?hash=item3f575336ab. Thanks.

\$\endgroup\$

closed as too broad by Bimpelrekkie, Daniel Grillo, Dave Tweed May 4 '16 at 14:51

Please edit the question to limit it to a specific problem with enough detail to identify an adequate answer. Avoid asking multiple distinct questions at once. See the How to Ask page for help clarifying this question. If this question can be reworded to fit the rules in the help center, please edit the question.

  • \$\begingroup\$ It's CE marked hence should have full documentation i.e. a data sheet. Do some digging. \$\endgroup\$ – Andy aka May 4 '16 at 7:14
1
\$\begingroup\$

No.

The switch is rated for 10A. 4500W @ 220V is about 20.5A, double the maximum rated current.

\$\endgroup\$
1
\$\begingroup\$

The purpose of this switch is to turn on/off the safety relay. If you do not intend to use safety relay, than use at least a normal contactor/relay.