I need a little help determining what I need in order to measure frequency from an Encoder containing the attached Open Collector Output. The 5 Volts will actually be 24 Volts in my scenario (this is just the datasheet).
The device reading the output will be a NI cDAQ DI 24V Sinking Module. According to the datasheet, the minimum "ON" Current and Voltage is 3mA/11V. My thoughts are that I need an External Pull-Up resistor for wire Z and just read the period to get the Frequency. From what I've read, I'll need 3939 Ohms to do what I want.
I_en = 3mA; I_lkg = 30mA; I_pullup = I_en + I_lkg = 33mA V_out = 24V; V_IH = 11V; R_pullup = (V_out - V_IH)/I_pullup = 3939 ohms.
Am I doing this right or am I completely off and not understanding this at all?enter image description here
  • \$\begingroup\$ What's the maximum voltage on the open-collector outputs? How about a datasheet link for your encoder? \$\endgroup\$
    – DoxyLover
    Jun 14, 2016 at 19:55
  • \$\begingroup\$ 24 V for Open Collectors. But yeah, here's a datasheet. cui.com/product/resource/mes30.pdf \$\endgroup\$
    – D4ILYD0SE
    Jun 14, 2016 at 19:58
  • \$\begingroup\$ What device are you interfacing the encoder to and why does it require 24V? \$\endgroup\$ Jun 14, 2016 at 20:34
  • \$\begingroup\$ "The device reading the output will be a NI cDAQ DI 24V Sinking Module" This module can range from 11-30 V Input. The reason for 24V is because I'm trying to limit the need for more power supplies. \$\endgroup\$
    – D4ILYD0SE
    Jun 14, 2016 at 20:44
Figure 1. Likely schematic for one channel of encoder with current sinking NPN transistor output driving PLC with current sinking input. The buffer would likely be a Schmitt trigger to prevent chatter on transition.
As you have correctly alluded to in your question, the problem is that you are using a current sinking output to drive a current sinking input. The best way to do this would be to use a converter unit or industrial opto-isolator but your method is not uncommon.
R4 value
The PLC is guaranteed to turn on at 3 mA / 11 V on the input. Let's give it 12 V to make the maths easier. R4 then has to drop 12 V at 3 mA. \$R = \frac {V}{I} = \frac {12}{3m} = 4~k\Omega \$. The next lower value is 3k9.
Q2 current
Now check the max current through the encoder transistor shown as 30 mA max. When Q2 is on R4 will be have 24 V across it. \$ I_{max} = \frac {V}{R} = \frac {24}{4k} = 6~mA \$. We're fine. In fact we could decrease R4 to 3k3 for extra PLC margin if we wanted.
R4 power dissipation
Finally check the power rating of R4. Worst case will be if the encoder stops with Q2 on. \$ P = VI = 24 \cdot 6m = 150~mW \$. A 1/4 W resistor would suffice.
Your final result for the resistor value was correct - although your calculations are a little difficult to read.
[From comment:] And just one other thing. In your diagram you have 5V Input. Although, yes, the circuit I have for my encoder says 5V, I am told that 24V there is acceptable. Would you agree?
The datasheet says, "5 ~ 12 V dc ± 10%, 24 V dc ± 10% (open collector output only)." I would read that as the 5 V power input could take up to 12 V (remember it's powering the LED and the logic so the max voltage is limited and a 5 to 12 V range suggests CMOS chips). The open-collector output is probably good to 50 V but the manufacturer has de-rated it to 24 V as it's a normal industrial supply.
So where are you going to get 5 to 12 V DC in your panel. Again, the right thing to do is get a small PSU but we may be able to cheat again. Looking at my "likely circuit" we can guess that the LED is going to account for the majority of the current. (The current through the open-collector transistor, Q2, doesn't affect the current drawn at the 5 V input.)
Let's take some measurements. If you have an adjustable bench power supply use that. If not get whatever you can - 5 V USB charger, 9 V battery, etc. and take some measurements. Connect the common to negative and +5 V to positive via your multimeter on 200 mA range. Measure and record the current in each case while turning the encoder, looking for changes in readings as segments turn on and off. (I wouldn't expect any changes.)
Let's say it takes 25 mA at 5 V and 35 mA at 9 V. We could use a simple Zener regulator to supply the correct voltage.
Figure 2. Simple Zener regulator.
We'll set this up so that the encoder is powered with 9 V and the Zener is barely conducting so that its power dissipation is kept to a minimum.
\$ R = \frac {V}{I} = \frac {24-9}{35m} = \frac {15}{35m} = 430~\Omega \$.
Now check what happens if the encoder gets disconnected. We'll have 9 V across the Zener and 15 across the resistor. \$ I = \frac {V}{R} = \frac {15}{430} = 34~mA \$. This current will run through the Zener so the power dissipated in it will be \$ P = VI = 9 \cdot 34m = 306~mW \$. A Zener rated at 0.5 W should be fine and will run very cool if the encoder remains connected and draws steady current.
  • \$\begingroup\$ This was amazingly helpful! Thank you. And just one other thing. In your diagram you have 5V Input. Although, yes, the circuit I have for my encoder says 5V, I am told that 24V there is acceptable. Would you agree? \$\endgroup\$
    – D4ILYD0SE
    Jun 14, 2016 at 21:38
  • \$\begingroup\$ No, I think 24 V would destroy the electronics. See the update. Thanks for accepting this answer. \$\endgroup\$
    – Transistor
    Jun 15, 2016 at 4:51
  • \$\begingroup\$ I've got one more question for you. Because I'm using two separate Power Supplies for this, in order to make sure it works, do I have to wire the V- of both the 12V and 24V Supply together? \$\endgroup\$
    – D4ILYD0SE
    Jun 16, 2016 at 2:33
  • \$\begingroup\$ Correct. That will provide a common reference for both circuits. I'll add it to the schematic. Thanks. \$\endgroup\$
    – Transistor
    Jun 16, 2016 at 7:28