On my balcony I have a satellite dish and two coaxial cables attached to it. I don't use that dish, and I want to remove it and reuse those coaxial cables to power some other device on the balcony (a kind of IoT stuff).

Can I send DC power over that coaxial cable? If yes, then can I use a single cable and its centre wire as positive and outer wire mesh and foil as ground?

EDIT: my dish has LNB sign on it if it matters: enter image description here

\$\endgroup\$
1
  • \$\begingroup\$ Would you care to mark one of the answers as accepted? You have several that explain things clearly. \$\endgroup\$
    – JRE
    Jun 17, 2017 at 17:40

3 Answers 3

16
\$\begingroup\$

Yes, this should work fine. Even in its original application, the coax was probably carrying a DC bias to power the LNB on the satellite dish.

Assuming it's RG-6 cable, it should be good for at least 3 amps.

It's considered conventional to use the shield as ground and the core as +V, though it doesn't particularly matter from a functional point of view.

\$\endgroup\$
9
  • \$\begingroup\$ Typical resistance per foot for rg 6? \$\endgroup\$
    – Passerby
    Sep 16, 2016 at 16:52
  • 2
    \$\begingroup\$ Consult the data sheet/specification for the actual thing you have. Don't assume that someone on the internet knows what it is. Also it would probably be nice to confirm keeping the shield as ground. \$\endgroup\$
    – user117772
    Sep 16, 2016 at 17:17
  • \$\begingroup\$ "Also it would probably be nice to confirm keeping the shield as ground" So do you think using 2nd cable center wire as ground is better? \$\endgroup\$ Sep 16, 2016 at 17:55
  • \$\begingroup\$ @MarianPaździoch Yes. I think it is expected to use the shield as ground unless you have a good reason. \$\endgroup\$
    – user117772
    Sep 16, 2016 at 18:24
  • 1
    \$\begingroup\$ @roses assuming you could find the datasheet for some random run of unmarked coax cable... it's typical to use typical numbers for standard cable. AWG reference guides are used all the time. \$\endgroup\$
    – Passerby
    Sep 16, 2016 at 21:11
12
\$\begingroup\$

RG-6 coax has a 18-gauge center conductor, and exhibits a resistance of 6.385mOhm per foot. Its insulation is suitable for a max of around 10A, but it may get too hot before that. Typical satellite TV operates at voltages between 13v and 18v. At 18v, a 200ft long RG6 will allow up to ~14A. However at 10A, the voltage drop is about 7.8v, so your mileage will vary.

So, yes, it is entirely suitable to carry power. That is after all what it does in a satellite TV setup. The set-top box powers the LNB through the coax.

\$\endgroup\$
6
\$\begingroup\$

Yes, you can. In fact, using coaxial cables to deliver power to small-scale electronics is a common engineering practice, with all corresponding approvals (EA, UL, etc). You can combine DC on coax even with AC signal transmission if you need. All TV cable amplifiers (usually located on attic) use this method of delivering DC over a single coax cable.

Using outer shield of coax cable as negative end of supply makes a lot of practical sense since it is frequently exposed at connectors and junction boxes, and it is advisable to maintain it as common ground.

\$\endgroup\$
5
  • 17
    \$\begingroup\$ Please note that anything standing outside with a cable running inside should be earth-grounded. You don't want lightning to follow the cable inside. \$\endgroup\$ Sep 16, 2016 at 18:57
  • 3
    \$\begingroup\$ @DrunkenCodeMonkey wished I could +1M on that comment. People forget that a conductive wire running outside to inside is a perfect opportunity for lightning to "pay you a visit inside". \$\endgroup\$
    – cbmeeks
    Sep 16, 2016 at 20:26
  • 1
    \$\begingroup\$ Practically speaking how does one ensure that something standing outside with a cable running inside is indeed "Earth-grounded"? \$\endgroup\$
    – Keegan Jay
    Mar 24, 2017 at 4:09
  • 1
    \$\begingroup\$ @JayKeegan, I believe that in accord with any reasonable building code, coax cables (say RG-59 for cable TV) are connected via F-F couplers that are attached to earth ground, like this one, computercablestore.com/grounding-block-single-f-type \$\endgroup\$ Mar 24, 2017 at 6:14
  • \$\begingroup\$ In addition to the F-F coupler it's a good idea to ensure the antenna frame is also connected to earth. Run a thick copper wire from the coupler and antenna to a metal rod planted at least a few feet in the ground. Or run the wire the shortest route possible to a metal structure that is already grounded. \$\endgroup\$ May 14, 2017 at 4:30