Is there a benefit to the utility company, or potentially to me, for balancing the loads across the two 120V legs in my mains power? this About page suggests some benefit, though the explanation seems suspect. I understand that, on my end, whether I am drawing 100A on one 120V leg, or 50A across both 120V legs, I am still going to be paying for 12kW.

Given that, does balancing the loads have any impact? I don't know quite enough about center-tapped transformers to say how the center tap affects transformer performance on either the high- or low-side.

\$\endgroup\$
2
  • 1
    \$\begingroup\$ Either way they're both on the same phase, it makes no difference upstream of your supply transformer. \$\endgroup\$ Jan 9, 2017 at 5:48
  • \$\begingroup\$ In the edge case of only one leg being used, I wasn't sure if the transformer simply acted as if it were a non-center tapped transformer or not. That's why I wasn't sure how it changed how the upstream portion behaved. \$\endgroup\$
    – Hari
    Jan 9, 2017 at 6:54

2 Answers 2

1
\$\begingroup\$

We have to look at an example including the cables resistance. I assume 0.05 Ω for both legs. If the load is 100 A for one leg only, the voltage drop at the cable is 5 V and we loose 500 W in the cable. If the load is 50 A for one leg only, we get a drop of 2.5 V and a cable loss of 125 W. If both legs are loaded with 50 A each, the loss in the cables is 250 W only. But we have to pay for all power what is used after the companys power meter. In both cases we pay for 12 kW, but we can use 11.5 kW with unbalanced load and 11.75 kW with balanced load.

But the cables between the center tapped transformer and the secondary windings of the transformer have a resistance too. The same is true for those, the balanced loss is smaller than the unbalanced one. If the power company installed a power meter with extra charges for unbalanced loads, you pay a little more money for the unbalanced 12 kW load. But a suitable extra charge is not unfair, without it the customers with better balanced loads have to pay for the losses caused by customers with unbalanced loads.

If there is one single large load like a washing machine, it is better to use a machine for 240 V and 10 A instead of one with 120 V and 20 A. A loads using 240 V will be balanced by itself.

\$\endgroup\$
1
\$\begingroup\$

Given that line voltage regulation is designed to be 5% p.u. for all of distribution, it improves the voltage regulation for loads to be balanced. This also balances thermal rise in 3 phase cores and reduces aging from elevate temperatures due to unbalanced loads. Surge currents cause further disruption of neutral shift from 10x surge currents of loads are not balanced in industrial loads that may cause over voltage on under loaded phases using single phase voltage during surges on the other two phases during startup. This may trip the breaker but can easily also damage large power supplies .

For the consumer, unbalanced loads or operating breakers near the limit may cause more rapid aging and premature failure. Otherwise a Watt used is a Watt charged regardless of which line of a split phase power meter it comes from.