I have a single machine connected to an infinite bus with the following parameters:
  • Sending end power = 3.75MW
  • RL=5.18 ohms
  • XL=130 ohms
  • VS (Generator bus)=161kV
  • VR (Infinite bus)=161kV
  • Sending end voltage angle (delta) = 0.01877 (Angle which allows 3.75MW to be transferred)
Using these I want to calculate the amount of reactive power sent by the sending end as well.
I calculated it first without factoring in the line resistance (RL=0) Then got the result for Q as : 35.24kVAR
Next I calculated it with the line resistance factored in Then got the result for Q as: -114.77kVAR
When the line resistance is factored in, the answers for reactive power vary immensely. And when the resistance is factored in, the sign of Q is negative indicating the generator bus is absorbing VARS which doesn't seem to make sense.
Why are they so different? What am I doing wrong?
The equations I used are here
I derived these equations using Matlab to do the algebra, so it hopefully should be correct :)
  • \$\begingroup\$ perhaps your assumptions are wrong. You must conjugate match the impedance by phase shift but also add voltage for line R loss. try adding V²/W voltage to Vs and adjust phase lead to 0.538 degrees (using power per phase not total) \$\endgroup\$ – Tony Stewart Sunnyskyguy EE75 Jun 22 '17 at 2:49
  • \$\begingroup\$ Thanks for the response Tony. I didn't get what you meant by "conjugate match the impedance by phase shift"? and how did you calculate 0.538rads and why do i need to adjust it by this much? \$\endgroup\$ – CKCK Jun 22 '17 at 3:46
  • \$\begingroup\$ www.ece.rutgers.edu/~orfanidi/ewa/ch13.pdf I said degrees \$\endgroup\$ – Tony Stewart Sunnyskyguy EE75 Jun 22 '17 at 3:52
  • \$\begingroup\$ Apologies i misread. Ill have a look at that link. Thanks \$\endgroup\$ – CKCK Jun 22 '17 at 4:01
  • \$\begingroup\$ did u not understand the voltage loss part? Conjugates use easy vector match with opposite reactance which is your phase with R +jX \$\endgroup\$ – Tony Stewart Sunnyskyguy EE75 Jun 22 '17 at 4:05