[UPDATE The problem is fixed and the results are in my answer below]

I have designed a board with, among other things, six max31865 on it. From those six I use five of them. The device reads out the temperature of five domes and if the temperature is to low or to high it sends an alarm sms via a gsm module.

Here some knogledge about the device:

  • I use five 2-wire NI1000 RTD elements (like PT1000 just not as accurate)
  • The probes are connected via 2-wire connection and each of them have their own max31865
  • Every probe is connected via extension cable of minimum 20 meters
  • The Domes where the sensors are in can have up to 90% air humidity
  • the farthest probe is 100 meters away from the device
  • Every 5 seconds I read out a different probes. 4 seconds before I initiate the conversion VBias is turned on. After the conversion I shut down VBias.

Now to the problem:

Four of the sensors I can read out without a problem. But if I connect probe 5 which is the farthest away from the device among the other four probes the max31865 from probe 5 spits out a over/undervoltage fault (fault D2). But if i connect only probe 5, the max31865 gives back valid temperature data. The conversion also works if I connect a probe next to probe 5, which is directly connected to the board (without extension cable).
The fault means that the voltage on any input pin of the max31865 is >VDD or

I changed the timing of "VBias ON -> Conversion, VBias off -> VBias ON" and I tried to let VBias always on but it didn't work.

How can it be that this over/undervoltage fault only occurs constant when sensor 5 is connected? (without probe 5 the error sometimes occurs with another probe but not that much) Is it possible that the extension cable of the sensor is inducing so much noise that it can cause any protected pin to have a negative voltage or have a voltage greater than vdd?

Thanks in advance!

The schematic of the sensor: enter image description here

\$\endgroup\$
  • \$\begingroup\$ Can you provide a schematic? \$\endgroup\$ – whatsisname Jul 13 '17 at 6:09
  • \$\begingroup\$ have you measured the voltage or are you just relying on the error code? \$\endgroup\$ – Solar Mike Jul 13 '17 at 6:11
  • \$\begingroup\$ Shielded cable? \$\endgroup\$ – Jeroen3 Jul 13 '17 at 6:16
  • \$\begingroup\$ I measured the voltage on the pins at RTD+ and RTD-. On Sensor 5 the voltage on both pins are higher than on the other Sensors. (RTD- 0.1V instead of 0.05V and RTD+ 0.48V instead of 0.44V) If VBias is not applied the voltage on those pins are changing in the 100mV range. The other Sensors show 0V. \$\endgroup\$ – ruemi Jul 13 '17 at 6:22
  • 1
    \$\begingroup\$ I would suspect the total capacitance of the cables; it may be interfering with the communications. The amount of cable hanging on the communication port is quite high. \$\endgroup\$ – Peter Smith Jul 13 '17 at 12:01
3
\$\begingroup\$

It's difficult to fully understand your RTD cabling, since you've mentioned "Two of them have a multi-core and the other three have a single core", yet you would need at least two wires to connect to each RTD, so using a single core (wire) seems impossible!

[Update - Above original wiring now clarified in later comment to have been: Two sensors using cables with stranded wires, and the other three sensors using cables with solid core wires.]

However, some of the other information suggests the answer to your original question could be "yes". Noise induced in the sensor 5 cable (from external sources) seems to fit with information presented so far, and being the longest cable, it's not a surprise that this sensor would be more affected than the other sensors, which have shorter cables.

the cables are unshielded

Use of long unshielded cables for RTDs is a concern, especially if external sources of electrical noise are present. You've also explained that the affected sensor is the one with the longest cable (150m). That's an interesting correlation. Shielded, twisted conductor (2, 3 or 4 wires) is a common cable type for long RTD cables, with the shield grounded at one end (typically the "measuring end") only.

The use of only 2-wire connections to the RTDs, especially with long cables, will affect the accuracy of the measurements, although that might not be important to you.

The cable of the probe 5 runs in parallel with different cables in a cable channel and at one spot it crosses a wireless router.

Again, it's an interesting correlation between that long cable run, close to other cables (potential "radiators") and the wireless router (a definite radiator) and the affected sensor. That is especially interesting if the cables to the other sensors, are further away from potential and actual EM radiators.

On Sensor 5 the voltage on both pins are higher than on the other Sensors. (RTD- 0.1V instead of 0.05V and RTD+ 0.48V instead of 0.44V) If VBias is not applied the voltage on those pins are changing in the 100mV range. The other Sensors show 0V.

That is interesting. The difference between the sensor 5 measurements and those from other sensors, is telling you something. If you can do more work to understand the specific differences, and what changes them (i.e. what makes those differences increase or decrease), you can extract more value from that difference.

This is an example of the type of difference which can form part of the tests, comparing the measurements between "good" and "bad" configurations which I mentioned in earlier comments (if you are experienced with that type of troubleshooting approach - but you might prefer to follow a different approach of your own).

I assume those voltage measurements you listed were made with a DMM. I would use a 'scope and look at the voltages on those sensor 5 signals, and use that to try to find the cause e.g.:

  • What is the waveform shape? Does the magnitude match what you measured with the DMM or is it different (perhaps larger)?
  • Is there more AC ripple at 50Hz/60Hz (whatever the mains frequency is at the affected site) on the sensor 5 cables, compared to the cables from other sensors?
  • Are the cables which are parallel to the sensor 5 cable, carrying mains power, or low voltage signals, or something else? Can you match that answer to whatever induced voltage waveform you see on the sensor 5 cable?
  • Is the waveform shape and magnitude of the externally induced voltage on the sensor 5 cable, different from that on the cables to other sensors? Anything unusual, considering cable length and routing for each cable?
  • Can you temporarily switch off the wireless router close to the cable for sensor 5, and see whether the faults reported by its MAX31865 stop or are reduced?

Also ensure that you have selected the correct "notch frequency" (50Hz or 60Hz - whatever is the local mains frequency) in the configuration of the MAX31865, so that it has the best chance of ignoring induced voltage at that frequency.

How can it be that this over/undervoltage fault only occurs constant when sensor 5 is connected? (without probe 5 the error sometimes occurs with another probe but not that much)
[...]
The "funny" thing is that I can read the probe without a problem if it is connected alone. But as soon as I connect the others (not even measuring just connecting the other probes) it generates a error.

I suggest you look for differences in any measurement, between the different cases. If nothing changes (between different test cases) to cause different voltages to be externally induced in the sensor wiring to other sensors, then the "better" behaviour when only sensor 5 is attached may suggest an additional problem.

One hypothesis which might start to explain that, could be that externally induced voltages from all sensors are fed back to the "controller" (i.e. MAX31865 devices) and have some sort of cumulative effect there. This could explain why connecting sensor 5 on its own is not enough to cause errors to be reported ("only" 150m of cable attached); whereas when all sensors are attached (e.g. 250-300m [my guess] of cable attached in total, spread over 5 channels) this has a worse effect on the MAX31865 devices, enough for errors to be reported. This is why I suggested (in a comment) looking at the Vcc supplies for the MAX31865 devices - that's just an initial place to start looking; look for any measureable differences at the "controller board", when different numbers of sensors are connected.

That data point of when only sensor 5 is attached you don't get errors, is telling you something, but I'm not sure exactly what it means with the data given so far. Either gathering additional data and finding anomalies, or performing substitution tests (e.g. changing the cable type) and getting different results, will help.

I wasn't joking when I suggested making a diagram of the physical layout of the sensor wiring and potential interference sources. That may help you to understand the timing of when the MAX31865 reports errors, e.g. if that correlates with the operation times of specific interference sources.

It seems possible that the only way to resolve these errors, may be to rewire with suitable shielded, twisted conductor cabling. Depending on your budget, time pressures, availability of suitable shielded cabling etc., one option is that you could choose to take a risk, postpone additional investigation at this stage, and perform some testing with equivalent lengths of that different cable, laid temporarily in the same position as the existing sensor 5 cable. Get some measurements with the 'scope and see if there is an improvement in the magnitude of the induced voltage and, of course, see if you still get errors from the MAX31865.

Inevitably that approach has risks e.g. it might be a waste of time/money, but it would allow you to gather useful measurements, to see if the shielded, twisted conductor cable helped at all.

One final thought: The hypothesis is that your system is suffering from externally induced voltages, especially on sensor 5. When that voltage is large enough, it triggers the fault detection in the MAX31865 to set bit D2 in the Fault Status Register. However perhaps that induced voltage would not always be large enough to trigger the fault detection, and instead it might only cause erroneous temperature readings. It would be interesting if you are seeing unexpected intermittent high or low readings (especially on sensor 5, but the other sensors too), as well as the actual faults reported by the MAX31865.

I hope that review of the information, suggestions for additional data gathering and hypotheses to consider, are helpful. However getting a conclusive answer to your question, will require more work.

\$\endgroup\$
  • 1
    \$\begingroup\$ For the used cables I meant that it is a cable with two wires in it, each with a size of 1.5mm2. Two of the extension cables have stranded wires the other three have solid wires in it. Thank you for all your help. It helped a lot! \$\endgroup\$ – ruemi Jul 15 '17 at 16:53
  • \$\begingroup\$ @ruemi - I'm glad I could help :-) I've updated my answer to clarify the details about the wiring which you have given. I don't believe the difference between stranded & single-core wiring will affect the signals significantly, if that was the only difference between the cables. \$\endgroup\$ – SamGibson Jul 15 '17 at 17:32
1
\$\begingroup\$

Thanks to SamGibson I could narrow down the problem. I tried to eliminate the possible radiation devices. It changed a bit but not enough. After quite a bit of measuring I decided to exchange the cable. We luckily had enough Cat.6 ethernet cable in house and I did some tests with the hole spool. The results were promising so we replaced the old cable. The results are very good (in comparison to the old cable). Here are some results:

On the left is probe 5 without any other probe connected. On the right is probe 5 with the other probes connected. Both measured on RTD+: enter image description here

On the left is a probe with a closer distance to the device with a unshielded cable. On the right is probe 5 with the shielded cable. Both with the other probes connected and measured on RTD+: enter image description here

The result is that probe 5 with the shielded cable is as good as the sensor that is at about 80m with the unshielded cable. As it changed so much for this sensor I might also change the other cables.

It would be interesting if you are seeing unexpected intermittent high or low readings (especially on sensor 5, but the other sensors too), as well as the actual faults reported by the MAX31865.

I do see a deviation on the temperature measurements up to 0.8°C. I guess if I change the other cables it would reduce the amount of noise significantly. The fault of the max31865 disappeared nearly completely.

\$\endgroup\$