A possible electrical/wiring problem rather than a core electronics problem; please feel free to vote to close.

I just noticed that the neutral pin, and live pin in all the 3-pin sockets in this building test live. This was not the case a few months ago. To test the status of the pins I used a continuity tester

Attaching a load (1kw well pump) to the socket did not cause damage to the motor, but the motor did not power-on either.

  • Does this indicate a possible short between the live/neutral wires?
  • If this does indicate a short, how could supply possibly continue? I know from painful first-hand experience that shorting neutral+live is a sure way to blow a fuse and disrupt supply.

Edit/Update: OK ... this is weird. Following Russell's recommendation I applied a test-probe

Below are the results from applying the probe

Pins connected  Probe Lighted

PN              No

PE              No

NE              No

I then applied a lead to an iron angle support for a tin-sheet; that worked. Does this mean there is an Earth fault someplace, and I have to ouch rip out the wiring?

\$\endgroup\$
2
  • 1
    \$\begingroup\$ Can you elaborate on "test live"? What does that mean? Also, there is only one neutral. The third prong is ground, not neutral. When measuring a socket with a multimeter, there should be an AC voltage between ground and hot, and between neutral and hot, but not between neutral and ground. \$\endgroup\$
    – Kaz
    Commented May 18, 2012 at 4:30
  • 1
    \$\begingroup\$ Use a light bulb and two SAFELY INSULATED probes - it's a loaded tester with only two connections. Pump may be wired P-E and would still work in most locations. Building may have P & N swapped and most loads will still work. BUT pump wired as above will work elsewhere but not in this building. SO light bulb tester with two probes allows detailed investigation as per my answer. \$\endgroup\$
    – Russell McMahon
    Commented May 18, 2012 at 5:26

3 Answers 3

2
\$\begingroup\$

Be careful! Death is easy to come by in such situations!

You need to say what you are testing with.
You need to say what you are measuring relative to.

If any equipment works when plugged in the pump is faulty or unsuitable for testing with.
If nothing works then something is broken.

If P & N are connected correctly and shorted the a fuse or equivalent will blow.

Measuring a floating conductor with a high impedance input meter may show high voltages due to capacitive coupling.

Make a test unit: Mains voltage light bulb with two probes.
Test PN PE NE If PE and NE light N is connected to P.
If PE lights and NE doesn't and PN doesn't then P OK but N O/C.

If no light from any = major problems.

If no light as above, connect a long lead to outside ground. If any light from P/N/E to outside ground = problems.

You need to establish what voltages are genuinely present that can provide power - not just an O/C meter reading. Draw a diagram and show what does and doesn't light light bulb.Meter alone can fool you if unloaded.

\$\endgroup\$
1
  • \$\begingroup\$ I'll check it out immediately, and update the details into the question. \$\endgroup\$
    – Everyone
    Commented May 18, 2012 at 5:11
1
\$\begingroup\$

The tester you link to is a continuity tester, not a voltage tester. It states that "NB Not suitable for direct connection with live circuitry". I do not think any results you obtain with this are valid - you need better tools. If it behaves as the voltage test screwdrivers, it doesn't enable you to measure the potential between two chosen points, only between yourself and a point.

I understand that the motor doesn't run, which indicates an issue, but it may be hard to work out what that is.

The most common fault for seeing a voltage on neutral is a broken neutral. Capacitive coupling, combined with the high input impedance (MOhms) for most meters results in voltage showing. This will generally not be constant and will visibly change once the meter is connected. These are often termed "stray" or "ghost" voltages. Fluke has some information on this. The solution is to present a low impedance load in the range of kOhms. Some multimeters have this built in as a Lo-Z (Z for impedance) function - the Fluke 289 and 117 are ones that do.

Russell's lightbulb tester is essentially performing the same task - it draws current to light the bulb so won't respond to stray voltages.

A broken neutral would also stop the motor running - this is the first thing I would check.

Have you checked if any other appliances work in these sockets?

UPDATE - based on the lightbulb tester not lighting across any pair, but lighting between phase and an arbitrary earthed point, it sounds like both earth and neutral may be disconnected. This is an uncommon fault across an entire building in Europe as nearly all buildings use a TN-S earthing system where neutral and earth are delivered as discrete conductors from the substation. It may be that TN-C or TN-C-S is used in your area, where a fault in the cable supplying the building can easily break both neutral and earth. Refer to the wikipedia page on earthing systems to see diagrams.

Of course, neutral may be floating and there might not be any earth connected at all - stranger things have happened.

For diagnosing mains issues around the home, I always recommend two pieces of test equipment. Your profile says India, and I am not familiar with availability of test equipment there, but in the UK:

  1. A simple voltage only tester such as a Fluke T50, which costs approximately £25. These only measure voltage and are very safe as a result. I have seen several incidents now where over-enthusiastic DIYers have either tried to "see if 13A was coming from the socket" or left the probes in current mistakenly. You can diagnose most common issues without needing to measure current.
  2. A socket tester - these detect a number of conditions such as phase/neutral swapped, earth missing etc. Very quick and easy to use.
\$\endgroup\$
1
  • \$\begingroup\$ No appliances seem to work. A single-element room-heater, and a pocket soldering iron (25W) failed to show any sign of life. The soldering iron worked earlier though. Thanks a tonne for the link to the voltage, and socket tester. Such instruments though are usually sold at a premium here - and probably not available in my city; I'll check with a few retailers over the weekend. \$\endgroup\$
    – Everyone
    Commented May 18, 2012 at 6:06
0
\$\begingroup\$

If hot shows a current, then neutral must show exactly the same current, otherwise you have a ground fault.

Fuses/breakers detect overcurrent, not ground faults. Ground fault circuit interrupts (GFCI's) detect a current mismatch.

Although your pump is rated at only 1000W (less than a typical hair dryer), it may have a high inrush current at the moment when it is turned on.

Is it possible that the pump is seized inside? Is there a manual way to crank it?

\$\endgroup\$
2
  • \$\begingroup\$ The pump is not seized; it works elsewhere. The only place it does not work is at any points in the building where this is the problem. \$\endgroup\$
    – Everyone
    Commented May 18, 2012 at 5:10
  • \$\begingroup\$ When he says "shows a current" I believe he really means "both show mains VOLTAGE when tested against ???" \$\endgroup\$
    – Russell McMahon
    Commented May 18, 2012 at 5:29