Let's say I've a \$3\times450\$ VAC \$60\$ Hz \$1150\$ kVA generator. How much current will there be generated when it runs at maximum capacity?


MY WORK:

The total Active power over a three-fase system is given by:

$$P=\sqrt{3}UI\cos\varphi\tag1$$

Where \$U\$ is the line voltage and \$I\$ is the line current.

The total Reactive power is given by:

$$Q=\sqrt{3}UI\sin\varphi\tag2$$

Where \$U\$ is the line voltage and \$I\$ is the line current.

The total Complex power is given by:

$$S=\sqrt{3}UI\tag3$$

Where \$U\$ is the line voltage and \$I\$ is the line current.

So, I know that:

$$1150\times1000=\sqrt{3}UI\tag3$$

But what is the line voltage? Is it \$450\$ volts? So, then we get: \$1150\times1000=\sqrt{3}\times450I\$ which give that the line current equals \$I=\frac{1150\times1000}{\sqrt{3}\times450}\approx1475.5\$ A.

\$\endgroup\$
7
  • \$\begingroup\$ Huh, what? "Well, also that is not possible, because I get 3740 A and that current is two times bigger than the fuse that is used!" What fuse? Is this real or homework? \$\endgroup\$
    – Tyler
    Commented Dec 24, 2017 at 18:10
  • \$\begingroup\$ @Tyler It is a real schematic for a project I'm working on \$\endgroup\$
    – asdasdw
    Commented Dec 24, 2017 at 18:10
  • \$\begingroup\$ The fuse does not need to be sized for the maximum that the system can produce. \$\endgroup\$
    – Tyler
    Commented Dec 24, 2017 at 18:26
  • 2
    \$\begingroup\$ Anyone messing around with MW power levels shouldn't have to ask here. Conversely, anyone asking here shouldn't be messing with MW power levels. \$\endgroup\$ Commented Dec 25, 2017 at 14:32
  • \$\begingroup\$ If 450 VAC is the line-to-line rms voltage (which is the usual convention) then the phase current rms is 1475 A. \$\endgroup\$
    – UweD
    Commented Jul 2, 2020 at 6:45

2 Answers 2

1
\$\begingroup\$

Power engineers always use line-to-line rms when describing the voltage rating of three phase equipment.

So, in your case that is 450 V rms line-to-line. Your answer is correct (1,475 A).

\$\endgroup\$
-1
\$\begingroup\$

There is a some information in this article of Wikipedia.

Let \$V\$ be the RMS voltage between each of the phases and the neutral, and \$V_p\$ be its amplitude: \$V_p = \sqrt{2}V\$.

Let \$U\$ be the RMS voltage between two phases, and \$U_p\$ be its amplitude:

\$U = \sqrt{3}V\$, \$U_p = \sqrt{2}U\$.

Finally, let \$P = 1150 kVA\$ be the apparent total power available from the generator: it is the sum of the powers of each dipole.

It is unclear in the question whose of these voltages is meant by 450V AC. I suppose here that that this is RMS voltage between the phases and the neutral, that is \$V\$: \$V = 450\$.

Next, the question of "how much current it runs" is ill-posed. A current flows through two terminals, but here there are 4 terminals. Is it the current flowing through the phase and the neutral? the current flowing through 2 phases (if connected), the total current flowing through the terminals in a balanced "Delta" configuration? or the total current flowing through the terminals in a balanced "Wye" configuration? This need be specified, because the answer is different in each case.

Assuming for example you demand the maximal current between two phases: Then

\$I_{max}\ (rms) = P / U\$, which is the value you have to use for your "fuse" between 2 phases. The maximum current amplitude is \$ \sqrt{2}P/U\$

If you demand the maximal current between a phase and the neutral, then \$I_{max}\ (rms) = P / V\$ and the maximum amplitude is \$\sqrt{2}P/V\$.

The other cases are processed similarly.

\$\endgroup\$
8
  • 1
    \$\begingroup\$ Well, this is not true. Because the voltage and current are always the RMS ones (not the maximum/amplitude). P is in Watt (W) not in VA. Since I only not the things (of the generator) that are listed in my first line of the question I can not use anything about the impedance. Next the current is big and can never be as low as \$3.74\$ A!!! \$\endgroup\$
    – asdasdw
    Commented Dec 24, 2017 at 17:26
  • \$\begingroup\$ Well, also that is not possible, because I get \$3740\$ A and that current is two times bigger than the fuse that is used! \$\endgroup\$
    – asdasdw
    Commented Dec 24, 2017 at 17:35
  • \$\begingroup\$ What is wrong, when I use the formula: $$\text{S}=\sqrt{3}\cdot\text{U}\cdot\text{I}$$ Where \$\text{U}\$ is the effective line voltage and \$\text{I}\$ is the effective line current? Or I can write $$\text{S}=\sqrt{3}\cdot\frac{\hat{\text{U}}}{\sqrt{2}}\cdot\frac{\hat{\text{I}}}{\sqrt{2}}=$$ $$\frac{\sqrt{3}}{2}\cdot\hat{\text{U}}\cdot\hat{\text{I}}$$ \$\endgroup\$
    – asdasdw
    Commented Dec 24, 2017 at 17:44
  • \$\begingroup\$ My book tells me the formula's I used! \$\endgroup\$
    – asdasdw
    Commented Dec 24, 2017 at 17:57
  • \$\begingroup\$ Where did you get that? \$\endgroup\$
    – asdasdw
    Commented Dec 24, 2017 at 17:59

Your Answer

By clicking “Post Your Answer”, you agree to our terms of service and acknowledge you have read our privacy policy.

Not the answer you're looking for? Browse other questions tagged or ask your own question.