We usually have 3 wires in the outlet: L (line), N (neutral) and PE (protection earth). It is pretty common that the N is tied to PE in the distribution board or power plant.
If the device has a conductive case, this case should be connected to PE to make the device safe for a human.
However, I still have a question: should be signal ground network connected to PE or not? Or should it be connected through, let's say, a 10 MΩ, 1 W resistor?
If the device doesn't have galvanic isolation there should not be any connection between SGND and PE, right?
If there is a galvanic isolation the question becomes tricky for me. For example - if it is a RS-485 transceiver - I should have a return path for differential pair. This means that the isolated signal grounds of the transceivers should be connected to each other. This connection can be done through a third conductor in the cable or - if it is absent - it can be a PE, right? So in this case I should directly connect the SGND to PE.
I suppose that in some cases SGND should be connected to PE through a 'big' resistor (for example 1 MΩ 1 W) to prevent the circuit from floating (to drain the static or any charge).
I examined some similar question on Stack. I was able to find (one, two, three). They have some useful information which I included in this question, but they actually asked for some particular cases (say RS-485 usage in the first question) and don't have general information on the subject.
If the device have conductive case, this case should be connected to PE to make the device safe for a human.
This is usually true but not always. Double insulation is a method that avoids a protective earth connection.
It completely depends on the system you refer to. PE can offer a good conductive route for EMI and so capacitors can be used on signal lines to improve signal quality but it isn't a given that a galvanic connection is also required. However, it may be required to improve EMC in some instances. The down side of a galvanic connection to PE is that if there are signals passing from point A to point B then both ends grounded is usually a recipe for disaster because, in a plant, earth fault currents can flow between these two points and disrupt signals.
Or it should be connected through let's say 10meg 1W resistor?
Connecting a signal ground to PE through a 10M resistor might be done to prevent a signal floating outside the common-mode range of (say) a signal measurement device such as a DAQ (data acquisition system). There is no real problem with this resistor being significantly lower such as 10 kohms but, again, it is down to the type of system.
If the device don't have galvanic isolation there should not be any connection between SGND and PE
If it doesn't have galvanic isolation then it has some form of galvanic connection to PE.
This means that the isolated signal grounds of the transsievers should be connected to each other. This connection can be done through a third conductor in the cable or - if it is absent - it can be a PE, right?
It does not make any sense to me to transmit RS485 over a cable that doesn't have a shield/screen. This would be asking for poor data integrity. If someone thought it might be a good idea to use PE instead of a shield/screen then they would have to substantially justify their position. I mentioned earth fault currents above and using the PE like this is asking for trouble.
  • \$\begingroup\$ Thanks, Andy! This was a lot of facts to consider. Regarding earth as a return path in RS485 network: you're right. Shield should be far better as a common line. Is it correct that the best solution for RS485 network is a shielded cable with three conductors (two is a teisted pair) with shield connected to PE at one end? \$\endgroup\$ Jan 26, 2018 at 17:22
    \$\begingroup\$ The third conductor is the shield and the two signal conductors are normally twisted around each other to cancel prevailing magnetic interference. This of course may inevitably produce a ground loop through the shield so care must be taken. This can be overcome by using an isolating 485 transceiver chip. \$\endgroup\$
    Jan 26, 2018 at 17:37
  • \$\begingroup\$ @RomanMatveev If we are done here, please take note of this: What should I do when someone answers my question. If you are still confused about something then leave a comment to request further clarification. \$\endgroup\$
    Feb 14 at 8:49
I'm assuming you are running rs485 a long distance.
You have basically one of two options.
  1. Galvanically isolate both ends and then use a cable with a separate shield line. Use the shield line as your low connections. This may be a simple as using an isolated power supply.
  2. Use some type of galvanic isolation in the signal connection itself.
These two options eliminate all the possible unknowns.
If neither end is isolated and you use a cable with a shield this may create a ground loop. At best it may make noise at worst the cable will catch on fire due to excessive current from a ground loop. If only one side is isolated there may be enough of a voltage difference to damage something.
If you tie both ends to PE and use a two conductor cable you may damage the transceivers from a voltage differential that they can't handle.
All of these scenarios may happen if PE connection is not as good as you thought. The individual equipment may have good connections but the interconnect may not be as good.
  • \$\begingroup\$ The question was in general. RS485 is just a good example to discuss the issues that you can face if the PE connection is wrong. \$\endgroup\$ Jan 26, 2018 at 17:39
  • \$\begingroup\$ @RomanMatveev Ethernet for instance completely eliminates the issue by using pulse transformers on both ends. You can string ethernet any which way from Sunday and never have an issue. \$\endgroup\$
    – vini_i
    Jan 26, 2018 at 17:43