Can someone explain to me the 3 main switching states of the following inverter? I understand the +Vd/2 and 0 output states but I do not understand how there is a (-)VD/2 state unless it has to do with the flyback diodes. 1 is considered actuated. If Sa1 is 1 nSa1 is 0 according to the text this was pulled from for clarification. enter image description here
You are being confused by the rather cryptic drawing and logic table.
Note the output is termed \$V_{aN}\$ That implies the measured output is the voltage difference between node \$a\$ and node \$N\$. Since node \$N\$ is already biased at \$V_{dc}/2\$ when the output is high \$V_{aN} = V_{dc}/2\$, when the output swings to the other rail \$V_{aN} = -V_{dc}/2\$.
However the truth table seems a tad messed up. From my understanding output low should be 0,0 on the inputs. Further the state 1,0 should produce open circuit, or high-impedance, output.
  • \$\begingroup\$ I also thought 0,0 would be the low state which is why I was confused originally. 1,0 is not causing a short because of the diode orientation correct? I did pull this directly from an IEEE review so i'm not sure if the table is actually incorrect. \$\endgroup\$ – Paul Feb 14 '18 at 15:12
  • \$\begingroup\$ @Paul correct. re source. mistakes happen, even in the most prestigious papers. \$\endgroup\$ – Trevor_G Feb 15 '18 at 4:05
For connecting the output (a) to (+Vdc/2) you can put Sa1 and Sa2 to on-state, for connecting (a) to the neutral point (N) you might put Sa2 and nSa1 into on-state, and for connecting (a) to (-Vdc/2) you might have the two lower switches nSa1 and nSa2 in on-state (while the not-mentioned switches are always off). This will work for both directions of (inductive) load current, output voltage at (a) will be current-independent.
  • \$\begingroup\$ I should've added that the complimentary switches are always the opposite of what is on the trtuh table for their paired switch. \$\endgroup\$ – Paul Feb 14 '18 at 15:04
  • \$\begingroup\$ Your table was a little bit confusing, I tried to be more clear. \$\endgroup\$ – UweD Feb 14 '18 at 18:30