According to this article (and a lot more published today on the same topic), Kosovo electricity net production balance has decreased during the last weeks.
This has led to a small deviation of the European network’s frequency (from 50Hz to 49.996Hz). In turn, this frequency deviation led to some electric clocks (like ones in ovens) being out of sync (up to 6 min since January).

  • How can a decrease in electricity production lead to a decrease of the frequency on the grid on the long term? Isn't the frequency a parameter controlled by the power plant at the end of the day?
  • If the loss of power from some countries causes a frequency deviation, shouldn't we also observe other impacts, like a drop of the output voltage? Does this mean that we've also been experiencing a drop of voltage for weeks here in Europe?
  • Why do some electric devices directly use the network frequency to sync their clocks, instead of a quartz crystal technology? This means the same oven needs two different firmwares for countries with different electric network frequencies, while, with a crystal (that should be needed anyway to run all the embedded circuits), the same device would run unmodified everywhere.
\$\endgroup\$
20
  • 51
    \$\begingroup\$ The kind of oven clock that gets timing from the grid probably doesn't have any firmware. \$\endgroup\$
    – The Photon
    Commented Mar 7, 2018 at 17:56
  • 10
    \$\begingroup\$ Possible duplicate of Why do generators have to rotate at a slower frequency if demand outpaces the supply? \$\endgroup\$
    – Andy aka
    Commented Mar 7, 2018 at 18:03
  • 6
    \$\begingroup\$ @Andyaka hmm.. actually that does not really answer the question over the long time. The real question here is, why didn't the system recover running at 50.111 long enough to catch up. \$\endgroup\$
    – Trevor_G
    Commented Mar 7, 2018 at 18:09
  • 8
    \$\begingroup\$ @EugeneSh many grids try to keep the pulses per day constant catching up during off-peak periods. \$\endgroup\$
    – Trevor_G
    Commented Mar 7, 2018 at 18:19
  • 10
    \$\begingroup\$ Back in my student days, I got an alarm clock for free : the downside was that it was designed to get its timing from a 60Hz grid, and I used it in Europe. It got 4h late every day, and was an interesting arithmetic problem to solve before going to bed every night : "What time should I set the alarm to if I want to wake up at 07:30?" \$\endgroup\$ Commented Mar 8, 2018 at 7:42

5 Answers 5

33
\$\begingroup\$

How a decrease in electricity production can lead to a decrease of the frequency on the grid on the long term? Isn't the frequency a parameter controlled by the power plant at the end of the day?

Answered before: Why do generators have to rotate at a slower frequency if demand outpaces the supply?

If the loss of power from some countries causes a frequency deviation, shouldn't we also observe other impacts, like a drop of the output voltage? This means we've also been experiencing a drop of voltage for weeks here in Europe?

frequency reduction is primary the means to regulate, not voltage. But, yes, you'll see some amplitude (envelope) variation.

Why some electric devices directly use the network frequency to sync their clocks, instead of a quartz crystal technology? This means the same oven needs 2 different firmwares for countries with different electric network frequencies, while, with a crystal (that should be needed anyway to run all the embedded circuits), the same device would run unmodified everywhere.

Now coming to the relevant question:

Nope, these won't have firmwares the way you think. Also, you can't sell 100% the same oven in countries with different grid frequencies, anyway, because 60 Hz countries tend to use different grid voltages.

These clockkeeping circuits will more look like zero-crossing detectors (that is, a very minimal comparator with a cap on one input, fed directly from the power line, most likely through a resistive voltage divider) and counters, feeding a very minimalistic dedicated clock IC. We're talking low-tech here. Things produced in the millions where using a decades-old ASIC is cheaper than using a quartz + microcontroller.

Also, notice that with a minimal amount of additional complexity (an RC filter) it would be relatively easy to figure out whether you're running on nominally 50 Hz or 60 Hz, so not even your "needs to be different for different grids" argument works!

\$\endgroup\$
14
  • 5
    \$\begingroup\$ All good info but really does not explain why the grid controllers did not play catch-up on the frequency count. \$\endgroup\$
    – Trevor_G
    Commented Mar 7, 2018 at 22:13
  • 18
    \$\begingroup\$ In addition to being cheaper than a quartz crystal, the circuits are more accurate. I've got two clocks that use the powerline frequency for timekeeping, and two (a thermostat and a light switch) that use internal oscillators. The powerline clocks haven't drifted measurably in years, while the thermostat drifts by about 20 minutes a year, and the light switch drifts by 30. \$\endgroup\$
    – Mark
    Commented Mar 8, 2018 at 2:39
  • 4
    \$\begingroup\$ @Evariste I'm not sure why you marked this as the right answer when it didn't answer your main question. If I understand correctly, your question is why the net hasn't kept up with the frequency. It's customary to wait at least 24 hours before accepting an answer, to give time for everyone around the globe to answer, and to give time to write quality answers. \$\endgroup\$
    – pipe
    Commented Mar 8, 2018 at 7:54
  • 4
    \$\begingroup\$ Some stoves/ovens have mechanical clocks. Would they maybe use an AC motor that rotates in sync with the line frequency, geared down? e.g. the stove in my mom's kitchen has digital numbers that mechanically flip over. (Or at least they did until I set the time back 1 hour by turning the knob left, when I was 8 or something and didn't know that clocks were commonly made in ways that let the user easily destroy them.) Anyway, the thing might well contain no digital logic anywhere, just a mechanical clock and oven timer, and some circuits for power regulation based on dial settings. \$\endgroup\$ Commented Mar 8, 2018 at 10:18
  • 3
    \$\begingroup\$ @Evariste even if I'm the one who wrote this very answer, the others are right - you should accept, and only accept, an answer that answers your question. I take your upvote with gratitude and do not hold any grudge should you unaccept my answer and accept a different one!! \$\endgroup\$ Commented Mar 9, 2018 at 20:52
49
\$\begingroup\$

From the Reuter's article referenced:

SARAJEVO, March 7 (Reuters) - European power grid lobby ENTSO-E urged Serbia and Kosovo to urgently resolve a dispute over their power grid, which has affected the broader European network, causing some digital clocks on the continent to lose time.

enter image description here

Figure 1. The ENTSO-E System Operations Committee has 5 permanent regional groups based on the synchronous areas (Continental Europe, Nordic, Baltic, Great Britain, and Ireland-Northern Ireland), and 2 voluntary Regional Groups (Northern Europe and Isolated Systems). Source: ENTSO-E.

The European grid shares power across borders. AC grids have to be kept 100% in-sync if AC connections are used. Britain and Ireland, for example, are connected to the European grid by DC interconnectors so each nations grid can run asynchronously with the rest of Europe whilst sharing power.

The grid shared by Serbia and its former province Kosovo is connected to Europe’s synchronized high voltage power network.

As explained above.

ENTSO-E, which represents European electricity transmission operators, said the continental network had lost 113 gigawatt-hours (GWh) of energy since mid-January because Kosovo had been using more electricity than it generates. Serbia, which is responsible for balancing Kosovo’s grid, had failed to do so, ENTSO-E said.

The energy hasn't been lost. It was never produced.

According to NetzFrequenzMessung.de (you might want to translate) the 113 GWh shortfall averages out to about 80 MW continuous on a total of 60 GW capacity. That's a 0.13%. The scary thing is that we're actually maxed out and can't find an extra 0.13%!

The loss [sic] of energy had meant that electric clocks that are steered by the frequency of the power system, rather than by a quartz crystal, to lag nearly six minutes behind, ENTSO-E said.

"Steered" is probably a mistranslation. "Regulated" would be better.

Many digital clocks, such as those in alarm clocks and in ovens or microwaves, use the frequency of the power grid to keep time. The problem emerges when the frequency drops over a sustained period of time.

enter image description here

Figure 2. An electro-mechanical timeswitch of the style popular with the utility companies.

Analogue, motorised clocks do too. The day / night clock on my electricity meter is > 40 years old and it has a mains-powered clock with a self-rewinding clockwork UPS to keep it OK during power cuts!

ENTSO-E said the European network’s frequency had deviated from its standard of 50 Hertz (Hz) to 49.996 Hz since mid-January, resulting in 113 gigawatt-hours (GWh) [sic] of lost energy, although it had appeared to be returning to normal on Tuesday.

The frequency is not held constant to three decimal places for months on end. That might be an average figure. Here's the data for the last five minutes:

enter image description here

Figure 3. Note that frequency deviation will be much wider over a longer time period. Source: MainsFrequency.com.

enter image description here

Figure 4. Network time deviation has increased from -100 s to -350 s in three weeks. Source: MainsFrequency.com.

enter image description here

Figure 5. [WOW!] In our previous measurement operation (July 2011 to 2017), network time deviations of ± 160 seconds occurred (June 2013). But since January 3, 2018, the network time deviation is continuously decreasing. Changing the setpoint for the secondary control power on January 15 from 50,000 Hz to 50,010 Hz has not yet been able to reduce the mains time. Source: MainsFrequency.com.

Secondary control power is activated when the system is affected for longer than 30 seconds or it is assumed that the system will be affected for a period longer than 30 seconds. Prior to this, deviations in the system are only covered through primary control. Source: APG.at.

“Deviation stopped yesterday after Kosovo took some steps but it will take some time to get the system back to normal,” ENTSO-E spokeswoman Susanne Nies told Reuters. She said the risk could remain if there is no political solution to the problem.

If they start generating and feeding into the grid it will speed up.

The political dispute centres mainly on regulatory issues and a row between Serbia and Kosovo over grid operation. It is further complicated by the fact that Belgrade still does not recognise Kosovo.

“We will try to fix the technicalities by the end of this week but the question of who will compensate for this loss has to be answered,” Nies said.

This doesn't make any sense to me. Energy flow is metered and billed accordingly. Each country pays for their imports.

ENTSO-E urged European governments and policymakers to take swift action and exert pressure on Kosovo and Serbia to resolve the issue, which is also hampering integration of the western Balkans energy market required by the European Union.

“These actions need to address the political side of this issue,” ENTSO-E said in a statement. The grid operators in Serbia and Kosovo were not immediately available to comment.

Kosovo seceded from Serbia in 2008. Both states want to join the European Union but Brussels says they must normalize relations to forge closer ties with the bloc.

Serbia and Kosovo signed an agreement on operating their power grid in 2015. However, it has not been implemented yet as they cannot agree on power distribution in Kosovo amid conflicting claims about ownership of the grid, built when they were both part of Yugoslavia. (Writing by Maja Zuvela; Editing by Susan Fenton)

I guess neither of the above are electrical engineers.



Answering the questions:

  1. How a decrease in electricity production can lead to a decrease of the frequency on the grid on the long term? Isn't the frequency a parameter controlled by the power plant at the end of the day?

If demand is approaching peak capacity then we have to let either the voltage or the frequency droop if we wish to avoid disconnecting customers. Dropping the voltage will cause problems with certain loads and is to be avoided.

The Reuter's article fails to explain why the system average frequency has been low for so long. It can only be that it hasn't been able to run above 50 Hz for long enough to catch up. Off-peak seems the time to do this but there will be an upper limit on the frequency deviation - about 50.5 Hz (but I don't have a definite number).

  1. If the loss of power from some countries causes a frequency deviation, shouldn't we also observe other impacts, like a drop of the output voltage? This means we've also been experiencing a drop of voltage for weeks here in Europe?

No, we reduce frequency to avoid the drop in voltage.

  1. Why some electric devices directly use the network frequency to sync their clocks, instead of a quartz crystal technology?

They don't sync the clocks in the sense of adjusting or correcting the time. They maintain synchronisation by keeping the average frequency at exactly 50 Hz. One reason for this is the millions of electro-mechanical clocks in service. These are fantastically reliable, don't require batteries and do the job. Why replace them?

This means the same oven needs 2 different firmwares for countries with different electric network frequencies, while, with a crystal (that should be needed anyway to run all the embedded circuits), the same device would run unmodified everywhere.

Crystals will drift and the further complication of real-time clock with battery backup are required. Electrical utilities work on timescales of 20 to 50 years. How long do you think the electrolytic capacitors in your digital clock will last?


Links:


Other interesting bits:

This grid time deviation is constantly balanced out. If the time deviation is more than twenty seconds the frequency is corrected in the grid. In order to balance out the time deviation again the otherwise customary frequency of 50 Hz (Europe) is changed as follows:

49.990 Hz, if the grid time is running ahead of UTC time

50.010 Hz, if the grid time is lagging behind UTC time

Source: SwissGrid.

Meanwhile on 2018-03-08:

NTSO-E has now confirmed with the Serbian and Kosovar TSOs, respectively EMS and KOSTT, that the deviations which affected the average frequency in the synchronous area of Continental Europe have ceased.

This is a first step in the resolution of the issue. The second step is now to develop a plan for returning the missing energy to the system and putting the situation back to normal.

Source: ENTSO-E.

Hmmm! They're referring to it as "missing energy".

\$\endgroup\$
12
  • 6
    \$\begingroup\$ "mainsfrequency.com"? Seriously? I'm amazed of what can be found on the internet. +1 for this. \$\endgroup\$
    – dim
    Commented Mar 7, 2018 at 20:06
  • 15
    \$\begingroup\$ We're pedaling as hard as we can over here to get the frequency up above 50 Hz for long enough to resync the clocks. We need those eastern guys to stop quarreling and get back on their bikes. OK I'll see if I can answer the actual questions but it's bedtime. ;^) \$\endgroup\$
    – Transistor
    Commented Mar 7, 2018 at 22:32
  • 2
    \$\begingroup\$ Right, @Trevor_G: More pretty pictures for you. I'm having to look all this stuff up as I don't work in the power industry. It's rather interesting but if I'm tired in work tomorrow it's your fault. \$\endgroup\$
    – Transistor
    Commented Mar 7, 2018 at 23:20
  • 3
    \$\begingroup\$ Is it because they can't find 80 MW of generation, or are there other constraints they're trying to stay within (perhaps not overloading transmission lines into Serbia/Kosovo)? \$\endgroup\$
    – user20574
    Commented Mar 8, 2018 at 9:53
  • 14
    \$\begingroup\$ "The scary thing is that we're actually maxed out and can't find an extra 0.13%!" This is presumably wrong. In fact nobody wants (or better wanted) to pay the extra power needed to balance things out. Kosovo Govt to Pay €1m for Serbs’ Electricity. It's rather a political problem than a lack of capacity. \$\endgroup\$
    – klanomath
    Commented Mar 8, 2018 at 13:52
20
\$\begingroup\$

How can a decrease in electricity production lead to a decrease of the frequency on the grid on the long term? Isn't the frequency a parameter controlled by the power plant at the end of the day?

You can think of the electricity grid as being like a giant mechanism. Induction motors are like belts that can slip a bit. Synchronous motors and generators are like gears that cannot slip.

In the short term frequency is used to regulate the power flow in and out of the grid. If the grid is overloaded it will start to slow down and conventional generators will increase their power to compensate. Similarly if the grid is underloaded it will increase in speed slightly and generators will back off.

Eventually if the grid frequency gets too low then the grid will start dropping loads to prevent a complete collapse.

When the grid frequency drops below nominal, central control should command some power stations to increase their power set point so that the grid comes back up to its nominal frequency. Those power stations will need to be paid to increase their setpoints.

It seems that the political issues resolve around who should pay the power plants to increase their setpoints. If no one pays then the grid frequency remains reduced (and all the conventional power plants end up generating slightly more than they were contracted to generate).

\$\endgroup\$
1
  • 3
    \$\begingroup\$ +1 The last paragraph here is likely, and ultimately, the right answer to this question. \$\endgroup\$
    – Trevor_G
    Commented Mar 9, 2018 at 16:23
4
\$\begingroup\$

To answer the "Why not quartz?" question:

Crystals are actually pretty terrible even for short-term timekeeping. A nice crystal on Digi-Key will typically have about 20 ppm accuracy.

$$1\ \mathrm{day} * 20\ \mathrm{ppm} = 1.728\ \mathrm{seconds}$$

But you probably won't have a nice crystal. Nice crystals don't sell consumer products. For example, the crystal in my wristwatch is about 66 ppm fast:

$$1\ \mathrm{day} * 66\ \mathrm{ppm} = 5.702\ \mathrm{seconds}$$

So after 12 days the watch is off by 1 minute. After a month it's off by ~2.5 minutes. 5-10 minutes (2-4 months) is enough drift to start causing problems. And that's not including temperature drift.

The power line frequency might not be more precise on a time scale of seconds or minutes, but the number of cycles per day is usually well-controlled. That's why the European grid issues made the news.

\$\endgroup\$
3
  • 1
    \$\begingroup\$ The value of 5.072 is wrong, 5.702 is right, but it is not possible to change only two characters. \$\endgroup\$
    – Uwe
    Commented Mar 9, 2018 at 21:40
  • \$\begingroup\$ @Uwe It is if you've got enough rep. Thank you for the correction. I need to proofread my answers more; I've been making a distressing number of errors. \$\endgroup\$
    – Adam Haun
    Commented Mar 9, 2018 at 22:21
  • \$\begingroup\$ In the olden days, power grid was used for synchronizing events across remote locations. Nowadays (in the last 20 years) this kind of timing and synchronization is done using GPS. \$\endgroup\$ Commented Mar 9, 2018 at 22:35
3
\$\begingroup\$

Why do some electric devices directly use the network frequency to sync their clocks, instead of a quartz crystal technology? This means the same oven needs two different firmwares for countries with different electric network frequencies, while, with a crystal (that should be needed anyway to run all the embedded circuits), the same device would run unmodified everywhere.

Because it is cheaper and still reliable (even more accurate?) then quartz crystal. And particularly the entire European continent is running on the same electricity network. So you can sell your oven to that total number of customers. For other countries manufacturers would make different versions anyway. There aren't many items that are sold everywhere (in every country) exactly the same.