I am working on a project to monitor a power meter parameters like voltage, frequency, current and so on and this monitoring for both AC and DC. For DC we are using Cummins diesel generator, now I need to calculate the generator running hours based on the load.

For example, I have a generator with 10 kVA capacity which consumes the diesel as follows:

On 1/4 load the generator will take 1.5 ltr/hour

On 1/2 load the generator will take 2 ltr/hour

On 3/4 load the generator will take 3 ltr/hour

On Full load, the generator will take 5 ltr/hour

How to calculate these 1/4, 1/2, 3/4 and full load from the power meter parameters? And how can I calculate the diesel consumed by the generator using the same parameters?

\$\endgroup\$
3
  • \$\begingroup\$ Welcome to EE.SE. Do you know about basic physic laws like P=UI and E=Pt? \$\endgroup\$
    – winny
    Aug 10, 2018 at 13:46
  • \$\begingroup\$ Honestly I don't know, I am an IT Guy \$\endgroup\$ Aug 10, 2018 at 14:09
  • 1
    \$\begingroup\$ Then you need to read up and learn. Start with a google search and Wikipedia. \$\endgroup\$
    – winny
    Aug 10, 2018 at 14:15

2 Answers 2

4
\$\begingroup\$

For the best estimate of fuel consumption, you should use the power in kilowatts (kW), not apparent power in kVA. Most DGs have three-phase output for which power is equal to voltage X current X square root of 3 X power factor. Since it is difficult to measure power factor (phase difference between voltage and current) you should use a three-phase wattmeter.

The DG manufacturer may assume that the average load power factor is 0.8 or higher. You could assume that pf is 1.0 and say that power = voltage X current, but that would make your fuel consumption estimate high. You could measure the line to neutral voltage and the current for each phase and then add the three power calculations to estimate power.

Say that you have a 10 kVA generator that has a 3-phase, 400 volt output that has connection points to provide three single phase 230 volt supplies. Each supply would be rated 3.3 kVA and be capable of 3300/230 = 14.3 amps. If you connect an assortment of lighting and heating appliances that draw 8, 11 and 13 amps, you would have 8 X 230 + 11 X 230 + 13 X 230 = 7360 watts or 7.36 kW. That would be about 3/4 load, so the fuel consumption would be about 3 liters per hour.

\$\endgroup\$
2
  • \$\begingroup\$ Can you please elaborate with example values, so that the novice like me also can understand? 0) \$\endgroup\$ Aug 10, 2018 at 14:30
  • 1
    \$\begingroup\$ I added an example, but I can't provide a tutorial on single-phase and 3-phase AC power. You probably need to do as @winny suggested. Find an online resource that can take you through the basics step-by step with illustrations and examples. This site is better suited to answering specific questions to clarify things you don't understand while studying more detailed material. \$\endgroup\$
    – user80875
    Aug 10, 2018 at 15:00
1
\$\begingroup\$

A very simple means of calculation will be as follows.

  • 1 litre of fuel oil can release about 10 kWh of energy. (Wikipedia's Energy density page says 10.7 kWh/L.
  • You state that your generator consumes 5 L/h at 10 kVA. Let's assume that 1 kVA = 1 kW for the moment. That means that 1 litre of fuel is giving out only 2 kWh of electrical energy. The energy conversion is only 20%! This may be reasonable for a small generator as efficiency can increase with scale.

In summary:

  • 1 L/h --> 2 kWh
  • 1 kWh --> 0.5 L/h

Now let's compare with your figures with our simple rule of thumb above.

Load     kVA     Manufacturer  Rule of thumb
1/4       2.5    1.5 L/h       0.5 x 2.5 = 1.25 L/h
1/2       5.0    2.0 L/h       0.5 x 5.0 = 2.50 L/h
3/4       7.5    3.0 L/h       0.5 x 7.5 = 3.75 L/h
4/4      10.0    5.0 L/h       0.5 x 10  = 5.00 L/h

If you plot these on a chart the rule of thumb will give you a straight line whereas your manufacturer's figures will form a curve with fuel consumption being disproportionately higher at low load due to further inefficiencies.


I would be inclined to dip the tank and take a meter reading at the start of operations and again at before the tank requires a refill and work out an average fuel consumption per kWh.

If an exact measurement is required then add an in-line fuel meter. Check your electrical energy meter to see if it has a pulse input that you could use as many have for gas / water monitoring.

\$\endgroup\$
4
  • \$\begingroup\$ A Diesel engine has an efficiency of 40%. That 10kWh is thermal, so a Diesel engine will give you 4kWh on the drive shaft out of 1l diesel. \$\endgroup\$
    – Janka
    Aug 10, 2018 at 16:07
  • \$\begingroup\$ @Janka. Correct. When estimating fuel consumption on a 100 kVA to 1.5 MVA generator I would use the 40% figure as an overall conversion figure to estimate how much fuel I'll need to purchase. This one is only giving 20%. \$\endgroup\$
    – Transistor
    Aug 10, 2018 at 16:23
  • \$\begingroup\$ How we can calculate that the DG is running on 1/4 Load, 1/2 Load and etc ? \$\endgroup\$ Aug 21, 2018 at 15:33
  • \$\begingroup\$ You said you had power / energy meters. Use them. \$\endgroup\$