What kind of self-test circuits or method do they used in the GFCI outlets generally? Is it just firmware or is there a physical addition (and what it is usually?)
This is because after 2015, it is required by UL. But there were many old stocks without it and the physical appearance of the product is the same. So is there any way to recognize or test the function if I buy a product which both has the function and not (depending on whether manufactured after or before 2015 which they don't specify?)
Note: This isn't about the manual test button, but a circuit inside... see
New Self-Test Requirements:
n Underwriters Laboratories (UL) made new revisions to the UL 943 (GFCI) standard that will take effect on June 29th, 2015.
n UL REVISION 943 STATES:
  1. All GFCI receptacles must have an auto-monitoring (self-testing) feature.
  2. If auto-monitoring determines the GFCI can no longer offer protection, one or more of the following will happen:
    (1) Unit is no longer able to reset and denies power.
    (2) Unit can reset and is subject to the next auto-monitoring test cycle within 5 seconds of power to the device.
    (3) All GFCIs must provide audible or visual indication if it does NOT go into power denial.
  3. Provisions to ensure receptacle will not reset if miswired during installation as well as reinstallation. "
An temporary imbalance (leak) between the hot and neutral is created, and the GFCI circuit should detect it.
Is it just firmware or is there a physical addition.
There is a physical addition: a resistor for creating a leak, some kind of switch for connecting and disconnecting this resistor. (By the way, most GFCI deices are hard-wired, and they don't have microcontrollers with firmware.)
I've designed an GFCI (RCD) circuit once, and it has a self-test. R9 provides the controlled leakage. U2 is the solid state relay for connecting the R9 during self-test and disconnecting it the rest of the time.
GFCI RCD circuit with self test
The automatic selftest is something I had to do some digging on.
I found patent US20170299656A1, which includes a schematic and detailed explanatory text.
It looks like it works just as the test switch, except the current stays lower than the trip threshold and it measures the feedback of the coil. It only self-tests the sensing part of the GFCI. Not the breaker part.
One advantage I can see in this is that if you have a DC (fault) current that saturates the sensing coil, this condition will be detected. A DC saturated coil significantly inreases the trip threshold or completely inhibits the device.
  • \$\begingroup\$ I was not referring to the Test button.. but self-test in which the GFCI would automatically test itself every minute automatically. \$\endgroup\$
    – Samzun
    Oct 22, 2018 at 6:26
    \$\begingroup\$ see the added passage above in UL943 which quoted: "New Self-Test Requirements: n Underwriters Laboratories (UL) made new revisions to the UL 943 (GFCI) standard that will take effect on June 29th, 2015. n UL REVISION 943 STATES: 1. All GFCI receptacles must have an auto-monitoring (self-testing) feature." \$\endgroup\$
    – Samzun
    Oct 22, 2018 at 6:48
    \$\begingroup\$ @Samzun Automatic mode... That was not clear. I have no clue how a breaker can test itself without actaully testing the breaker part. This UL seems to make it less safe, with the lockout (people will bypass them) and probably periodic inoperability due to test. \$\endgroup\$
    – Jeroen3
    Oct 22, 2018 at 7:10
  • \$\begingroup\$ I saw this discussion in 2012.. diychatroom.com/f18/leviton-self-test-gfci-questions-139980 that was 3 years before it becomes mandatory.. so I need to see some circuit diagram of it.. or circuit diagram of GFCI in general and how this automatic self test circuit is added or adapted. \$\endgroup\$
    – Samzun
    Oct 22, 2018 at 7:25
    \$\begingroup\$ @Samzun The power supply of the electronics might not like 240V. Europe does use GFCI, they are called RCD here. They are in the distribution box, not the socket. \$\endgroup\$
    – Jeroen3
    Oct 23, 2018 at 5:35