I have developed an MQ-5 based LPG gas sensor which uses a relay.

Is the relay itself a fire hazard (while switching) if gas is in the vicinity ? Thanks.

\$\endgroup\$
  • 3
    \$\begingroup\$ Yes, if it's open to the atmosphere. Redesign with a reed relay. \$\endgroup\$ – Janka Oct 31 '18 at 3:22
  • \$\begingroup\$ Would the typical relay module (blue casing, 5VDC, 10A @ 250VAC) count as "open to the atmosphere" ? \$\endgroup\$ – Frost Oct 31 '18 at 3:36
  • 1
    \$\begingroup\$ Yes it probably would. \$\endgroup\$ – Drew Oct 31 '18 at 6:56
  • 1
    \$\begingroup\$ Could one use a solid-state relay, are these safe in a volatile gas environment ? \$\endgroup\$ – Frost Nov 3 '18 at 17:17
2
\$\begingroup\$

There are relays that are made for use in hazardous locations such as one where explosive gases are present. The term for these relays is intrinsically safe and they either operate on such low energy that they will not ignite flammable or explosive materials, or they are sealed in such a manner that the gasses (or explosive dust, etc.) are protected from the live parts.

There are intrinsically safe barrier relays which are interposing relays designed to operate at intrinsically safe levels on one side and normal levels on the other.

It's a broad and complex topic way beyond this answer, but hopefully those terms will provide you with a start for further research.

\$\endgroup\$
2
\$\begingroup\$

Back when I still worked we sold instruments with control relays. Hermetic relays were an option.
enter image description here

\$\endgroup\$