Forgive my ignorance, but how can two 3-phase ratings on the same motor result in the same output power?

The one I have is rated for 0.7kW in triangle for both 400V and 690V.

\$\endgroup\$
  • \$\begingroup\$ delta/star or triangle/star configuration. You can't connect this motor in triangle on 690V, but star. On 400V you connect it in triangle, power is the same. \$\endgroup\$ – Marko Buršič Nov 17 '18 at 9:21
  • \$\begingroup\$ @MarkoBuršič I think it's the other way around; star/wye is 400V (phase-ground), and triangle/delta is 690V (phase-phase). \$\endgroup\$ – marcelm Nov 17 '18 at 9:53
  • \$\begingroup\$ @marcelm: Marko is correct. Have a look at my answer. \$\endgroup\$ – Transistor Nov 17 '18 at 20:52
1
\$\begingroup\$

schematic

simulate this circuit – Schematic created using CircuitLab

Figure 1. Connection possibilities.

  • On a 400 V phase-to-phase supply the motor windings are connected in delta (from the Greek 'D' or Δ).
  • On a 690 V phase-to-phase supply the motor windings are connected in star or wye (from the American letter 'Y').
  • From trigonometry you can show that the orange lines in Figure 1b are \$ \sqrt 3 \$ times the length of the black lines. \$ 400 \times \sqrt 3 = 692.8 \$.

schematic

simulate this circuit

Figure 2. Connection options.

How can two 3-phase ratings on the same motor result in the same output power?

In each case the voltage across each winding is 400 V so the same current will flow in each winding and the same power will be produced.

\$\endgroup\$
  • 1
    \$\begingroup\$ The 'American' letter? Well okay then transistor. \$\endgroup\$ – sidA30 Nov 17 '18 at 11:37
  • \$\begingroup\$ Ha! It's "star" on this side of the Atlantic. I've never seen "wye" as a word for 'Y' except in American literature. \$\endgroup\$ – Transistor Nov 17 '18 at 11:39
  • \$\begingroup\$ Ah of course. I misread the name plate on the motor. Indeed it says 400/690 Δ/Y. I confused it with being rated for both 50/60Hz. Additional question: Since it is 400/690 for 50Hz and 480V/60Hz in Δ - what would the Y voltage @60Hz be? It isn't mentioned on the name plate. \$\endgroup\$ – Claws Nov 18 '18 at 4:24
  • \$\begingroup\$ 480*sqrt(3)~831V? \$\endgroup\$ – Claws Nov 18 '18 at 4:30
  • \$\begingroup\$ I've never seen 830 V mentioned anywhere. Maybe it can only be run in delta on a 60 Hz, 480 V supply. Don't forget that insulation breakdown voltage becomes a problem at some point. \$\endgroup\$ – Transistor Nov 18 '18 at 7:59