I am using external CT to measure Current parameter. I am using PIC16F1938 to measure analog . Now here i am looking for circuit and calculation involved to get proper current rating
datasheet
Min Current : 0.8A max Current :30A Primary Current 30A nom., 75A max Turns Ratio 1000:1
I have 10 bit resolution ADC. Kindly suggest me the circuit how we can choose the value. I got article with arduino Energy meter reading with ac-1030
Let me know best circuit to be achieve better accuracy. Some forum recommend to use amplifier circuit . Let me know which is best
    \$\begingroup\$ Your link [2] is broken. 'Better accuracy' is meaningless. What accuracy do you want to achieve? \$\endgroup\$ – Neil_UK Dec 27 '18 at 10:55
Some missing specs, will assume PIC DC supply (along with voltage reference for 10-bit ADC) is +5V. Therefore, the maximum peak-to-peak voltage signal at ADC input should be 5V peak-to-peak, with a +2.5V DC offset. ADC reference voltage would be +5V.
If you really must provide a linear current-sense up to 30A from the current transformer, then peak-to-peak current would be 84.8A (the 30A is RMS current). This current is reduced by a factor of 1000 to 84.8 mA peak-to-peak flowing through the current transformer load resistor. A load resistor of 58.92 ohms would produce five volts peak-to-peak for the ADC.
You might use the next smaller standard value for R1 (like 56 ohms) so that noise and transients won't over-voltage the ADC input. The large value of R2,R3 may help prevent latch-up on really large transients.
As always, when dealing with high-potential AC with that current transformer, be careful!
  • \$\begingroup\$ If you really must provide a linear current-sense up to 30A from the current transformer, then peak-to-peak current would be 84.8A (the 30A is RMS current). I could not able to understand this part. How it will be 84.8A. As always, when dealing with high-potential AC with that current transformer, be careful! What is protection circuit i need to build. Why didnt u used amplifier circuit here. \$\endgroup\$ – AMPS Dec 28 '18 at 4:28
  • \$\begingroup\$ @AMPS A sine-wave current of 30A swings to a positive peak of 42.4A and a negative peak of -42.4A: there is a \$ 2 \sqrt 2 \$ factor between RMS and PEAK-to-PEAK. The result must fit within the ADC's range of 5V. By choosing R1 value properly, no amplifier is needed. A larger R1 (within reason) makes the current transformer more sensitive. \$\endgroup\$ – glen_geek Dec 28 '18 at 14:34
  • \$\begingroup\$ it is said lower value better accuracy what you recommendation.. \$\endgroup\$ – AMPS Dec 31 '18 at 3:39
  • \$\begingroup\$ Yes, for the CT itself, linearity improves with lower R1. But you pay with less voltage output - hence your ADC resolution suffers. Design this way: decide what maximum current you anticipate. Scale R1 so that current yields 5V peak-to-peak into ADC. The example above calculates R1 for 30A(rms) yielding 5v (p-p). Values of R1 much above 100 ohms result in poorer linearity. \$\endgroup\$ – glen_geek Dec 31 '18 at 14:43
By clicking "Post Your Answer", you acknowledge that you have read our updated terms of service, privacy policy and cookie policy, and that your continued use of the website is subject to these policies.