I had thought I could just connect the 24vac input to a relay input, and then setup a pin as an input on the arduino and be able to know that the relay had closed. But now I'm reading that relays need a minimum current or some such, and I don't really understand how I could meet that since I'll have no load.

I know just barely enough to even be dangerous. Am I even making sense?

\$\endgroup\$
  • \$\begingroup\$ Why not use diode and R divider with cap to detect 24Vac as DC? Contacts need a wetting current such as a pullup R and 10uF Tant cap. to prevent oxidation unless gold-plated rated <2A \$\endgroup\$ – Tony Stewart Sunnyskyguy EE75 Jan 22 '19 at 18:22
  • \$\begingroup\$ Yes you are making sense in that a little knowledge can be dangerous but, do you have a proper techy question? \$\endgroup\$ – Andy aka Jan 22 '19 at 18:24
  • \$\begingroup\$ Are you trying to switch the 24V side? Are you detecting the 24V? \$\endgroup\$ – Voltage Spike Jan 22 '19 at 18:24
0
\$\begingroup\$

Your setup is not super clear, but I will try to interpret. It sounds like you have a 24v ac signal connected to the coil on a relay. When that signal turns on, you want the relay to close. You want the arduino to use the relay contacts like a switch and detect whether it's open or closed.

I assume you mean that the contacts need some current? Assuming it's a mechanical relay, that's not really true. Some relays do recommend a bit of current to improve long term reliability, but I wouldn't worry about that right away.

Just hook up the contacts of the relay to your arduino as if it were a switch. Should work fine.

You could even hook up an LED to be turned on by the relay (google Led circuits). Set the current for 20ma, and that will give you a small load and a visual indicator at the same time.

If the relay is a solid state relay, it does need a load. But you haven't indicated that so I won't get into it.

|improve this answer|||||
\$\endgroup\$
  • \$\begingroup\$ Use a signal relay, they have no minimum current. \$\endgroup\$ – Jasen Jan 23 '19 at 8:27
  • \$\begingroup\$ I just browsed for signal relays, and can't find any with 24v AC input. Are there such things, or are they made for DC input only? \$\endgroup\$ – john west Jan 23 '19 at 13:34
  • \$\begingroup\$ Drew, i am worried about reliability. It might sit for months or a couple of years and never get any current, since this is around detecting water leaks, and the 24VAC only flows when a leak occurs (I have no control over any part of that). I have scoured digikey, mouser and other sites, and I see relays that support 24VAC input, but I just don't have experience to know what type and model are best. I'm hoping to learn enough to make that decision :). \$\endgroup\$ – john west Jan 23 '19 at 13:36
  • \$\begingroup\$ I do like the LED idea. And solid state is definitely best. Is "signal relay" synonomous with solid state relay, or are they not necessarily one and the same? \$\endgroup\$ – john west Jan 23 '19 at 13:42
  • \$\begingroup\$ They are not the same. And if you really want to go by the books, just use a resistor as a load. Make sure that if you do that that your power supply can handle it. \$\endgroup\$ – Drew Jan 23 '19 at 17:55
0
\$\begingroup\$

No relay is needed. You could rectify the 24V into DC, smooth it with a cap, then drive the input of an optoisolator with a proper current limit resistor. When AC is applied the opto's open-collector output could pull a uC input with internal pullup resistor low to signal that AC is present. Example part: https://www.onsemi.com/pub/Collateral/HCPL2631M-D.pdf