Electrician from Australia here. Just having an issue with a heater fan in a bathroom for a client. According to the diagram I have posted, I can wire a second fan up to this and it should all work.
The issue I am having is that because of the permanent supply to the unit, once that thermal switch goes above 55C it supplies power to both the fans via the 20W 330ohm resistor. By adding a second fan as drawn by the diagram, this also will be powered in an over current situation via the resistor.
The issue is, I don't believe the manufacturer has realised the implications of having a second fan fed from the ceramic resistor, and it heats up and blows the thermal fuse at 93C.
So what wattage resistor is required to power the 25W main fan in the unit, and a second 60W fan external to the unit?
I tried working it out as below;
Current draw of main fan = P/V = 25/230V = 0.1A
Voltage drop over resistor= I*R= 0.1*330= 33V
Power dissapated by resistor with main fan= V*I= 33*0.1 = 3.3W
All OK
With the second fan of 60W in the circuit, we now have 85W load.
Current draw of main fan = P/V = 85/230V = 0.37A
Voltage drop over resistor= I*R= 0.37*330= 122.1V
Power dissapated by resistor with main fan= V*I= 122.1*0.37 = 45.17W
45.17W on a 20W resistor- Houston we have a problem.
Is my maths and methodology correct??
  • \$\begingroup\$ IMO the second fan goes where depicted, not in parallel with first one. \$\endgroup\$ Commented Mar 1, 2019 at 7:39
  • \$\begingroup\$ @MarkoBuršič The second fan is in parallel with the first, isn't it. \$\endgroup\$
    – HandyHowie
    Commented Mar 1, 2019 at 8:24
  • \$\begingroup\$ G'day. Your basic premise that 2 fans overloads the resistor is probably true, but I don't agree with your maths. As you drop the voltage to the fan (through the resistor) the fan will take less power, hence less current. But I'm not smart enough to know by how much. I've got a simple solution. If you use a 25W fan for the 2nd fan then you can add another 330 Ohm 20W resistor just for that fan. The thermal switch will feed the 2 resistors. \$\endgroup\$
    – Steve G
    Commented Mar 1, 2019 at 9:26
  • \$\begingroup\$ Couldn't you just add a relay to turn on the second fan? Do the instructions mention a maximum wattage for the second fan? \$\endgroup\$
    – HandyHowie
    Commented Mar 1, 2019 at 10:03
The second fan is not connected in parallel with the first. It is connected directly to the neutral while the path to the neutral from the first fan goes through the thermal switch. You should make sure that the second fan is suitable for connection to the mains without an external thermal switch.
When the speed of a fan is reduced, the power required to drive it is greatly reduced. Power is proportional to speed cubed. That means reducing the speed to 2/3 of full speed reduces the power to 30% of full power. However, that calculation does not fully take losses into account.
In addition, the voltage drop and current calculations are not a simple matter because of inductance in the fan.
The bottom line is that it will not really be possible for you to verify if it is ok to add the second fan without connecting it and observing if the resistor gets too hot.