I am getting several PSUs (LRS-350-24) from Mean Well. Here's the specs:
https://www.meanwell.com/Upload/PDF/LRS-350/LRS-350-SPEC.PDF
1) The input current is stated to be 3.4A/230VAC at 88%. 350W output at 88% efficiency would mean 398W input/230V = 1.73A input which is 50% of the rated input current @ 3.4A/230VAC.
So should i take it as 1.73A or 3.4A? Because up to 3 PSUs will be tied to a switch rated at 10A, 240V. 3.4A would have exceeded the limit.
2) The stated inrush current is 60A/230VAC. Does this change if say, i am only going to use 50-60% of the PSU's output?
Reason is because the circuit for this PSU is tied with other lighting with 10A type C breaker which may trigger due to the inrush since the minimum is 5x.
Thanks.