In my neighbourhood, a 220 kiloVolt high voltage line is being renovated. It seems that they are replacing the cables, and they also may do some other maintenance. This, however, gave rise to some (possibly) noob questions.
  • What sort of maintenance is required for high voltage lines?
  • Which parts need replacement?
  • What are the life-time determining factors for high voltage transmission lines?
  • \$\begingroup\$ Surely google is your friend here: eprmagazine.com/uncategorized/maintenance-of-transmission-lines. This was the 2nd hit when searching using your first bullet point. \$\endgroup\$
    Commented Jun 6, 2019 at 9:39
  • \$\begingroup\$ Yes, google is good for everything which is why SE is redundant \$\endgroup\$ Commented Jun 6, 2019 at 13:26
  • \$\begingroup\$ While the linked article deals a lot with insulators and towers, it barely mentiones the cables themselves. \$\endgroup\$
    – Dohn Joe
    Commented Jun 6, 2019 at 14:36
  • \$\begingroup\$ That website does give you topics to Google under cold line maintenance and Regular (monkey) thorough line patrolling with digital photography of the line components is carried out. \$\endgroup\$ Commented Jun 6, 2019 at 15:34
  • \$\begingroup\$ But what are the damage mechanisms? What happens to the cables over time to warrant line inspection? \$\endgroup\$
    – Dohn Joe
    Commented Jun 6, 2019 at 16:14
Some of the maintenance tasks we do on transmission lines (Rural Australia; 11 kV - 132 kV)
  • Grade the access roads along the line corridor - access roads tend to get overgrown / washed out over time. Inacessible roads are very inconvenient when "running the line" to find a fault at night-time.
  • Cut down trees encroaching on the line.
  • Perform visual inspection of the line - look for damaged conductors or hardware i.e. broken insulators.
  • Scan for hot joints using a thermal camera. Current-carrying connections can corrode or become loose over time, resulting in overheating and eventual failure. Crimped connections are usually OK. Most of our problems are with bolted connections, particularly "parallel-groove clamps".
  • For wood poles- check that the wood hasn't been eaten by termites. The simplest test is a "knock test" i.e. hit the pole with a hammer and listen to how it sounds. If the pole sounds hollow, it's probably been eaten by termites.
  • For steel structure towers - check the structural condition of the tower. Rust is bad. Missing fasteners (nuts/bolts) are bad. Loose fasteners are also bad. All these things reduce the strength of the structure under load.
  • For all kinds of towers - check the earthing at the base of the tower/pole - each tower/pole should have a earth grading ring and an earth electrode. This is important for lightning protection and personnel protection (touch/step voltage). The earth electrode should be 10 ohms or less. Replace/refurbish earthing electrode if required.
We don't really worry too much about the conductor (wire) itself.
  • We have conductors that have been in service for 60 years with no issues.
  • Where conductors have failed, this is usually due to lightning strikes. (I have an example on my desk.)
  • Metal fatigue doesn't tend to be an issue - any lines that would be susceptible to wind-induced oscillations will also have dampeners or other engineering controls, to mitigate that.
    \$\begingroup\$ Very thorough list. Yet, metal fatigue may be an issue in other climates where there is heavy icing. p5.focus.de/img/fotos/origs5103489/… \$\endgroup\$
    – Janka
    Commented Jun 9, 2019 at 9:27
    \$\begingroup\$ @Janka: Interesting! Ice is not an issue we encounter here in outback Australia. If we had that sort of cold weather, the kangaroos would need warm coats and mittens. :) \$\endgroup\$ Commented Jun 9, 2019 at 9:35
    \$\begingroup\$ In Canada they have the same problems each year so they deliberately heat the conductors in ice storms. en.wikipedia.org/wiki/Levis_De-Icer \$\endgroup\$