-1
\$\begingroup\$

The internal generated voltage EA of a 2-pole, delta-connected, 60 Hz, three-phase synchronous generator is 14.4 kV, and the terminal voltage VT is 12.8 kV. The synchronous reactance of this machine is 4 ohm, and the armature resistance can be ignored.

The answer is given as: enter image description here

However, I do not understand why this is correct. Shouldn't VΦ be equal to VT/√3 = 12800/√3?

\$\endgroup\$
2
  • \$\begingroup\$ Why is this being down-voted? \$\endgroup\$ Commented Jul 1, 2019 at 20:43
  • 1
    \$\begingroup\$ community here is like this, the reason stackexchange is dying. Down vote compensated. \$\endgroup\$
    – Deep
    Commented Oct 9, 2019 at 15:52

1 Answer 1

0
\$\begingroup\$

VΦ = VT because it's delta-connected.

\$\endgroup\$