Currently I'm building the electric part in my converted RV. I got all components that I need and want to start to wire them now. But my biggest lack of understanding is the grounding part.

The power inverter needs to be grounded, that's for sure, and is mentioned in the manual. Grounding the AC breaker box is for sure, just because it's 120V and needs to be grounded. But I'm unsure about grounding the battery bank. I asked an electrician and he told me that I don't need to ground my battery bank. But after a lot of research I found many diagrams online where the battery bank is grounded.

So my questions:

  1. Do I need to ground my battery bank? (2x 12V GEL Batteries connected in parallel)

  2. When doing this, will I have problems with the lights, heater etc. of my RV? Everything is just connected with a plus wire and grounded to the metal frame. My starter batteries are grounded to the frame as well.

  3. When doing this, which cable size should I choose? Mostly all other components are wired with short 4 AWG cables. But the grounding wire will have a length of 7 feet.

  4. Can I ground the AC breaker box on the same metal frame as the other components? For my understanding I've the 12V minus and 120V grounding connected on the same place. Is this possible?!

  5. The manual of my solar charger mentioned that the charger is positive grounded and when I have a negative grounding system I shouldn't ground it. So I don't need to ground it? I attached a screenshot of the manual.

Diagram

Solar Charger Manual

I'll appreciate your help.

\$\endgroup\$
2
  • 2
    \$\begingroup\$ I am hesitant to answer this question because it is surprisingly complicated. But if you could update your question to include the make and model of your inverter and solar charge controller and links to the manuals, that might improve your chances of getting a decent answer. Also, are you going to have a "shore power" connection? \$\endgroup\$
    – user57037
    Mar 28, 2020 at 5:54
  • 1
    \$\begingroup\$ Sure, no problem. Inverter: renogy.com/2000w-12v-pure-sine-wave-inverter Solar Charger: renogy.com/rover-li-40-amp-mppt-solar-charge-controller (This model, but with 60A. They don't sell this model anymore) Under the tab "Downloads" you find the manuals. No, no short power in this system. \$\endgroup\$
    – cYbton
    Mar 28, 2020 at 13:13

1 Answer 1

2
\$\begingroup\$

It's probably better to stop using the word 'ground'. It's used for too many things, and not well understood.

In the case of vehicles, the chassis is usually used as a 'common return', and these days, that's usually the negative terminal of the battery.

The chassis is the large system you're working within, so stick with this convention to avoid messing with any of the vehicle circuits. Connect the negative of your batteries to the chassis. Connect the inverter negative input to the battery negative (preferably, or chassis if it's a long way away). Connect the neutral and safety ground of the inverter output to chassis. Connect your 12v loads' negatives to chassis or battery negative. Connect the neutral and safety ground of AC sockets as suggested in the inverter manual, they may prefer them to go directly to the inverter, or go via the chassis, that's a safety and regulations issue rather than a physics issue.

The wires between terminals and chassis need to be large enough to carry the current flows expected. If the inverter input travels through the chassis, then the ground bonding wires for battery and inverter need to be rather thick. If the inverter connects directly to the batteries, then the bond wire to chassis from that connection can be sized for the other loads.

Your charger subsystem has been designed to use a common positive +12 V connection between its components. The panels, charge controller, and batteries all share a common wire. Let's call this the PG wire. Connect the PG wire to your battery positive. Connect the panels and charge controller to the PG wire. Connect the panels and charge controller other terminals as they specify in their diagrams.

Keep all wires and metal boxes of the solar sub-system isolated from chassis. The PG wire is not at chassis potential. The panels negative is not at chassis potential. It's best to connect the charger negative directly (via fuses/isolators as required) to the battery negative, not via the chassis.

Both battery terminals are now connected to their own 'common return', the negative to the chassis, the positive to the PG wire. As far as each system is concerned, all the components are wired correctly. This is the only place where there is connection between the two systems. Notice this follows the instructions given in the PG charge controller subsystem, to not ground (aka connect to chassis) when adding to a negative ground system.

\$\endgroup\$
9
  • \$\begingroup\$ This is a pretty good answer. OP's diagram shows a 200 A fuse and a 2000 W inverter. So what do you reckon, 3/0 or 4/0 wire from battery to inverter? \$\endgroup\$
    – user57037
    Mar 28, 2020 at 6:06
  • \$\begingroup\$ Wow thank you very much. This is a well-defined answer. When I understand everything right, I can ground my components like in the diagram. Battery, Inverter and AC Breaker Box to the metal chassis. Is is better to use different wires and different mounting places on the frame? I understand your answer about the positive grounded solar charger, that I shouldn't ground it. But when talking about solar panels they are mounted on the roof. I've a lot of screws that are connected to my metal roof. I think there is no alternative. Will this be a problem? \$\endgroup\$
    – cYbton
    Mar 28, 2020 at 13:49
  • \$\begingroup\$ You can have screws in contact with the metal roof, as long as they don't contact any conductors in the solar panel. If the panels' mounting points are connected to panel wires, then you will need to isolate. While you could use insulating washers, I would tend to go for something with a less likelyhood of mis-assembly and failure, so fitting the panels to a fibreglass (GRP) sub frame, which is then attached to the roof. \$\endgroup\$
    – Neil_UK
    Mar 28, 2020 at 15:35
  • \$\begingroup\$ Ok good to know. Now I just need to know which wire size I need for the battery grounding cable. As mentioned above all other wires are short 4 AWG ones, only the inverter has a 2 AWG one. I need a length of 7 feet. What do you recommend? \$\endgroup\$
    – cYbton
    Mar 29, 2020 at 3:43
  • \$\begingroup\$ I don't have a specific RV knowledge of regulations, only physics. Are there any RV regulations that would apply to you? What currents do you expect to flow through that cable? What voltage drop are you happy to tolerate? BTW, I would expect it to be very unlikely that mounting screw holes in a solar panel frame would be making contact with the conductors, but then I don't know your specific panels. \$\endgroup\$