I am designing a PID temperature controler; as far as I managed to write it so far, you find the code below.
Can you please help me check if Integrator wind up and other PID elements are configured please?
When i run the code at some point close to the set point , it starts behaving like an ON and OFF code
I don't know if this is a valid question but im asking it anyways .
and if you can make any edits . i will be glad to check them out
// programing the pid
const int pin = 3;  // PWM analog output
double cumerror = 0; // Initialising the cumulator of the integrator to 0
double input, setpoint, integral, proportional, piderror, pidvalue;
// Input values
double kp = 25; // seting proportional at 25
double ki = 0;  // seting the integral at 0
void setup() {
  setpoint = 37; // seting the setpoint at 37
  Serial.begin(9600);
void loop() {
  double inputvalue = map(analogRead(A0), 0, 1023, 0,
                          100); // reading the values from the analog signals
                                // and mapping it to a 100 deg scale
  piderror = setpoint - inputvalue; // calculating the error
  // calculating the integral ((Naturally ki= cumerror *dt), we do not have to
  // multiply by dt, since dt = 0 because i am using the sample time delay(1000)
  // every time )
  cumerror += piderror;
  integral = ki * cumerror;
  // calculating the proportional error
  proportional = kp * piderror; // calculating the proportional error
  // changing the P and I parameters as the error approaches the set point
  if (3 < piderror < 10) {
    kp = 10;
    ki = 0.5;
    cumerror += (1 * piderror);
  // Making the parameters =0 as the error approaches more 0
  if (piderror < 3) {
    proportional = 0;
    pidvalue = 0;
    integral = 0;
  pidvalue = proportional + integral;
  if (pidvalue <= 0) {
    pidvalue = 0;
  if (pidvalue > 255) {
    pidvalue = 255;
  analogWrite(pin, pidvalue); // sending the pid value to the heater
  delay(1000);
  cumerror=cumerror;
    \$\begingroup\$ Where are your design specs? > Max Temp. rate of change expected. load profile, error tolerance, resolution, step change overshoot? \$\endgroup\$ Jul 14, 2020 at 16:48
    \$\begingroup\$ Maybe you could explain what you are trying to implement rather than dumping the code. You have a PI controller with no antiwindup and are doing some weird stuff near the setpoint is what I make of it. \$\endgroup\$ Jul 14, 2020 at 17:03
  • \$\begingroup\$ Your code is poorly formatted, making it difficult to read and difficult to debug. Please edit to fix that first. Indent it properly and consistently. Remove blank lines within a section unless they are required for clarity. Remove all the Serial.print() lines as they (should) have no affect on the operation - unless you suspect there is a problem there (in which case you should explain why you think there is a problem or why we need to see them). Remove spaces before punctuation , or ; and add spaces after punctuation for legibility and clarity. i.e, Make it look professional. \$\endgroup\$
    – Transistor
    Jul 14, 2020 at 17:11
  • \$\begingroup\$ Marcus has tidied the code for you. Why are you manipulating the P constant based on the value of piderror? \$\endgroup\$
    – Transistor
    Jul 14, 2020 at 17:32
  • \$\begingroup\$ @Transistor , yeah , because i am assuming as the temperature approaches the set value , to reduce te PID error , i should reduce both P and I \$\endgroup\$ Jul 14, 2020 at 17:35
KP, KI and KD are usually fixed and not manipulated based on the error as you are doing. Instead try and get the controller working as P-only.
Try reducing it to this and get P-only control working properly: -
  pidvalue = 0;
  pidvalue = 255;
Start with a much gentler KP - maybe 1 or 2, try it out and report back. Plot a graph if you can and edit it into your question. We'll proceed from there.