Okay so I was replacing some sockets the other day and accidentally got a small shock (for some reason one upstairs socket was not connected to the upstairs sockets breaker...) Anyway I only felt a small tingle in my finger and I'm trying to discern what happened. I was sat directly on top of carpet, and the breaker did not break upon being shocked. Which of the following is correct:
  1. If I only touched one wire it must have been the live wire. The only way I could have felt a shock from the neutral is if there was a significant current draw elsewhere, but the property is empty with next to no appliances plugged in. So it must have been the live. In that case why did I only feel it in my finger? The current would flow down my arm to my legs and to ground. I get carpet is a great insulator but even so surely I should have felt it somewhere other then my finger? Also shouldn't the breaker have switched upon current flowing down live but not detected back on neutral (even if this current was tiny)?
  2. I somehow bridged live and neutral with my finger. The current only flows between a small section of finger and thanks to the high resistance of my skin only a small current flows. The breaker doesn't switch because this is perfectly normal behavior. What I don't understand is from what I have read I would expect my finger to at least burn slightly, rather than a small tingle and no discernable mark on my finger. Also since I would have to have touched one wire first (law of probability) I suppose it would have had to be neutral then live (else we're back to 1)?
  • 4
    \$\begingroup\$ You can feel about 1mA and the RCD/GFCI won't trip until you get to 5-30mA. \$\endgroup\$ Jul 23, 2020 at 1:06
  • \$\begingroup\$ The real question is Why are you working on a powered circuit?" \$\endgroup\$ Jul 26, 2020 at 0:34
  • \$\begingroup\$ Two is a possibility also. It is possible for a light touch to produce only a very small current. It depends on many things (for example if your hand is moist and if you have callouses on your hand, etc). \$\endgroup\$
    – user57037
    Jul 26, 2020 at 4:28
  • \$\begingroup\$ sitting on the carpet !!! the voltage that enters ur finger, I hope u realize from where it will reach the ground \$\endgroup\$
    – Indraneel
    Jul 26, 2020 at 6:10
You could have felt the shock only in your finger because that small point was where it all entered and therefore had the highest current density, and once it was inside you, the charge spread out while flowing through you thereby reducing the current density. I would think if you were standing on just a tippy toe you would also have felt something there too.
The closest I ever got to be shocked was when I was holding two wires on some ~50V (I think?). I felt a tingling in both my hands where the current entered and exited.
  • \$\begingroup\$ okay that would make sense but surely the breaker should have switched though? \$\endgroup\$ Jul 22, 2020 at 21:12
  • \$\begingroup\$ @Mr_Random_Guy Your breaker trips at ~15A (in North America anyways) otherwise you wouldn't be able to plug a lamp or toaster into it. If 15mA were flowing through you, you would not be here to ask about it, let alone 15A. \$\endgroup\$
    – DKNguyen
  • \$\begingroup\$ Right but the breaker should switch at any current if its flowing down live but not back on neutral right? \$\endgroup\$ Jul 22, 2020 at 21:13
    \$\begingroup\$ @Mr_Random_Guy Oh, that's not a breaker. That's a GFCI. Did your circuit have one? \$\endgroup\$
    – DKNguyen
    Jul 22, 2020 at 21:14
    \$\begingroup\$ All circuits are required to have a GFCI in the European Union, as I understand it, but for some reason there is no such requirement in the US. \$\endgroup\$
    – Hearth
    Jul 22, 2020 at 21:39
Assume capacitance, as you sat, created by 30cm by 30cm area, thru 1cm of carpet, into underlying conductive underflooring/concrete.
Using C = E0 * Er * Area/Distance, with E0 = 8.9e-12 farad/meter and Er = 5, we now have
C = 45e-12farad/meter * Area/Distance
C = 45-12 * (30cm * 30cm / 1cm ) * 1meter/100 cm
C = 45e-12 * 900/1 * 1/100 == 45 * 9 pF = 405 pF. Call it 500pF
Now, from Q = C * V, and differentiating with constant dC/dT using chain rule,
I = C * dV/dt
and for clean power line sin, you have dV/dT = 160v peak * 377 radians/second ~ 60,000 volt/second.
I = 0.5e-9Farad * 6e+4 volt/sec= 3e(-9 + 4) = 3e-5 = 30 microAmps
which is well below the danger (heart pulsations, or muscle lockup), but enough to feel.
  • \$\begingroup\$ Okay, so the current was too small to trip the GFCI but enough to feel? And thanks for the maths! \$\endgroup\$ Jul 23, 2020 at 9:48
-2
Some electricians in Canada and the US di not use a light or a meter to test if a circuit has 120VAC. Instead they use their fingers.
  • \$\begingroup\$ This doesn't really answer the question, does it. \$\endgroup\$ Jul 25, 2020 at 23:47
  • \$\begingroup\$ And it is promoting unsafe behaviour... \$\endgroup\$ Jul 26, 2020 at 0:32
  • \$\begingroup\$ Lots of electricians are willing to work on energized circuits, too. But I don't do such things nor recommend it to non-electricians. \$\endgroup\$
    – user57037
    Jul 26, 2020 at 4:25
  • \$\begingroup\$ that doesn't mean much.... 110 V and wooden houses !! electricians in India do this regularly 230V and humid brick houses. ... (full 230V has a jarring impact on the whole arm... for a 10 year old kid... don't ask me how I know) \$\endgroup\$
    – Indraneel
    Jul 26, 2020 at 6:07