3
\$\begingroup\$

I am certain this question has been asked before but I search and cannot see anything just yet. I read most AC current is 60 cycles per second in the United States and some say 50 but that does not matter to the question.

I am thinking a typical electric generator belonging to a hydroelectric plant generating power. The generator has some value for the revolutions per second as the water produces mechanical motion to spin its rotor. As the rotor spins the polarity switches from positive negative and visa versa. Is it the case that this value is the same as the 60 cycles per second that feeds into my home?

The transformer I believe does not affect frequency so must the frequency produced at the generator match the value at the electric plug. It is such a precise value I have difficulty thinking it is the speed of the generator but I do not know so I ask.

\$\endgroup\$
8
  • 3
    \$\begingroup\$ You are correct. Number of poles matters too. It is possible to produce multiple electrical cycles from a single mechanical revolution. That way, the turbine can spin more slowly so the water can be traveling slower, but pushing harder. They continuously adjust the speed to keep it so precise. They do this by adjusting the strength of the magnets (field) which changes the mechanical resistance/torque but also changes the sine wave amplitude. I don't know how or if they control RPM and amplitude independently. \$\endgroup\$
    – DKNguyen
    Aug 4 '20 at 14:22
  • 2
    \$\begingroup\$ @DKNguyen I guess we lust built the speed control sytem over generator by control water flowrate to fix frequency after that voltage can use magnetic field strength to adjust output power. \$\endgroup\$
    – M lab
    Aug 4 '20 at 14:30
  • 1
    \$\begingroup\$ @Mlab Ah that makes sense. Throttle back the water or steam. Two degrees of freedom. \$\endgroup\$
    – DKNguyen
    Aug 4 '20 at 14:38
  • 2
    \$\begingroup\$ Across the whole grid, the frequency actually drops when load is added, because those large spinning machines slow down slightly. Not much ... maybe 0.01 or 0.1Hz. Network operators watch this frequency drop and start another generator if necessary. (Slightly over-simplified). In the UK you can watch the grid frequency in real time, at gridwatch.templar.co.uk Mayeb you can find a similar site for the US. \$\endgroup\$ Aug 4 '20 at 14:56
  • 2
    \$\begingroup\$ Rotor speed is controlled by the governor (input power), not by the field. \$\endgroup\$ Aug 4 '20 at 16:31
2
\$\begingroup\$

It's a market evolution, and partly a product of Edison's sour grapes in losing the DC vs. AC war with Westinghouse.

tl; dr version: 40 and lower flickered with lights, 50 was acceptable, 60 worked better with arc lights (flicker again), higher frequencies than those were less compatible with generators and induction motors, based on Tesla's work. So Westinghouse ultimately settled on 60Hz.

Edison, meanwhile, had a hand in AEG (Germany) choosing 50 as a way to create a separate (some would say, monopolistic) market in Europe. Edison was kind of a jerk that way.

More about all that here: https://www.quora.com/Why-is-60Hz-AC-used-in-America-What-are-the-advantages-and-disadvantages-of-using-60Hz

\$\endgroup\$
1
  • \$\begingroup\$ I will accept the answer ...It's amazing how to get the generator to make that sweet spot of 60 cycles. \$\endgroup\$
    – Sedumjoy
    Aug 5 '20 at 21:13