I have a second-order unity feedback control system with forward transfer function $$G(s) = \frac{10}{s(s+2)}$$
Here damping ratio, $$\zeta = \frac{1}{\sqrt{10}}$$ and natural frequency, $$w_n = \sqrt{10}$$
First, I gave a unit step input to the system. Now I can calculate the maximum overshoot of the unit step response from $$\%M_p = e^{\frac{-\zeta\pi}{\sqrt{1-\zeta^2}}}$$ and settling time from $$t_s = \frac{4}{w_n\zeta}$$
Now, If I give a unit ramp input to the system, Can I use the same formulas above to calculate settling time and maximum overshoot?
For reference, this is my unit ramp response in the time domain $$y(t) = -\frac{1}{5}+t+\frac{1}{5}e^{-t}Cos(3t)-\frac{4}{15}e^{-t}Sin(3t)$$
As you can see, this is uniformly increasing. How can I find settling time from this? Can I just equate y(t) with unit ramp input and find the time at which they are equal?
    \$\begingroup\$ If I remember correctly, the formula is obtained as the maximum value of the transient response compare to the desired one being constant. Now with a ramp, the desired value change over time. So you can not use it to give accurately the maximum overshoot. If will give you a superior bound which can not be exceeded. \$\endgroup\$ Aug 15, 2020 at 8:25
    \$\begingroup\$ Concerning the seetling time, you can not use the formula as well. By the way, in a system specification (in electronic), it is expected to give the maximum error expected associated to the settling time. For instance a settling time to 0.01% of 15ns. \$\endgroup\$ Aug 15, 2020 at 8:28
  • \$\begingroup\$ I have added the ramp response of my system. Can you help me in finding the settling time? \$\endgroup\$ Aug 15, 2020 at 8:37
  • \$\begingroup\$ Why did you ask the same question again? You could have just edited it. \$\endgroup\$ Aug 15, 2020 at 9:40
  • \$\begingroup\$ Sorry, I am new here. I deleted the other question \$\endgroup\$ Aug 15, 2020 at 9:43
In a nutshell, the error is the difference between desired output and the one you got: $$e(t) = y^*(t) - y(t)$$
Then you resolve $$e(t) < ErrorMax$$.
To simplify the comparison note that $$sin(a + b) = sin(a)cos(b) + sin(b)cos(a)$$ so $$ a cos(\omega t) + b sin(\omega t) = M sin(\omega t + \phi)$$ where $$ M = \sqrt{a^2 + b^2}$$ and $$\phi = atan(a/b)$$
In consequence, you get something in the form $$M sin(\omega t + \phi) e^{-t} < ErrorMax$$
  • \$\begingroup\$ Consider that the absolute value of the error should be less than ErrorMax \$\endgroup\$ Aug 15, 2020 at 9:39
  • \$\begingroup\$ So the upper bound should be taken as my overshoot right? What about settling time? \$\endgroup\$ Aug 15, 2020 at 9:44
  • \$\begingroup\$ If you expect a settling time for an error less than 0.1, solve $$M|\sin(\omega t + \phi)| e^{-t} < 0.1$$. The value of t is the settling time (in this case close to 0.961). The overshoot is the maximum value of the error where $$y > y^*$$. So the overshoot can exceed the limits you desire \$\endgroup\$ Aug 15, 2020 at 9:57