I am trying to use a digital multimeter to measure a house solar panel installation. I'm just learning, but I can't find a good answer to my problem.
I tested the voltage on a 1.5 AA battery and as I moved the knob to higher voltages (from 200 mV to 1000 V) I get very divergent readings:
  • 200 mV : 1 (overloaded)
  • 2000 mV : 1580
  • 20 V : 2.56
  • 200 V : 12.4
  • 1000 V : 111
I don't know if I'm wrong, but I was thinking that as I increase the max voltage I'd get smaller values, but this jumps from 1580 to 2 then 12 and then 111, the pattern doesn't seem to grow evenly in the last 3 values either.
My original goal was to measure voltage in what was to be a 12 V installation, I got these readings:
  • 20 V : Overloaded
  • 200 V : 105+
  • 1000 V : 935+
I take it has more than 20 V, but the other readings don't make sense so I don't know how to interpret them.
Am I missing something, is there something I don't know?
    \$\begingroup\$ What multimeter are you using exactly? \$\endgroup\$
    – Ron Beyer
    Commented Aug 29, 2020 at 21:00
  • \$\begingroup\$ Are you sure the multimeter is not broken? \$\endgroup\$
    – Justme
    Commented Aug 29, 2020 at 21:38
    \$\begingroup\$ Replace the battery. If it still reads bad your meter is defective. \$\endgroup\$
    – td127
    Commented Aug 30, 2020 at 1:27
  • \$\begingroup\$ Just Learning: don't do that on house solar panels. They carry hundreds of volts, and disconnecting a cable may be dangerous. Hey, this is solar POWER. Keep learning on AA batteries! Or on a solar cell from e.g.. a garden ornament. \$\endgroup\$
    – Roland
    Commented Sep 28, 2020 at 14:16
First, if you don't know what voltage you are dealing with, you should set your multimeter to the highest voltage range available and go down until you get an acceptable accuracy.
Failing to do so, it is quite possible to damage your multimeter with a voltage 10x the range or more. It may as well be safe - depending on the multimeter. You didn't say your multimeter model.
In your particular case, it looks like your multimeter is broken or you are doing something profoundly wrong.
A sane multimeter connected properly to a fresh 1.5 AA battery will show:
200 mV : 1 (overloaded) - CORRECT
2000 mV : 1580 - MAYBE CORRECT
20 V : 2.56 - WRONG, it should be 1.58 or near it.
200 V : 12.4 - WAY TOO WRONG, it should be around 1.6
1000 V : 111 - if you can touch it without dying or at least swearing out loud, it is not 111V
What could be wrong?
  1. Multimeter battery is depleted. Some of these have "low battery" indicator while others don't have one. A lot of $10 multimeters will show "low battery" if the battery is near end and not show anything about the battery if it gets even lower.
  2. You are using AC setting for 20/200/2000 range instead of DC and the multimeter is one of those for $10
  3. You have a great deal of electromagnetic interference from other power equipment in your place.
  • \$\begingroup\$ 4: possibly current probes are connected instead of voltage probes. \$\endgroup\$
    – glen_geek
    Commented Aug 29, 2020 at 22:24
  • \$\begingroup\$ I'll look into it tomorrow but it sounds it could be damaged. Multimeter is the cheapest I could find, brand probably nobody's ever heard. Thank you. \$\endgroup\$
    – Rincewind
    Commented Aug 30, 2020 at 2:58
-1
my pool motor went out so i got my multimeter and measures from ground to a leg and got 220 volts the same on the other leg. then i measured across both and got 440. I then took my breaker panel cover off and measured across the 100 amp breaker it started at 360 and went up to 440. to make a long story short i took the multi meter apart and measured the 12volt battery which stated at 10 then dropped to 5. so my readings were way off.Moral of the story check your battery if your getting weird readings.