I read that power factor shows how much there is the apparent power, which circulates between power lines and the load and does nothing but heats up the transmission lines and transformers in them. They say that this is due to the current being out of phase with voltage. Particularly, power flows out of the load when voltage is positive but current is negative.
Also, I see that diode rectifier conducts only at the short moments of peak voltage, when input voltage exeeds the load voltage (rectifiers have an output capacitor = load voltage). So, all the power is consumed during these short bursts. I have read one an article saying that people do not understand anything and the whole problem is not power factor but these bursts that overload the transformers in power lines (it is not allowed to make large currents in transformers because of danger of magnetization loss). But, when you consume all power during very tiny fraction of the sine, huge current happens. Obviously, the current is not proportional to the voltage as it should in the reference (resistor) load with power factor of 1. But, I do not see any negative power here! The rectifier precludes having positive input voltage and negative current. All current is positive under peak positive voltage. So, how does the non-linear load produce the apparent power?
In other words, Wikipedia says http://en.wikipedia.org/wiki/Switched-mode_power_supply#Power_factor
Simple off-line switched mode power supplies incorporate a simple full-wave rectifier connected to a large energy storing capacitor. Such SMPSs draw current from the AC line in short pulses when the mains instantaneous voltage exceeds the voltage across this capacitor. During the remaining portion of the AC cycle the capacitor provides energy to the power supply.
As a result, the input current of such basic switched mode power supplies has high harmonic content and relatively low power factor.
How do they conclude that harmonic content produces the low power factor? Where the apparent power comes from?
I understand that current has harmonics (frequency components) which means that it oscillates forth and back while voltage remains of single polarity. It might be that these high-frequency oscillations of current produce the apparent power. However, the net flow is still positive, the current still flows only in one direction, corresponding to the voltage polarity and oscillations do not make it flowing in opposite direction to cause the apparent power.
The point you seem to be missing is that it does not require power transfer from the device back to the power line during part of the power cycle to have less than unity power factor.
There are various ways of looking at what power factor really is, although they all come out the same mathematically. One way is the ratio of real power delivered to the product relative to the RMS voltage and current. If the current is a sine (let's consider the voltage always a sine in this case, since the power line has such low impedance), then you have unity power factor when it is in phase with the voltage, and 0 when 90 degrees out of phase. In the case of a sine, power does have to flow back to the line during part of the cycle to have less than unity power factor.
However, lots of other waveforms are possible. You can have current that is always 0 or positive when the voltage is positive, or 0 or negative when the voltage is negative, but that is not a sine. The spikes you mention caused by a full wave bridge are a good example. Power never flows back to the power line, but yet the power factor is less than 1. Do some examples and calculate the RMS current drawn by a full wave bridge. You will see that the total real power drawn from the power line is less than the RMS current times the power line voltage (again, we are assuming the power line voltage is always a sine).
Another way to think of this is that losses in the tranmission system are proportional to the square of the current. The full wave bridge draws its current in short spikes of high magnitude. Because of the squared nature of the losses, this is worse than the same average current drawn more spread out. I you work out that math, you realize that the way to minimize the average square of the current is to make the current be a sine in phase with the voltage. That is the only way to achieve unity power fator.
Yet another way of looking at this, which you alluded to, is to think of the Fourier expansion of the current. We are assuming some current waveform that repeats every power line cycle, so it has a Fourier series. Any such repeating waveform can be expressed as a sum of a series of sine waves at the power line frequency and positive integer multiples thereof. For example with 60 Hz power, the waveform is a sum of sines at 60 Hz, 120 Hz, 180 Hz, 240 Hz, etc. The only question is what the amplitude and phase shift of each of these harmonics are. It should be obvious that only the fundamental (the 60 Hz component in this example) is capable of drawing any net power from the power line, and that only to the extent it is in phase with the voltage. Since all components are sines, each will draw power during part of the cycle and return the same power at another part of the cycle, except for the in-phase component of the fundamental. So your way of looking at power factor as having to put power back during part of the cycle is valid if you break up the current waveform into sine wave components. However, it is possible to have a set of sine wave components that take and return power to the power line at different times such that the net from all components at any one time is zero or positive. The full wave bridge current is one example of such a waveform.
  • \$\begingroup\$ If losses are proportional to the current squared then, intuitively, I feel like the best way to minimize them is a constant current, not sine. But, I am not familiar with math. Also, I can think of DC of 1 ampere as a sum of 1-1+1-1..+1=1. So, you see how many (virtual) currents are flowing. So, there must be a lot of apparent power and transmission losses everywere. However, no useless transmission happens because only net flow is real. That is why I am telling that virtual harmonics cannot cause losses due to apparent power and are very different from the square-based losses. \$\endgroup\$
    – Val
    Dec 28, 2012 at 15:04
    \$\begingroup\$ @Val: I can't figure out part of what you are saying and the rest is just plain wrong. You really need to do the math. \$\endgroup\$ Dec 28, 2012 at 16:50
  • \$\begingroup\$ I like the Fourier approach! I think it is important to realize that \$PF\neq cos(\phi)\$ in some cases. That would only be true with sine waveforms of the ground frequency. \$\endgroup\$