A few questions about three phase AC induction motors. All questions relate to a Wye connected motor, running off 120V rms (phase-neutral), each phase 120° apart. This is a pure and simple three phase motor; there is no starting circuit, overload protection, extra circuitry, etc.

Three Phase AC Induction Motor Wye Connected

  1. If I know the phase resistances, input voltage, and how the motor is wired (wye), is this enough to calculate locked rotor current? Everything I've found relates NEMA ratings to locked current ranges but I have a custom designed motor and need to calculate locked rotor current from the info I have.
  2. If I start a 3 phase motor with 1 phase (i.e. with power off, open the contacts to Phase B and C, leave Phase A closed, then apply power), what would the current on that phase be when voltage is applied? Would it just be the 120V divided by the phase-neutral resistance since the rotor would not rotate?
  3. If I started the motor with all 3 phases (normal operation), then dropped to just Phase A (as in question 2), would the rotor continue to rotate (assuming my power supply has no current limit)? What current draw is to be expected here (relative to steps 1 and/or 2, assuming there is a way to calculate/approximate it)?
\$\endgroup\$
3
  • \$\begingroup\$ Consider: An asynchronous machine is the same as a transformer with a shorted secondary. If you lock the rotor, the only thing that changes is there is no mechanical power output. All active power is turned into heat. (And the slip is always 1) \$\endgroup\$
    – Janka
    Dec 11, 2020 at 21:40
  • \$\begingroup\$ OP meant squirrel cage rotor? \$\endgroup\$
    – user263983
    Dec 11, 2020 at 21:55
  • 1
    \$\begingroup\$ Please feel free to take a couple of steps back and tell us what you have (do you have a motor or just a design?) and what your goals are (why do you need to know or think you need to know the locked rotor current?). Maybe more light can be shed on all this if you share a bit more information. No guarantee, of course, but sometimes it works out that way. \$\endgroup\$
    – user57037
    Dec 11, 2020 at 22:06

2 Answers 2

1
\$\begingroup\$
  1. No. The field coils are coupled to the rotor and the combination looks like a transformer with a shorted secondary. The characteristics of the rotor will effect this current.

  2. No for the same reason.

  3. The rotor will continue to rotate but you now have an asymmetric rotating field which will lead to rough running and loss of torque. The amount of slip will have a large effect on the current (coupling with the rotor again) and I will not even try to estimate this.

Overall, give the number of variables your best bet would be to measure these values.

\$\endgroup\$
1
  • \$\begingroup\$ Thank you. Follow on question... I actually already tested the 3 phase locked rotor current draw, that is 45 Amps rms per phase (intent of me asking above was to correlate results). So based off your answer, there is no way to approximate the current draw for running and/or starting off 1 phase? For example, I've read that dropping 1 phase/running on 2 phases (for 3-phase ac induction motor) should increase the draw per phase by sqrt(3). I found a pretty similar result in test (16 amps vs 28 amps). \$\endgroup\$
    – jmansfield
    Dec 11, 2020 at 22:36
1
\$\begingroup\$

The line-neutral equivalent circuit of one phase of an induction motor is shown below. The rotor circuit, consisting of X2, R2 and R2(1-s)/s is connected to the stator components through an ideal transformer. The transformer is usually not shown and the rotor component values are adjusted accordingly. The input terminals correspond to the motor's phase and neutral points.

enter image description here

When the rotor is locked, s = 1, so (1-s)/s = 0/1 = 0. Therefore the locked rotor current is determined by R1 in series with X1 with that combination in parallel with the series of rotor components in parallel with the magnetizing branch components, G and B. Therefore the winding resistance, R1 is considerably less than the total impedance that determines the locked-rotor current.

Three-phase motors normally do not have the neutral connected externally. That point may not even be accessible. If that point is available and rated voltage is applied, the resulting current would be approximately the same as the locked-rotor current. Locked rotor current with voltage applied to two phases without a ground connection will be approximately the same as half the line voltage divided by the normal line to neutral voltage (208/2)/120 = 87%.

If one phase of a three-phase motor is disconnected while the motor is running, the remaining winding creates something like a single-phase motor. It is like two magnetic fields rotating in opposite directions. In the direction that the motor is already rotating, the torque is strong, because the slip is comparable to the normal operating slip. However the torque is less than normal because the voltage per winding is about 87% of the normal voltage. The torque produced by the reverse-rotating magnetic field is smaller because the slip is nearly 2. However the resulting torque is significantly less than the motor's normal torque. The reduced torque capability will be compensated somewhat by increase slip, but that will result in increased current.

\$\endgroup\$