Scenario: Installing a grounded center-tapped transformer in an ungrounded system on a ship.

We have eight 11 kV to 460 V ungrounded three-phase delta-to-delta transformers feeding as many switchboards. We will often get a ground faulted phase on these switchboards, due to the many consumers. We have ground fault detection and we usually find the culprit in a few hours. On one switchboard there is a "single-phase" transformer with a grounded center-tapped neutral secondary that is installed in a temporary office container. It is being fed with two legs of 460 V.

What actually happens when one of the phases that feeds this "single-phase" transformer goes to ground? You are essentially connecting one of the primary phases to the center tap on the secondary. What voltages will present themselves and in potential to what? You will obviously have 460 V potential to the primary creating some hybrid autotransformer.

Is there possibly a bucking/boosting effect that can take place? Are there dangers associated with this installation? Am I overreacting?

\$\endgroup\$
2
  • \$\begingroup\$ Are your generators grounded via a reactance or resistor? At 11kV, it is strange to see ungrounded generators to limit current in a short circuit. And you are not over-reacting. \$\endgroup\$ Apr 4, 2021 at 16:46
  • \$\begingroup\$ Each 11KV bus is earthed through an 11KV to 220v earthing transformer into a 10 Ohm earthing resistor. Sorry for the unclarity, I am only speaking ungrounded at 460 and below. \$\endgroup\$ Apr 4, 2021 at 19:12

2 Answers 2

0
\$\begingroup\$

The lack of clarity in your question would be greatly reduced with some diagrams. In most situations, connecting transformers to ground simply sets what 0V is in relation to each other. Each voltage source can produce positive or negative voltages at any moment in time in relation to ground or 0V.

In a well designed system, the voltage of ground will only differ significantly from point to point when massive ground currents are flowing, which should trigger a shutdown, whether blown breaker/GFCI or actual generator shutdown. This allows us to just assume ground is 0V.

Transformers perform electrical isolation, so having the secondary grounded differently from the primary is not a problem. If electrical isolation breaks down, you could see full primary voltage on the secondary, so then you have bigger problems than where your ground is attached. In this case the transformer has been destroyed, typically resulting in a large fault current to trip the upstream overcurrent or ground fault protection. Depending on how the fault occurs, primary voltage could appear on the secondary for long enough to damage secondary systems.

When split single phase is added to a 3 phase system, sometimes the primary is connected to only 1 phase of that system to achieve "true" split phase where the positive and negative voltages directly oppose each other in time rather than the \$1:\sqrt{3}\$ ratio achieved with a 3 phase wye arrangement. Advantages include having fewer wires to the primary and simpler wiring on the secondary and a more useful line to line voltage.

As soon as you start putting single phase loads on a 3 phase system, load balancing becomes an issue. Ideally load imbalance should be small compared to the total power of the system. As long as there are a sufficient number of panel sized single phase loads that they can be spread across the phases of the system, there is no advantage to running 3 phase to all of the smaller loads fed by the panels.

What actually happens when one of the phases that feeds this "single-phase" transformer goes to ground?

A large current flows from the source feeding the primary, tripping the upstream overcurrent or ground fault protection device. The ground reference of the secondary is irrelevant in this case as the fault will shunt current away from the primary winding feeding the secondary, and the current is flowing back to source.

What voltages will present themselves and in potential to what?

All non-isolated voltages will present themselves as positive or negative at any moment in time in relation to ground. One of the coils on the secondary will be in opposition to the primary and one will be in agreement with it. If you cross connect the systems line to line, the highest voltage you could get would be a line to line sum of the line to ground voltage of the primary (460V / \$\sqrt{3}\$ = 265V) and the line to ground voltage of the secondary (presumably 240V / 2 = 120V). The resulting line to line voltage of 385 is less dangerous than the 460V line to line of the source system. Note that in this case, for current to flow, both systems must be ground referenced somewhere in order to form a loop.

Is there possibly a bucking/boosting effect that can take place?

No, you would need an absurdly large reactance to achieve bucking or boosting at line frequencies. Transformers change voltage by modifying turns ratios of common core inductors rather than with a boosting or bucking effect. You can also take multiple transformers and parallel the inputs and series the outputs to increase voltage, but in the end this just amounts to messing with turns ratio. If you just mean is it possible to end up with a lower or higher voltage than you expect at some point in the system, or between two points, this particular transformer connection is not particularly concerning. On the primary it is no more dangerous than the system it's connected to and on the secondary, with a split phase output, the highest voltage to ground without transformer failure is half the line to line voltage, which is optimal for safety and significantly safer than the 460V system.

Are there dangers associated with this installation?

You're adding a less dangerous system as a load on a more dangerous system. As long as components are correctly selected, there's nothing extra dangerous about doing that. Beyond that, there are only the usual balancing risks to adding a single phase load to a 3 phase generator.

Am I overreacting?

Better safe than sorry. A pound of research is worth two birds in the bush. That said, if you don't fully understand transformers, single-phase and 3-phase systems yet, you should probably not be particularly comfortable working on them unless there is a qualified person present directing you who does. Then again, not every Journeyman is good at 'splainin' this kind of thing and that's why electricians also go to school.

\$\endgroup\$
2
  • \$\begingroup\$ Very nice. Since this is an ungrounded system for reliability, we use ground fault detectors that notify us when a phase goes to ground. Nothing trips in this condition unless a second phase goes to ground. Does this information make the ground reference of the secondary relevant? \$\endgroup\$ Apr 5, 2021 at 12:09
  • \$\begingroup\$ If anything that would make it safer. Current only flows in loops, so an isolated system like yours requires two failure points to actually flow current. Note that I don't believe current that flows to ground on the secondary of that transformer will be detected by the ground fault detection on the primary, so you could have an undetected ground fault on the secondary system. If one of the line wires on the 460V system shorted somehow to the secondary of the transformer, your system would detect the secondary ground connection as a ground fault. \$\endgroup\$
    – K H
    Apr 6, 2021 at 1:58
0
\$\begingroup\$

You have not told us the secondary voltage is on the secondary transformer, which is critical to a good answer.

eight 11 kV to 460 V ungrounded three-phase delta-to-delta transformers feeding as many switchboards. We will often get a ground faulted phase on these switchboards, due to the many consumers. We have ground fault detection and we usually find the culprit in a few hours.

Uninsulated neutrals on ships allow for a single ground-fault to occur without interrupting the flow of power to the ship. When a single ground-fault occurs the ship is energized at the potential of the line the ground-fault occurs on. Ships personnel are not directly at risk unless they touch a second power line.

It's why you have to clear ground-faults as quickly as possible to: prevent black-outs if a second ground-fault occurs; or injury to personnel. Even then, the person has to touch a live wire with one hand and the hull with the other hand (PPE requires all personnel to have electrically insulated shoes).

You find fault with a little bit of trial and error at switchboard with active ground fault detection.

Similarily, a second ground fault on any power line will cause tripped breakers.

You want a single-phase transformer with a grounded center-tapped neutral secondary. You know this is wrong, hence the question.

The hard connection at the secondary is the same as a second ground fault on any power line. Any ground faults on your 8 secondaries of your transformer secondaries will trip breakers on transformers and single-phase transformer.

Instantaneous or hard ground fault + hard grounded center-tapped neutral secondary complete short-circuit path. You have defeated the uninsulated neutral of the transformers, but ground-fault detection will be easier because a breaker will trip.

Now is this a problem. You are obviously an offshore oil rig with 11kV, possible drill ship. Lose power on a ship at wrong time, in a channel or dynamic positioning, then ship is at risk. A stationary rig is not directly at risk. You have to assess the risk, whatever your vessel is.

If a fault occurs at the secondary of the single-phase transformer, then single-phase transformer breakers will trip. The rest of the ship should be unaffected. This would be the same as on land.

\$\endgroup\$