I have an inverter/charger unit, with features I want, that is not typically used in an RV. It (unfortunately) does not automatically make/break a ground to neutral bond. I would like to automatically do this anytime shore power is connected to the RV. (As required by electrical codes).
I experimented with a 2 NO 2NC electro-mechanical relay with the coil connected to incoming 120V shore power. For the test, I ran a ground to neutral bond through one of the NC contacts, so that when shore power was not present, the bond was made. This appeared to work. When energized, the bond was broken, when de-energized the bond was restored.
But the coil could fail someday, and the manufacturer said it should fail in its normal state, not its energized state. I understand that is not a certainty, and therefore will deal with that issue separately. But for those reasons I also tested having shore power run through one of the NO contacts. That way if it the device fails and the ground to neutral bond is not broken, power is also not passed through to house loads.
When testing this, the coil began bouncing and no power was passed through the contacts. I called the manufacturer who stated that you can not power an EM coil with the same source that you're running through the contacts. The coil and and contacts are normally isolated, but by using the same source for both, you've now effectively created a jumper between them, which results in constant vibration/bounce, much like old AC doorbells use.
That being the case, in a chassis fault scenario where ground becomes hot, the coil would again be connected to the same source as one of the contacts, so it appears a contactor like this can not be used for this application.
I am therefore exploring alternatives. One option may be solid state relays, but does anyone know for certain if they will have this same issue? I see many for sale on Amazon boasting "switch the fan on when you turn the lights off," and other similar statements suggesting the SSR input and output can be connected to the same source with no issues. Is this correct?
Please note, I appreciate words of caution, and I am being careful. I am testing everything with full protective gear on a bench.
Here is the system's wiring diagram, but I had not yet drawn a diagram for the contactor that I was planning to use to make/break the ground to neutral bond It's the large yellow box with text on the lower right. (update: separate drawing is now included). I originally tested with the coil powered from 1 leg of the 120V utility hot (the one that will always be powered when using either single phase 120V hookups or when using split phase 120/240V hookups), and that same leg went through the contactors NO contact and then connected to the AC breakers in the diagram. That way if the coil's NC contact failed to break the ground to neutral bond when on shore power, no power would even reach the breakers, and I'd know to replace the contactor. But this didn't work in bench tests and manufacturer says it won't ever.
Update: I've added a drawing. Please understand my diagram skills are still limited, and I was trying to draw the device using the only available objects in EasyEDA's library. I also wanted the orientation to match the Contactor's diagram and my wiring. EasyEDA does not indicate when a wire jumps over another, so near R2 you'll see I tried to make the typical jump shape, but if there is no red node, then it means there is no connection. Please also note the Vehicle Chassis Ground to Neutral connection via R1 and R2 is mandatory code for RV power when not running on shore/main utility power. There is no debate over this. Where I have a circuit breaker and load drawn below, that is where the incoming power arrives at the AC Switchgear pictured above, then out to loads. But I included a simple CB and load below to complete the drawing.
Here is also a drawing of the front of the Contactor. You'll note its 4 pole, but I couldn't find a 4 pole in EasyEDA, so I used the next best thing.
  • \$\begingroup\$ Use the inverter to power the relay which is NC to shore ground then opened. Gnd current is normally low and only SMPS noise currents. Do you use GFCI’s? \$\endgroup\$ Commented May 18, 2021 at 22:59
    \$\begingroup\$ Consider adding a wiring diagram to your post if you would like more useful feedback. \$\endgroup\$
    – Pat
    Commented May 18, 2021 at 23:13
  • \$\begingroup\$ @Tony I can't use the inverter output because it also takes AC input and just passes it through to loads, so the ground to neutral bond must remain broken. But the instant shore power is disconnected, that bond needs to be restored because now the inverter is the source and there's no other ground to neutral bond. \$\endgroup\$
    – VanGogh66
    Commented May 19, 2021 at 2:29
  • \$\begingroup\$ @Pat good call Pat. I added one of the overall system but need to make one for the contactor I was attempting to use. \$\endgroup\$
    – VanGogh66
    Commented May 19, 2021 at 2:41
    \$\begingroup\$ @mkeith Absolutely 100% certain. It is explicitly stated in the user guide that the device does not do this and the user must do this when in true off-grid situations. I can update to include the datasheet but the install doc is around 100 pages and manual is very long too. It's a complex device. But right now it's not even connected. This is entirely just a test of making/breaking ground to neutral bond with a contactor. Nothing else is being asked of this group. I have no reason to believe inverter will function in any way different than its user manual when the time comes to connect it. \$\endgroup\$
    – VanGogh66
    Commented May 19, 2021 at 14:45
4 Answers 4
If I understand correctly you had a working solution where when the RV is unplugged the RV Neutral and RV chassis ground are connected through a NC contact on a contactor (I call it 'GN' contactor). When Shore power is applied that contactor opens disconnecting the RV Neutral and chassis ground.
You identified that if this GN contactor were to fail there would be no other protection from improper grounding. You would like some redundancy if this contactor failed to open properly.
You could implement the following:
On the left is the Shore power plug that provides a Line, Neutral, and Earth Ground connection. On the right side is the RV's internal 120Vac circuits.
To reduce the wire spaghetti I have broken up the RV Ground-Neutral contactor into a separate coil (inductor) and NO and NC switch. See the labels in the schematic.
Contactor M1 has 3 NO contacts (I had to add a third contact), when no shore power is available the connections between the shore Line, Neutral, and Earth ground are disconnected from the system. The RV neutral and chassis ground are connected.
When Shore Power is applied, first the RV ground-neutral contactor switches. This opens the RV ground-neutral connection. This also closes the NO contact in series between the Shore Line and M1's coil. When that contact closes the M1 contactor will then close.
This ensures that the RV ground-neutral contactor opens before the shore line is connected. If the GN contactor fails to open the Shore power will remain unconnected to the RV.
  • \$\begingroup\$ Hi @clipboard_waving_enginerd, Thank you for your response. It does appear you have understood the overall goal (finally someone does! -thank you!). Please clarify -- it appears from your drawing M1 coil has to already be energized before it's coil has a N return path. That won't work, right? And even if we fix that, I think at the end of the day the coil will always be powered by the same source its contacts are switching, which the manuf claims won't work. They may be wrong. I'm open to that. But I do like the idea of using staggered relays to see if that could set an order-of-events flow. \$\endgroup\$
    – VanGogh66
    Commented May 19, 2021 at 18:48
  • \$\begingroup\$ @BeachInMexico Good catch I updated the schematic. I can't think of a reason why having the same source for the coil and contact would matter, with a couple hand switches and an evening you could throw a demo circuit together and verify. I suspect there was a miscommunication some where. \$\endgroup\$ Commented May 19, 2021 at 20:45
    \$\begingroup\$ It just occurred to me, if the shore supply 120V cannot deliver the inrush current through the contacts, the voltage at the coil would drop when the contacts close and possibly cause the contacts to open again. The 120V would recover energizing the coil creating a open/close cycle until something breaks. So it comes down to can the Shore supply deliver sufficient inrush current. If it were my money I would build it and try (with a good way to kill power of course). \$\endgroup\$ Commented May 19, 2021 at 20:52
  • \$\begingroup\$ Good idea. Someone else also mentioned voltage feedback from inrush. My original test was with a moderate inrush (shopvac left in on position) because that's about the worst case scenario of leaving many loads on then switching to shore. I intentionally used a 100' 14 awg old extension cord reasoning that was a likely worst case RV park/friend's house hookup scenario. Maybe that combo was too much for the contactor, but when removing the contactor from the equation, the shop vac fired right up with Vdrop at 115V. It could have been much lower during inrush though. \$\endgroup\$
    – VanGogh66
    Commented May 19, 2021 at 21:34
  • \$\begingroup\$ Sounds like a good test. Adding a push button with latch in series of the GN contactor coil is your best bet. That way applying shore power requires first plugging in the RV, then pushing a "connect" button. If the supply can't source the startup current the connection fails but doesn't automatically restart and cycle. This would prompt you to turn off the loads on the RV. Once the RV is connected you can reconnect the desired loads sequentially. At the end of the day the shore supply can only do so much. \$\endgroup\$ Commented May 20, 2021 at 18:19
I would like to automatically [make/break a ground to neutral bond] anytime shore power is connected to the RV
The following circuit should work if your inverter/charger unit has separate connections for inverter-out and charger-in.
When shore power is available, the Neutral and Ground of the RV AC distribution system are "unbonded". (Provided their only connection is through the relay.)
[The schematic shows the shore power protective ground connected to the RV protective ground. The assumption made is that the shore power protective ground is similar to the actual earth (or water) potential near the RV.]
[The schematic only shows one "Live" line. If there are two live lines, L1 and L2, are used, you will need a larger or separate relay to disconnect the inverter from the shore power, when shore power is available.]
[If the inverter/charger unit does not have separate inverter-out and charger-in connections, the above circuit, by itself will not work, and requires additional circuitry. Please provide the manufacturer and model number for the inverter/charger unit.]
The above circuit does that, but also connects the shore neutral to the RV neutral after the bond is broken, and breaks the connection between RV neutral and shore neutral before the bond is re-established (when shore power is removed).
In the circuit above, if the coil fails, then the shore power L1 will remain disconnected to the RV power L1. [There is another possible failure mode of relays, which is that the contacts become welded together. If this should happen, the RV can still draw from the shore power, but cannot supply power to the shore (or the RV) from the inverter.
I have still not seen an accurate circuit diagram of how this test was made. My guess is that there is a problem with design/wiring. There are problems with the diagram you have provided, which are discussed in my answer to your other question.
You most certainly can power the coil of a relay with the same power you send through the contacts, provided the coil is rated for that voltage. If you are getting a constant on-off oscillation, it may be due to mis-wiring. That is, the "door-bell" effect you are seeing is possibly due to the fact that the relay is wired such that when the coil is energized, it opens contacts that break the circuit powering the coil. The coil then de-energizes, closing the contacts, allowing power to be applied to the coil again, and the process repeats. This is a design or wiring issue, and in no way negates the fact that a relay can be powered by the same power source that is applied to its contacts. It just has to be done right.
  • \$\begingroup\$ This long comment chain has exceeded what is reasonable for comments. Therefore it has been moved to, and should be continued in, chat (link below). --- As this bulk moving of comments to chat can only be done once, any further comments posted here which try to discuss the answer, might be deleted without notice. Keep it in chat, please! Any factual updates to the answer which are decided during the chat, should be made via an edit to the answer. Thanks! \$\endgroup\$
    – SamGibson
    Commented May 19, 2021 at 18:16
  • \$\begingroup\$ Comments are not for extended discussion; this conversation has been moved to chat. \$\endgroup\$
    – SamGibson
    Commented May 19, 2021 at 18:17
The concern here is basically the risk of an upstream neutral fault?
The really right solution is probably an isolating transformer (Plastic cased) right behind the external feed, and treat the entire secondary side as a separately derived supply with no connection to the shore power earth at all.
This is what I do on the boat, as marina shore power is an utterly random shit show, and between this and being able to tap change on that transformer I can cope with most things and do NOT get electrolytic corrosion issues.
However, a boat does not have (providing you mount it low down) a serious issue with a few tens of kg of iron and copper.
A lighter approach for an RV, would be a three phase RCD (GFCI) wired with live neutral and external earth thru the three phase contacts, this does NOT function as a conventional RCD (So you need a two pole one as well) but it does detect the presence of current in the earth that is being driven externally and trip the entire line off in this situation (All three conductors). This is essentially what a PEN fault protection device for EV chargers does and that might be the easy way to get the gear.
  • \$\begingroup\$ Hi Dan, thank you for that suggestion. I'll look into it, but as you mentioned I had looked at transformers early on and the size and weight ruled them out. Interestingly, this inverter actually has a transformer within it to take incoming 120V single phase and generate 120V/240V split phase. Or it can take 120/240V split phase and just pass it through to loads. Hopefully your three phase RCD will be a viable answer. \$\endgroup\$
    – VanGogh66
    Commented May 19, 2021 at 12:47
As from you picture, the incoming supply has L,N and PE. You may not bond N and PE together, they must be separated. You can see from your pic. that there is no N to PE bond present.
The N and PE bond shall be made when the incoming supply is consisted of L and PEN wire, then you make this bond and separate N and PE. After this point, no additional bonding is allowed, they must be separated for the entire system.
Now there should be a standard way to connect a mobile object by means of standard plug. Therefore the L and PEN as form 2nd diagram is to be excluded, since this type requires the fixed connection done by electric company. Only the 1st diagram is possible for mobile, where N and PE is already separated. I want to make you clear that you shouldn't be messing around this bond connection. Find a standard solution instead.
EDIT:
  • \$\begingroup\$ The trap here is that an RV is OUTSIDE THE EQUIPOTENTIAL ZONE so the question of what happens in a neutral fault upstream of the bond very much applies, as that can cause the large metal box that is an RV to rise a significant voltage above local earth which is a rude surprise when you step out in bare feet and go to close the door.... There are standards for this but they vary by country (IIRC over here RV sockets should be TT and RCD protected). \$\endgroup\$
    – Dan Mills
    Commented May 19, 2021 at 10:11
  • \$\begingroup\$ Exactly, in an RV or marine situation you do make/break Ground and Neutral everytime you go off/on shore power. When you go off shore power, there is no G+N bond in the system (unless your inverter does this internally; not all do). Once off shore power, the inverter is the source. If it's hot makes it to chassis, there is no return path rip the breaker unless you made a G+N bond. Once on utility/shore power, you can't have a downstream G+N bond from the main panel, so you must break that bond the instant shore is connected. There is no debate on this subject. It is RV/marine code. \$\endgroup\$
    – VanGogh66
    Commented May 19, 2021 at 12:50
  • \$\begingroup\$ I've now added a drawing of the Contactor. Please see update notes at end of original post. \$\endgroup\$
    – VanGogh66
    Commented May 19, 2021 at 14:37
  • \$\begingroup\$ @BeachInMexico What contactor you have? Exact model? Those R3,R4 could be just auxiliary contacts, not power one. \$\endgroup\$ Commented May 20, 2021 at 8:36
  • \$\begingroup\$ @MarkoBuršič It's the 2NO 2NC contactor, second down from the top left. Of course I made sure they weren't aux contacts. I even spoke to the manufacturer: electrodepot.com/contactorNONC.htm#_2NO_-_2_NC \$\endgroup\$
    – VanGogh66
    Commented May 20, 2021 at 12:54