0
\$\begingroup\$

I'm tasked wich building a test rig for electrical machines which consists of

  • Machines mounted on top of a large ground plate which is connected to PE through a thick cable

  • A torque transducer: The torque signal GND is internally connected to the chassis and thus also to PE

  • An oscilloscope which records the signals from the torque transducer.

  • A resolver which also internally has the signal ground directly connected to the chassis and thus also to PE

  • A digital controller (e.g. dSpace/RT Box). From Datasheet: "PE and signal GND are coupled internally by means of a high impedance RC network, consisting of a 1 MΩ resistor, a 1 µF capacitor and a 5V zener diode (SMAJ5.0CA), all connected in parallel". The resolver signals are connected to the signal GND of the controller and thus the signal GND is pulled to PE with two 3 meter long coax cables.

  • Oscilloscopes, controller and PC communicate via Ethernet: The ethernet connection also pulls everything to PE through the Ethernet socket in the wall.

    enter image description here

Now I'm wondering about the ground/PE concept. I want to have everything as failure proof as possible, because much hardware and software used in the test rig is self-made. I see 3 problems:

  • There are multiple parallel PE loops. Supposing a high voltage hits the ground plate until the RCP fires.
    • There is the desired low impedance connection from the ground plate to PE through the grounding cable
    • There is an undesired current path from the ground plate to torque transducer signal ground(=PE) to the oscilloscope to PE
    • There is an undesired current path from the resolver (signal GND=PE) to the controller through the "high impedance RC network" (which I assume will block the fault current) to PE
    • There is an undesired current path from resolver/torque transducer to controller/oscilloscope and then through all Ethernet devices to the Ethernet socket in the wall which connects to PE

My questions:

  1. Are my concerns valid? I'm concerned about a fault working through the entire test rig and destroying everything.
  2. How is such a test rig usually built fail-safe (e.g. in industry)?
  3. What do you think about (1) putting all Digital electronics behind an isolation transformer which breaks the direct PE connection and (2) using a WLAN stick to break the PE connection via the Ethernet socket? Then the only connection that remains is through the grounding cable

I apologize if the description isn't clear enough. I'm not a trained electrician, but more of a "theory idiot". Thank you!

\$\endgroup\$
2
  • \$\begingroup\$ Ethernet is an isolated interface. There should be no connection to PE. If you do have a wall socket that provides a PE connection to a shielded cable via shielded connector, use unshielded cable or connector so you don't have PE connection via Ethernet. \$\endgroup\$
    – Justme
    Commented Aug 4, 2021 at 10:58
  • \$\begingroup\$ There may be a coupling capacitance to PE on ethernet built in \$\endgroup\$
    – D.A.S.
    Commented Aug 4, 2021 at 11:15

1 Answer 1

0
\$\begingroup\$

For best noise immunity, use common PE connections with overvoltage and current limit protection and/or CM choke filter on signal lines.

Use STP cables for signals with source ground only to shield.

It is good to realize impedance paths for ground faults and use a GFCI and follow installation guides in manuals.

Industry standards were defined for immunity inhouse and gradually found their way into IEEE and CE standards.

PE is a standard practice for all equipment with PE plugs. Noise immunity depends on sources, cables, orientation and coupling and desired levels of signal/noise ratio.

\$\endgroup\$
1
  • \$\begingroup\$ Thank you. I'm not concerned with noise at this stage, but more with making sure that as many of my electronics survive in a fault. I'm wondering about the possible current paths that the fault current takes until the GFCI trips. Am I correct in worrying about fault current also flowing from (1) grounding plate->torque transducer->Oscilloscope->PE, (2) grounding plate->torque transducer->Oscilloscope->Ethernet network->PE and (3) flowing in ground loops in case of a ground fault? \$\endgroup\$ Commented Aug 4, 2021 at 12:00