I'm trying to derive formulas for active power (\$P_s\$) and reactive power (\$Q_s\$) at the sending end of a transmission line shown below:
Where: \$E_s\$ and \$E_r\$ are voltage magnitudes
\$X\$ is the unit line reactance
\$\alpha\$ and \$0°\$ are the load angles
I think the equations are these, but I'm unsure of how to take into account the reactance values.
Would line 2 and 3 be in parallel then in series with the rest?
And would the load angle be the sum of those shown in the diagram (in this case \$\alpha+0°\$)?
$$ S_r = P_r + jQ_r = E_r\dot{I^*}$$
$$ = E_r\left[\frac{E_scos\delta+jE_ssin\delta-E_r}{jX}\right]$$
$$ = \frac{E_sE_r}{X}sin\delta + j\frac{E_sE_rcos\delta-E_r^2}{X}$$
$$\boxed{ P_r = P_s = \frac{E_sE_r}{X}sin\delta \\ Q_r = \frac{E_sE_rcos\delta-E_r^2}{X} \\ Q_s = \frac{E_s^2-E_sE_rcos\delta}{X} }$$
Any help with this would be greatly appreciated!