In an old farmhouse that I grew up in, it was possible to measure about 70 volts AC of stray voltage on the metal conduit of the building, relative to a properly installed buried copper ground rod. The building was originally designed to have only two-prong wall outlets without a ground/earth connection for devices.
Conduit, but not intended for earthing/grounding
The building that you are in, most likely has old wiring dating back to the 1940s when it was common to install 2-wire circuits without a ground/earth connection, but the cable was typically installed in rigid conduit or flexible spiral armor-flex.
In this situation the conduit was primarily intended to protect the building wiring from damage, since it was sheathed in a relatively fragile rubber and cloth insulation.
Since the conduit was not really intended to carry power, no particular measures were taken to assure it was thoroughly conductive across its entire length end-to-end, and grounded/earthed properly at the fuse panel or circuit breaker panel.
It may have been painted over, or the lock nuts in electrical boxes are loose, or the conduit was not anchored into the electrical boxes at all. Later reconstruction work, replacing a metal box with a plastic one, would also split the conduit into separate sections that are electrically insulated from each other.
Knob and tube wiring
These old buildings may also still contain a mixed amount of even older wiring known as porcelain knob-and-tube, which ran individual wires on ceramic standoffs nailed into the wood frame of a building.
The ceramic knob has a ring indentation or notch on it, holding wire off the wood frame. Where wire has to pass through a wall or floor, it is inserted into a ceramic tube through the wall or floor.
If the ceramic insulators are still in good condition, knob and tube is still acceptable in the United States, though no new installations are being done with it, and it was not intended to provide grounding/earthing.
Stray voltage induction into poorly earthed/grounded conduit
If you have an exposed knob and tube circuit running parallel to unearthed or poorly earthed conduit, the nearby power conductor can inductively induce electrical current into the conduit, known as stray voltage.
Conduit induction can also occur where there are one-wire circuits nearby where power only flows in one direction next to the conduit through one part of the building to a load, and then returns back to the fuse panel along another path, possibly next to some other conduit.
Conduit induction does not normally occur with modern wiring as the wiring is typically installed in pairs (or for 3-phase, in triplets) through the same conduit, and the opposing current flow in the pair/triplet wires will cancel out any stray voltage induction into the conduit.
Single-wire circuits like this sometimes occurred with knob and tube because it was economical and saved money on always running the circuit wires grouped together in pairs.
Our farmhouse yard light started in the house, through a 2-way switch and up to the roof, to suspended wires out to the dairy barn milkhouse, through another 2-way switch in the milkhouse, and then back to the light pole in the yard, where it was connected to neutral at the pole.